Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

What can cause a Continuum controller to reset, cold start or lose data

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What can cause a Continuum controller to reset, cold start or lose data
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • PaulFr
    PaulFr
  • DavidFisher
    DavidFisher
  • chris_clerc
    chris_clerc
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
3885 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What can cause a Continuum controller to reset, cold start or lose data

Picard Product_Support
‎2018-09-06 11:56 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 12:37 AM

Issue

Controller loses data following power failure or mains noise (from transients or spikes).

Product Line

Andover Continuum

Environment

All CX, ACX, i2, bCX, b3 controllers

Cause

Controllers are exposed to operating conditions outside their operating envelope and tested limits. This can cause them to reset, go offline or lose data.

In extreme circumstances, poor installation can take controllers outside their operating envelope and cause damage requiring a repair.

Resolution

If a controller is setup on a bench with a clean power supply and the correct grounding, you will be able to turn off/ on the power and the controller will warm start every time.

This test will confirm the controller is operating correctly, not faulty and that the software settings are correctly set for warm starting. Also that the RAM backup battery is connected and operating.

If site resets, lockups, loss of memory or other corruption are seen on a site, then here are some of the installation issues to consider:

  1. Grounding - All controllers require a clean low impedance earth to sink all of the noise and emission energy a controller may be exposed to. The noise protection circuitry within a controller is designed to dissipate this energy down to earth, if this path is not low impedance the energy can cause a controller to reset or even be damaged permanently.
  2. Shared Ground - The earth cable to the Controller should not be shared with any other equipment that is a high inductive or capacitive load, these can generate noise spikes back into the controller. This includes motors (pumps/ fans etc) lighting circuits (capacitive loads), inverters (high frequency noise).
  3. Induced emissions - The controller should not be installed near any equipment that may induce excessive radiated emissions into the unit, the radiated emissions from Motors, inverters, radio & microwave equipment, lighting circuits, power wiring can all produce radiated emissions that could exceed the specified limits of the Controllers.
    By fitting the controllers into earthed metal enclosures you can minimize the external emissions by effectively creating a Faraday cage protecting the controllers circuitry.
  4. Power feed - The power requirements for every controller is defined in its datasheet with the defined tolerance, taking the power levels outside these limits can cause incorrect operation.
  5. Power spikes - Surges or spikes in power feeds or connection I/O cabling can cause controllers to reset, lose data or even become damaged. Fitting varistors to the power supplies and across any output loads can minimize the impact on the controller, See What Varistors should be used?.
  6. Shared Supply - The power feed to a controller should never be shared with other equipment that can generate electrical noise. Never use the same supply to power both controllers and field equipment like valve/ damper actuators in BMS systems or magnetic door locks in Access control, both actuators and the solenoids in Mag locks can generate large back EMF pulses into the controllers that can cause resets or even damage..

Fitting power filters or an external UPS on the controller can protect it from spikes on power up/ down, it is however always best to remove the noise spikes at source, so fit filters the generators, motors, contactors etc.

It is also possible for the above issues to cause Infinet networks to Reconfig as well as other networking problems.

Note: All controllers are approved and tested to the defined limits for FCC and CE induced and radiated emissions as detailed in the datasheets, for a controller to fail, restart or lose data it must be exposed to levels exceeding these specifications.

They are not however power equipment and cannot be exposed to the noise levels power and industrial controls equipment is designed to withstand.

Labels (1)
Labels:
  • Andover Continuum
Tags (4)
  • Find more articles tagged with:
  • 11152
  • earthing
  • PaulFrost19
  • reconfigs
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of