How to read individual bits from a Modbus Holding Register

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to read individual bits from a Modbus Holding Register
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
17466 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to read individual bits from a Modbus Holding Register

Picard Product_Support
‎2018-09-07 02:33 PM

Last Updated: Crewman ContentModerator ‎2025-09-25 02:45 AM

Issue

How to read individual bits from a Modbus Holding Register that holds a 16-Bit Word and represent each Bit as a separate Digital point

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Enterprise Server
  • Building Operation Automation Server (AS, AS-P, AS-B)
  • Modbus TCP/IP
  • Modbus RTU (RS485)

Cause

There is a requirement for a Modbus Holding Register that is a 16-bit unsigned value, each bit represents a digital state in the Modbus device and to replicate this as 16 separate digital states in EBO. The 16-bit unsigned value is an integer with a range of 0 to 65,535 and needs to be converted into 16 digital values.

Resolution

Use a Modbus Digital Input point for each bit required. Each object will be configured to read the same Modbus register address, but with a different bitmask value applied prior to evaluating the value.

For example: Read Modbus Holding Register 40123 with a value of 32769 (16-bit unsigned) and decode bits 0, 8, and 15 as three separate Digital points

Since the actual Value of 32769 being read at address 40123 is shown in Binary as 1000000000000001 it can be seen that Bit 0 and Bit 15 should return TRUE while Bit 8 should return FALSE

Reg 123.png

Configure each point as follows:

  • Modbus Digital Input Point 40123 bit 0
  • Register number 123
  • Register type 16 bit unsigned
  • Read function code 03
  • Bit mask - enable only Bit 0

Bit 0.png

 

  • Modbus Digital Input Point 40123 bit 8
  • Register number 123
  • Register type 16 bit unsigned
  • Read function code 03
  • Bit mask - enable only Bit 8

Bit 8.png

 

  • Modbus Digital Input Point 40123 bit 15
  • Register number 123
  • Register type 16 bit unsigned
  • Read function code 03
  • Bit mask - enable only Bit 15

Bit 15.png

 

Additional information can be found in the EcoStruxure Building Operation - Technical Reference Guide - Search for Bitmask.

 

If you need to break this bit information out for programming this can be done with a FB application and just binding the full 16 bits to the FB as shown here.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (4)
  • Find more articles tagged with:
  • 15375
  • DavidShore20
  • PeterLarsen20
  • PeterLarsen23
Was this article helpful? Yes No
90% helpful (9/10)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore