Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,841
  • TAC IA Series 1,823
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 7
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 25
    • 26
    • 27
    • …
    • 507
  • Next »

Installing I/NET Seven on a 64-bit operating system

Issue Initialization errors when starting I/NET Seven 2.42 or higher Error: "You must install an instance of SQL 2008R2 (64bit) before completing the INET install" Product Line TAC INET Environment I/NET Seven 2.42 Windows Server 2008 64-bit Windows 7 64-bit SQL 2008 64-bit Windows 8 Cause I/NET 64-bit requires specific installation process in order to function on a 64-bit PC Resolution Installing SQL Download SQL2008 R2 Express 64 bit (SQLEXPR_x64_ENU.exe) from this location: http://www.microsoft.com/en-us/download/details.aspx?id=30438 Run SQLEXPR_x64_ENU.exe In the left hand section, select Installation In the Right and section, select New SQL Server stand-alone installation of add features to an existing installation. At the "Setup Support Rules" screen select OK At the "Product Key" screen, select Next At the "License Terms" screen, check accept and select "Next" At the "Setup Support Files" screen, select Install At the "Setup Support Rules" screen, select Next At the "Feature Selection" screen select: Database Engine Services, SQL Server Replication, Management Tools - Basic (If Present) and SQL Client Connectivity SDK. Leave the Shared feature directory as default. At the "Instance Configuration" screen, select the Default instance option, accept the default Instance ID, accept the Instance root directory default settings and select next. At the "Disk Space Requirements" screen, select Next At the "Server Configuration" screen, under SQL Server Database Engine set the Account name to NT AUTHORITY/SYSTEM, leave the password field blanks, and set the startup type to automatic. Under SQL Server Browser Service, set the Startup Type to Automatic At the Database Engine Configuration screen, set the Authentication Mode to "Mixed Mode", Define a strong password (example: @sql2008), in the Specify SQL Server administrators section click "Add Current User". Select Next. At the "Error and Usage Reporting" screen, select Next At the "Installation Rules" screen, select Next At the "Ready to Install" screen, select Install At the Installation Progress screen, when the setup process is complete, select Next At the "Complete" screen, select Close. SQL Configuration: In the Windows Start Menu, launch the SQL Server Configuration Manager In the Left hand section of the window, highlight SQL Server Services Verify that SQL Server Browser and SQL Server are Running In the left hand section of the window, expand SQL Server Network Configuration and highlight Protocols for MSSQLSERVER Enable Named pipes and TCP/IP Close the SQL Server Configuration Manager Restart the PC Installing SQL Server 2005 Backward Compatibility On the I/NET 2.42 or higher installation CD, look in Support\SQLBCM_64Bit and launch the SQLServer2005_BC_x64.msi file Follow all the prompts on each screen and accept all defaults. Install I/NET Seven 2.42 or higher Install I/NET Seven 2.42 or higher using the installation CD Follow prompts and use defaults When prompted for the SQL password, select "Windows Authentication" Restart the PC Open I/NET Configuration through the start menu. Modify the default Config profile or create a new profile. Close I/NET Configuration Start I/NET NOTE: If error occurs during SQL installation stating invoke or begin invoke failed, follow instructions at this link: http://support.microsoft.com/kb/975055 UPDATE: SQL2008 SP1 prevents the invoke failed error. It can be installed with the same instructions as above. Download it at this link: http://www.microsoft.com/en-us/download/details.aspx?id=25052
View full article
Picard Product_Support
‎2018-09-10 12:28 PM

Last Updated: Administrator DavidFisher Administrator ‎2023-09-11 01:49 AM

Labels:
  • TAC INET
7154 Views

Changing a third party BACnet device's object identifier using VTS

Issue The object identifier of a BACnet device (device id) must be unique internetwork-wide, different vendors use different methods for calculating the device id default value. When integrating devices from different vendors sometimes it become necessary to change a device's default object id. Product Line Andover Continuum Environment bCX4040 b3s Third party BACnet devices Cause BACnet integration Resolution If the BACnet device is a Continuum device (bCX4040 or b3), Continuum provides a mechanism for changing the default device id. For a third party BACnet device, VTS can be used to write to the Object Identifier of the device in order to change the device id. Note that this will only work if the device manufacturer has made the object identifier for the device object writable. Click here to download VTS Click here to see the procedure to follow to set a third party device id using VTS.
View full article
Picard Product_Support
‎2018-09-06 12:49 PM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 01:47 AM

Labels:
  • Andover Continuum
2953 Views

Sigma Username and Password encryption

Issue Are username and passwords encrypted during transmission from the remote client or the web client to the Sigma server? Product Line Satchwell Sigma Environment Sigma Remote Client WebClient Cause Are username and passwords encrypted during transmission from remote client to the Sigma server? Are username and passwords encrypted during transmission from web client to the Sigma server? Resolution Usernames are not encrypted during HTTP transmission from the remote client and web client to the Sigma server. Passwords are encrypted during HTTP transmission from the remote client and web client to the Sigma server.
View full article
Picard Product_Support
‎2018-09-06 12:46 PM

Last Updated: Administrator DavidFisher Administrator ‎2023-09-11 01:47 AM

Labels:
  • Satchwell BAS & Sigma
2790 Views

Setting up a Local / Internal NTP Server to allow time synchronization

Issue When external internet access is not possible an alternative NTP Server is required to allow ES and AS to by time synchronized onsite. Product Line EcoStruxure Building Operation Environment Enterprise Server / Automation Server on closed network Eg Windows 7 Cause AS will not synchronize the time with a local NTP such as Windows 7 (32 or 64 bit) without it first being configured. Even then, increasing Cyber Security features within EBO means that the use of a 3rd Party NTP is becoming a much better option. Resolution Preferred Solution The very best option for the latest versions of EBO would be to investigate. Meinberg NTP which is a third party NTP server that runs on the Win7 or Win10 OS and provides NTP by synchronizing with four or more Internet clocks and is a trusted time source in NTP.  It is not an officially supported PSS tool, but it does fix the issue of the ES/AS not trusting the time.   Windows 7  Config If you still wish to attempt the Windows 7 NTP option first the procedure to setup is as follows:    In the 'Services' window (part of Administrative Tools) Stop the 'Windows Time' service if already running. The 'Startup Type' could be set as Manual or Automatic depending on the user needs. In the Registry Editor following changes to be made under the Key HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\services\W32Time: ** Config -> AnnounceFlags = 5. ** HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\services\W32Time\TimeProviders\NtpServer -> Enabled = 1. Start the 'Windows Time' service in the 'Services' window(part of Administrative Tools). Note: NTP uses UDP Port 123 Below is a Wireshark capture using filter udp.port == 123 indicating the “Leap indicator” bits are 11, meaning “clock unsynchronized”. NOTE: The NTP client in the AS may ignore the time sent by the NTP server if the root dispersion is greater than 'X' seconds (unknown at this time). See Automation Servers ignore time sync message sent from Windows NTP server that uses local internal clock for information on how to determine whether this is a problem at the site and how to resolve it. Note: Test Lab results show that once validated and synchronized, the AS asks the time from the NTP about every 17 minutes. Two enhancements have been requested for a future release: Workstation gets an alarm if the NTP is not a valid reply A tick box setting in Workstation so the ES/AS can accept an invalidated reply(time)
View full article
Picard Product_Support
‎2018-09-11 01:37 PM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 01:45 AM

Labels:
  • EcoStruxure Building Operation
14442 Views

Some attributes used within Continuum PE programs on b3/i2 controllers are no longer appropriate with SmartStruxure

Issue Some attributes used within Continuum PE programs on b3/i2 controllers are no longer appropriate with EBO Script programming Product Line EcoStruxure Building Operation Environment b3 Infinet Building Operation Server Script Programming Cause Some attributes used within Continuum PE programs on b3/i2 controllers are no longer appropriate or cannot be used with EBO Resolution An example of this would be the ElecValue attribute for an input or output. This can be used within the Conversion field of an input but cannot be used within a Script Program or Script Function. The Continuum example PE program for an STR502 or STR504 includes the line "If STR5xx ElecValue <= 0 then Return Upper" The correct result can be obtained within SmartStruxure by dropping the "ElecValue", so "If STR5xx <= 0 then Return Upper" Then ensure the STR5xx analog input is a Voltage type with no conversion configured. Note: The ElecValue keyword can still be used in the Conversion line of an Analog Inputs (e.g. for Counter input scaling). Some other Attributes not supported in Script Programming are: Size LogType
View full article
Picard Product_Support
‎2018-09-06 10:00 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 01:45 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
1800 Views

Enabling .NET Framework 3.5 fails using DISM fails with error 1910

Issue When attempting to enable .NET Framework 3.5 on Windows using the DISM command mentioned in the WebReport installation guide, the attempt fails with error 1910 Command: dism /online /enable-feature /featurename:NetFX3 /all /Source:e:\sources\sxs /LimitAccess Deployment Image Servicing and Management tool Version: 10.0.14393.0 Image Version: 10.0.14393.0 Error: 1910 The object exporter specified was not found. The DISM log file can be found at C:\WINDOWS\Logs\DISM\dism.log Product Line EcoStruxure Building Operation Environment WebReports Cause The Windows Modules Intaller service is not operating correctly, and has to be restarted. The service is however protected, so this can not be done through the services control panel. Resolution Kill "TrustedInstaller.exe" from the Windows task manager (CTRL+SHIFT+ESC) Start the "Windows Modules Installer" service from Windows services (Start->Run->services.msc) Try again, either using the command or the SBO Reports Preparation tool.
View full article
Picard Product_Support
‎2018-09-10 10:54 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 01:42 AM

Labels:
  • EcoStruxure Building Operation
5237 Views

Error displayed when importing a device XIF into SmartStruxure

Issue When importing an XIF into SmartStruxure, errors can be generated that vary in nature. Product Line EcoStruxure Building Operation Environment SmartStruxure Enterprise Server SmartStruxure Automation Server Building Operation Workstation Cause The XIF does not import successfully for a variety of possible reasons: There exists a device template in the server already that contains the same device ID as the XIF that is being imported.  The XIF does not comply with the LonMark Device Interface File Reference Guide published by LonMark. Resolution Before performing any of the steps below: Import the XIF file provided by the manufacturer of the Lon controller - if the manufacturer did not provide a XIF, try searching the LonMark product catalog If the provided XIF does not work, upload the XIF from the device to ensure that it is the correct file by following How to extract an XIF out of a Lon controller. Use the SBO SNVT Support tool found on The Exchange to identify unsupported SNVT's. Work through the troubleshooting steps below.   Device Template Fails without an Error This issue has been seen in some of the older versions of SmartStruxure (1.5 and older) and upgrading to the latest version will resolve the issue in many cases. If the issue occurs at the latest version of SmartStruxure: Use the SBO SNVT Support tool located on The Exchange to identify unsupported SNVTs. If the SBO SNVT Support tool does not identify any unsupported SNVTs, then send the XIF in to Product Support for further investigation.    Device Template Already Exists In order to complete the import of the XIF, follow these steps. Delete all controllers in that database that are using the device template that has the same device ID as the XIF file you are trying to import.  Now import the XIF again. Select the server in the system tree on the left and go to File > LonWorks import > Device Template. Click the Browse button and select the XIF you want to import. Click Import. Note: When the import is complete it will have overridden the old device template with that device ID. Two device templates with the same device ID will not be able to reside in the same database. For more information about device templates see Delete Device Templates.   Detailed Error Prompt with Specific Fields Listed Some examples of the detailed errors include but are not limited too: "Field X has error(s). The string must between X and X characters. nvoActualCapacity has X characters" on row X. "Field X has error(s). The number must between X and X. Field X has value X." on row X. "Field X has error(s). The value must be X but was X." on row X. Space or tab are not allowed in field 0Node Object on row X.   To Address these issues: Download Notepad++ to be able to better navigate the XIF by row number. Using Notepad++, open the XIF. NOTE: Backup the original XIF just in case there is a mistake when modifying. Find the row and field number prompted by the error messages and modify them accordingly. All the rules can be found in LonMark Device Interface File Reference Guide published by LonMark. Import the XIF again to verify whether it works. If not, contact Product Support for further investigation.
View full article
Picard Product_Support
‎2018-09-11 09:41 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 01:40 AM

Labels:
  • EcoStruxure Building Operation
4298 Views

Replacement of Satchwell "M 1201" Actuator forming part of combined Actuator / 2-port Valve Body assembly due to obsolescence.

Issue Satchwell “M 1201” Actuator forming part of combined Actuator / 2-port Valve Body assembly requires replacement. Environment Stand alone Satchwell “M 1201” Actuator forming part of combined Actuator / 2-port Valve Body assembly M 1201 Actuator 2-port Valve Body Cause Obsolescence of Satchwell “M 1201” forming part of combined Actuator / 2-port Valve Body assembly. Resolution There is no direct replacement for the "M 1201" Actuator and as a result both the "M 1201" Actuator and the 2-port Valve Body to which it is connected will also require replacement.  Replace Satchwell “M 1201” combined Actuator & 2-port Valve Body assembly with Schneider Electric MD10B-230 Actuator, LMD-MB Linkage Kit and Satchwell MB series 3-port Valve Body of appropriate size. Details of the original Satchwell “M 1201” combined Actuator & 2-port Valve Body assembly may be viewed here. Details of the replacement Schneider Electric MD10B-230 Actuator may be viewed here. Details of the replacement Schneider Electric LMD-MB Linkage Kit may be viewed here. Details of the replacement Satchwell MB 3-port Valve Body may be viewed here. N.B. Satchwell MB series 3-port Rotary Shoe Valve Body may be converted for use as a 2-port Zone Valve by means of the installation of a plumber’s plug in Port 3 Install plumber's plug in Port 3 of MB series 3-port Rotary Shoe Valve Body. Tighten plumber's plug sufficiently to ensure PN 10 rating of Valve Body is not compromised. It is possible that the "M 1201" Actuator may have been fitted with an Auxiliary Switch. If so then an MD-S1 Auxiliary Switch may be fitted to the MD10B-230 Actuator if required. Details of the MD-S1 Auxiliary Switch may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 04:56 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 01:37 AM

Labels:
  • Field Devices
5504 Views

SpaceLogic SLP series sensor shows as Non-conformant BACnet Device in Discovery

Issue When discovering the SLP Series Living Space Sensors they show up in the BACnet discovery summary as Non-conformant. Attempting to add this non-conformant sensor results in a WorkStation error similar to the following:  Validation Error Workstation Error in "~/BACnet Interface/MSTP Network/Living Space Room Unit 4E5932F5_«1»_07/ForeignAddress". Property value "<device, 10000>" already assigned to "~/BACnet Interface/MSTP Network/SLPSTC2/ForeignAddress". COML Validator0 Product Line EcoStruxure Building Operation Environment BACnet MSTP Living Space SLP Series Air Quality Sensors Living_Space_REV2.05.21 Cause Building Operation does not allow duplicate BACnet IDs and hence, during discovery, if a device is found with a BACnet ID (Object Identifier) the same as an existing device it shows as a non-conforming BACNet device. The default device ID for SLP devices should be equal to (Vendor ID * 1000) + MAC Address. Where vendor ID is our Schneider Electric BACnet vendor ID = 10 and the MAC address is unique to each devices MAC address DIP switch setting. This will be corrected in a future release of the Living Space firmware.  Until corrected, and since the Device ID is a read/write attribute the customer is able to change it to avoid duplicates on the bus. Unfortunately, Building Operation does not currently have a method to write a new device ID. Resolution The current workaround is to use a third-party BACnet Explorer such as Yet Another BACnet Explorer (YABE) to write a new device ID value. Once the new ID has been updated the SLP device can then be rediscovered within Building Operations'. 
View full article
Guinan RobertAndriolo Guinan
‎2021-03-10 07:08 PM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 01:35 AM

Labels:
  • EcoStruxure Building Operation
2389 Views

Where to find commands used in Security Expert objects to implement new functions

Issue Unable to find details on all commands that have been added to Security Expert objects to implement new functionality. Having this information available would help determine feature set possibilities. Product Line Security Expert Environment Security Expert Client, SP-C Cause Commands used in objects such as Controllers, Doors, and Access Levels may not be documented in the online help, installation, or operation manuals as they are being used to implement new functionality that has not been added to the Security Expert yet. There is no stand-alone list of all available Commands. Resolution Commands are listed in the firmware Release Notes and defined further in Application Notes.
View full article
Kirk AdamSteele Kirk
‎2020-07-28 05:08 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2023-09-11 01:31 AM

Labels:
  • EcoStruxure Security Expert
1251 Views

What can cause a Continuum controller to reset, cold start or lose data

Issue Controller loses data following power failure or mains noise (from transients or spikes). Product Line Andover Continuum Environment All CX, ACX, i2, bCX, b3 controllers Cause Controllers are exposed to operating conditions outside their operating envelope and tested limits. This can cause them to reset, go offline or lose data. In extreme circumstances, poor installation can take controllers outside their operating envelope and cause damage requiring a repair. Resolution If a controller is setup on a bench with a clean power supply and the correct grounding, you will be able to turn off/ on the power and the controller will warm start every time. This test will confirm the controller is operating correctly, not faulty and that the software settings are correctly set for warm starting. Also that the RAM backup battery is connected and operating. If site resets, lockups, loss of memory or other corruption are seen on a site, then here are some of the installation issues to consider: Grounding - All controllers require a clean low impedance earth to sink all of the noise and emission energy a controller may be exposed to. The noise protection circuitry within a controller is designed to dissipate this energy down to earth, if this path is not low impedance the energy can cause a controller to reset or even be damaged permanently. Shared Ground - The earth cable to the Controller should not be shared with any other equipment that is a high inductive or capacitive load, these can generate noise spikes back into the controller. This includes motors (pumps/ fans etc) lighting circuits (capacitive loads), inverters (high frequency noise). Induced emissions - The controller should not be installed near any equipment that may induce excessive radiated emissions into the unit, the radiated emissions from Motors, inverters, radio & microwave equipment, lighting circuits, power wiring can all produce radiated emissions that could exceed the specified limits of the Controllers. By fitting the controllers into earthed metal enclosures you can minimize the external emissions by effectively creating a Faraday cage protecting the controllers circuitry. Power feed - The power requirements for every controller is defined in its datasheet with the defined tolerance, taking the power levels outside these limits can cause incorrect operation. Power spikes - Surges or spikes in power feeds or connection I/O cabling can cause controllers to reset, lose data or even become damaged. Fitting varistors to the power supplies and across any output loads can minimize the impact on the controller, See What Varistors should be used?. Shared Supply - The power feed to a controller should never be shared with other equipment that can generate electrical noise. Never use the same supply to power both controllers and field equipment like valve/ damper actuators in BMS systems or magnetic door locks in Access control, both actuators and the solenoids in Mag locks can generate large back EMF pulses into the controllers that can cause resets or even damage.. Fitting power filters or an external UPS on the controller can protect it from spikes on power up/ down, it is however always best to remove the noise spikes at source, so fit filters the generators, motors, contactors etc. It is also possible for the above issues to cause Infinet networks to Reconfig as well as other networking problems. Note: All controllers are approved and tested to the defined limits for FCC and CE induced and radiated emissions as detailed in the datasheets, for a controller to fail, restart or lose data it must be exposed to levels exceeding these specifications. They are not however power equipment and cannot be exposed to the noise levels power and industrial controls equipment is designed to withstand.
View full article
Picard Product_Support
‎2018-09-06 11:56 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 12:37 AM

Labels:
  • Andover Continuum
3945 Views

Security Expert - Denied Entry by "Entry Mode Error Door Waiting for Bio Mode Card Input Credentials"

Issue Security Expert is denying user entry to a door and generating an event message stating waiting for Bio Mode Card Input Credentials.  Biometric credentials are not being used for the door. Product Line EcoStruxure Security Expert Environment Security Expert Client Cause Custom credential settings are not correctly configured for the door and reader.  The door is set to use a Door Type expecting a Custom Credential but the Reader is configured to use a standard card format.   Resolution To fix the issue the Reader must also be configured to use a Custom Credential.  Navigate to Reader Expanders and select the associated Reader Expander. For the Reader set the Reader(x) Format to Custom Credential as expected in the Door Type Right click the Reader Expander, select Update Module, and after a successful update test the operation.
View full article
Sisko GavinHe Sisko
‎2023-09-10 07:10 PM

on ‎2023-09-10 07:10 PM

Labels:
  • EcoStruxure Security Expert
1690 Views

20k (Honeywell) Thermistor does not work on an EcoStruxure IO Module

Issue When using the 20k (Honeywell) thermistor type on an EcoStruxure IO Module, the temperature value does not change and reads an inaccurate value. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server IO Module Cause The 20k (Honeywell) thermistor type does not work properly in Automation Server IO module firmware versions 2.009 and older. Resolution Check and upgrade the Automation Server IO module firmware to the latest version. Follow the steps below: Select the module in the System Tree (1) and on the Properties tab (2) check the Firmware version (3) If the firmware requires upgrading the latest version can be downloaded from The Exchange Download Centre.  For instructions on how to upgrade the firmware see Upgrading Automation Server IO Module Firmware.
View full article
Picard Product_Support
‎2018-09-11 01:41 PM

Last Updated: Sisko GavinHe Sisko ‎2023-09-08 01:18 AM

Labels:
  • EcoStruxure Building Operation
1155 Views

Upgrading Automation Server IO Module Firmware

Issue How to upgrade Automation Server IO module firmware. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Automation Server Premium Building Operation I/O Module  Cause Occasionally new firmware builds will be released for the Automation Server IO Modules to address issues or add enhancements to the products. These firmware builds must be downloaded to the modules through Workstation. Resolution Upgrading IO Module Firmware The latest version can be downloaded from The Exchange Download Centre.  Once the firmware is downloaded right click on the IO module in the System Tree and select "Update IO module firmware..." The "Update IO Module File" browse window will automatically open.  Browse to the new firmware file and click "Open". The latest IO firmware files can be downloaded from The Exchange Download Centre.  Once the IO module update is complete, click "Exit". To check the firmware version in the IO module, select the module in the System Tree (1). Click on the Properties tab (2) and check the Firmware version (3). For additional information refer to Updating Central IO Module Firmware
View full article
Picard Product_Support
‎2018-09-06 09:20 AM

Last Updated: Sisko GavinHe Sisko ‎2023-09-08 06:10 AM

Labels:
  • EcoStruxure Building Operation
2946 Views

IO module status shows 'Bootloader'

Issue IO module status shows 'Bootloader' Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server IO Module Cause The most likely cause is a failed upgrade process.  During an upgrade, the IO module's firmware is deleted allowing it to be replaced with the new firmware.  If the process fails before completion the module will be left without the application and in bootloader mode. Resolution Upgrade the firmware by following the instructions at Upgrading Automation Server IO Module Firmware. The operation takes less than a minute and the Module status should show status 'Configured' or 'Unconfigured' depending on whether points have been created on the module.
View full article
Picard Product_Support
‎2018-09-11 07:48 AM

Last Updated: Sisko GavinHe Sisko ‎2023-09-08 02:42 AM

Labels:
  • EcoStruxure Building Operation
1416 Views

Advanced Display v3 (AD v3) displays Website Not Available

  Issue Cannot communicate to an ADV3 connected to the USB port of an AS-P or AS-B. The error message “Website not available” is displayed. Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation Advanced Display v3 (AD v3) Cause The AS-P or AS-B’s USB port uses a IP network connection to the ADV3 that defaults to 192.168.42.116. If the AS-P’s primary port is in the same range, for example the main LAN network range is 192.168.42.* there is a conflict with the USB IP network. Resolution Change the sites main LAN, which the AS-P or AS-B primary port connects too, to another network range.
View full article
Gary Schneider Alumni (Retired)
‎2023-09-08 03:36 AM

on ‎2023-09-08 03:36 AM

Labels:
  • EcoStruxure Building Operation
2758 Views

Cannot clear Semantic DB default admin password alarm when Enterprise Server added to Enterprise Central

Issue On a system requiring Semantics after adding Enterprise Servers to an Enterprise Central alarms are generated that cannot be cleared.  Changing the password for the Servers does not fix the issue. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Central Building Operation Enterprise Server Building Operation Workstation Cause Incorrect method used when setting up Semantics during installation, Semantics were enabled on the Enterprise Server as well as the Enterprise Central.  After adding to the Enterprise Central the Enterprise Server points to a different address where the alarm is for the original Enterprise Server address.   Resolution On the Enterprise Server the alarm needs to be verified against the original connection, this involves removing the lead object link and changing the settings to look at the original Semantic Database.   On the Enterprise Server Semantic Settings remove the lead object entry pointing to the Enterprise Central.  Open the Services Manager and Stop and Re-Start the GraphDB service, if stopped start it. Additionally, Stop and Start the Enterprise Server service, this can also be done in the Services manager using Software Administrator to stop and start will show any errors if evident. Log back into the Enterprise Server and the password alarm should be cleared, this may take a minute or so but not any longer.  This is only if the password has been changed, please see Semantic DB authentication failure" alarm. Also, in the EC the password alarm should have cleared. Once the alarm is cleared the GraphDB service can be disabled from within services as it is not required. Re-instate the lead object entry pointing to the Enterprise Central that was initially removed. For more information on Semantics please see Semantic Overview
View full article
Sisko GavinHe Sisko
‎2023-09-07 07:57 PM

on ‎2023-09-07 07:57 PM

Labels:
  • EcoStruxure Building Operation
3147 Views

Access Expert User Group Permissions 'Password is incorrect' Error

  Issue After adding a new group with limited permissions to a User, the User cannot change their password or Login to the Instance. The Error 'Password is incorrect' is displayed When trying to change the password the dialog box may flash, but not continue. If you click the Ok button again, it will show the 'Password is incorrect' box. Product Line EcoStruxure Access Expert Environment Access Expert Hosted V3 Cause A User Group with restricted access to specific objects didn't have permissions to the Instance object Resolution Add permissions to the User Group If 'All Types' are a part of a UserGroup then the 'Instance' object is included. However, if specific object permissions are selected for the User Group then the 'Instance' Read permission must be added at a minimum for the User to have access to the Instance. If the User is required to change their password then they will also need Publish permissions. Original Changed
View full article
Admiral Alan_Wood Admiral
‎2023-09-07 07:54 PM

on ‎2023-09-07 07:54 PM

Labels:
  • EcoStruxure Access Expert
1326 Views

I/A Series Niagara 4 Hardening Guide - Tips to Secure an I/A Series Niagara 4 System

Issue Procedures and processes to secure I/A Series Niagara 4 Systems Product Line TAC IA Series Environment  I/A Series Niagara 4 Systems Cause Users accessing system without permission Potential damage done by malicious entry to the system Resolution The attached document describes how to implement security best practices in an I/A Series Niagara 4 system.  While it is impossible to make any system completely impenetrable, there are many ways to build up a system that is more resistant to attacks. In particular, this document describes how you can help make an I/A Series Niagara 4 system more secure by carefully configuring and using: Passwords System Passphrase Platform Account Management Station Account Management Role and Permission Management Authentication TLS and Certificate Management Module Installation Additional Settings External Factors Please note that while all of these steps should be taken to protect your I/A Series Niagara 4 system, they do not constitute a magic formula. Many factors affecting security and vulnerabilities in one area can affect security in another; it doesn’t mean much to configure a system expertly if your JACE is left physically unsecured where anyone can access it. Note: Schneider Electric strongly recommends upgrading to the latest I/A Series N4 version maintenance build that implements numerous security updates.  Before updating any system, make sure to review the build-included documentation to understand the behavioral impacts of the security enhancements and JACE hardware platforms supported. Download the Niagara 4 Hardening Guide_2023 for more details.
View full article
Lt. Commander WaynePeters Lt. Commander
‎2019-01-31 01:19 PM

Last Updated: Guinan RandyDavis Guinan ‎2023-09-07 12:14 PM

Labels:
  • TAC IA Series
5205 Views

Using a VPN with I/A Series Niagara G3 Systems

Issue Using a VPN with I/A Series Niagara Systems Product Line TAC IA Series Environment I/A Series Systems Cause A VPN's purpose is to provide a secure and reliable private connection between computer networks over an existing public network, typically the Internet. Resolution What is a VPN? "Virtual Private Network" or VPN is a mechanism to extend a private network across a public network such as the Internet. A VPN creates a point-to-point connection or "tunnel" across the Internet between two computers. The tunnel encrypts the data between VPN endpoints, preventing data from being deciphered without the required encryption keys. Why use a VPN? VPN provides an additional layer of security to your Niagara system without compromising your ability to access Niagara. A VPN can help protect your Niagara system from Internet-based attacks by requiring an additional layer of authentication to access Niagara resources. It can prevent automated Internet port scan tools from detecting the Niagara system. How can I set up a VPN? The following document describes how to use an Internet Security Gateway to provide VPN access to your ENC/JACE.  Click on the link to download Using a VPN with Niagara Systems for more details. In addition, the document describes setting up a VPN using a ZyWALL gateway.  The ZyWALL USG-20 unified security gateway (from ZyXEL) is a cost-effective device that you can add to an existing installation to provide VPN server capability. IMPORTANT NOTE: The information in this document is based on the assumption that the only IP devices on the network are Niagara devices. If Niagara devices share a network with other devices (such as a corporate LAN), DO NOT follow the approach described in the following pages. Instead, work with the customer’s IT department to determine the best method to protect both the Niagara and corporate systems while providing required access to the Niagara systems. In any scenario, if the VPN is installed or configured improperly, you can expose devices to the public Internet. If you are unsure about how to best configure and test your configuration, please consult an IT expert. Frequently Asked Questions I already use SSL, do I still need to use a VPN? The use of a VPN is still recommended as an additional layer of security. Attacks can come from both inside and outside of your network. Once I set up a VPN, do I still need to use SSL? Yes. The VPN only provides encryption between the VPN endpoints – the VPN client and server. Traffic from the VPN endpoint to and from the Niagara Station is not encrypted unless SSL is used. I’m running AX 3.6 or earlier without SSL support – should I still install a VPN? Yes. The VPN still helps protect against Internet-based attacks on your system. Do I still need a firewall? Yes. You should set up firewall rules to restrict Internet access to the VPN server port only. You should also consider setting up rules with the VPN server to restrict VPN access to only the required IP addresses and ports. For example, there may be non-Niagara devices on the LAN, but the VPN should be configured to only allow access to the Niagara systems. Additionally, you should only allow access to required Niagara services. Will a VPN affect LAN access to ENC/JACEs? No. LAN access to the Niagara devices remains the same as always. VPN only affects the ability to reach Niagara devices from external networks such as the Internet. If I use a VPN, will Niagara HTTP, Fox, and Platform tunneling work? Tunneling works normally over a VPN. You will need to update IP address assignments. What is the impact of VPN on Niagara Networking? Niagara Networking between systems on the LAN still functions the same whether or not there is a VPN installed. When I connect to a VPN, do I lose all other network connectivity? While your VPN client is connected to the remote VPN network, your Workbench (client) PC will have a new "Default Gateway" to allow you to make connections to stations on the VPN network. Typically, this happens without your knowledge and is mostly transparent. The change is undone after disconnecting from the VPN, and re-done when you reconnect. However (while you are connected to the VPN network) if your Workbench (client) PC tries to connect to sites on the [public] Internet or any other network through any router, you will find that you cannot reach those sites. If you must be able to reach those sites while connected to the VPN network, you will need to add static routes (temporary or permanent) to your Workbench PC’s TCP/IP configuration. The setting of those routes is beyond the scope of this document because they are specific to your PC’s network, your VPN network, and any other networks you try to reach. It is possible (but unlikely) that you cannot resolve these routing issues. This may happen if one or more of these networks have overlapping addresses. Consult with a TCP/IP expert if necessary. Likewise, if you use L2TP, PPOE, PPTP, or PPP for any part of your underlying network connection, the VPN client will probably conflict with it. Specifically, Windows only allows one connection of these four protocol types to be active at any given time. What is the impact on Single Sign On? You will need to define the SSO Domain and the hosts of the SSO Domain in your Workbench PC’s "hosts" file or default DNS server. The DNS server of the VPN will not be able to provide name services without changing your Workbench PC’s TCP/IP configuration. I use Dynamic DNS, can I still use a dynamic DNS provider with VPN? Yes. You will need to register the IP address of the VPN gateway and firewall with the DDNS provider. What is the impact of VPN on my system performance? Impact on performance should be minimal. It does take a little longer to set up the connection. References: Microsoft TechNet VPN Overview 
View full article
Picard Product_Support
‎2018-09-11 08:25 AM

Last Updated: Guinan RandyDavis Guinan ‎2023-09-06 10:26 AM

Labels:
  • TAC IA Series
2456 Views
  • « Previous
    • 1
    • …
    • 25
    • 26
    • 27
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of