PID definitions for Plain English/Script AutoTune PIDs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • PID definitions for Plain English/Script AutoTune PIDs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
18251 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

PID definitions for Plain English/Script AutoTune PIDs

Picard Product_Support
‎2018-09-06 03:28 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:49 AM

Issue

PID Definitions and definition for AutoTune PIDs.

Product Line

Andover Continuum, EcoStruxure Building Operation

Environment

  • Continuum 1.94
  • StruxureWare Building Operation 1.1 and higher

Cause

Argument for bPID in Continuum and StruxureWare Building Operation are:

Arg 1 Ena
Arg 2 Type
Arg 3 Cv
Arg 4 SP
Arg 5 Kp
Arg 6 LKi
Arg 7 LKd
Arg 8 Db
Arg 9 OP
Arg 10 Bias
Arg 11 Isum
Arg 12 err
Arg 13 Ltim

Arguments for AutoTuner PID Continuum and StruxureWare Building Operation are:

Arg 1 Ena Tuning Enable
Arg 2 Type type of control
Arg 3 Cv Measured variable
Arg 4 SP Setpoint
Arg 5 Kp Proportional gain constant
Arg 6 Ki Integral gain constant
Arg 7 Kd Derivative gain constant
Arg 8 Db Deadband
Arg 9 OP Output
Arg 10 Lag Output Device Lag time
Arg 11 Dev Deviation from setpoint allowed 
Arg 12 Pd Passed Data Array of 17 Numerics
Arg 13 Ta Time Date Array of 3 Variables

Resolution

For AutoTunerPID Wizard keep in mind that it is different than PID or often referred to as BPID. There are 3 types of PIDs

  1. bPID (normal PID)
  2. Simple PID (which was used for less memory available in controllers and had 9 Arguments)
  3. AutoTunerPID (designed to be run once on a system to ascertain the required values of Proportional, Integral and Derivative factors (Kp, Ki, Kd), when complete the function is normally to be replaced by the standard PID function as it will run faster with less system overhead. However when tuning is complete the PID tuning function will continue to control the plant using the standard PID function.)

Please note that PIDs are no longer autoconfig and there is no generic PID functionality with Continuum 1.94 and StruxureWare Building Operation 1.1 and higher, but custom solutions instead. 

  • bPID information on page 101 available in PID Function.pdf
  • Simple PID is on page 90 of the above link
  • AutoTunerPID information available in PID AutoTuner.pdf
Labels (2)
Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
Attachments
Tags (1)
  • Find more articles tagged with:
  • 7975
Was this article helpful? Yes No
0% helpful (0/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore