Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC INET
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,688
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac inet"

View in: "Building Automation Knowledge Base" | Community

1444 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 25
    • 26
    • 27
    • …
    • 73
  • Next »
Label: "TAC INET" Show all articles

Guard Tour for I/NET

Issue Guard Tour for I/NET Environment I/NET site with Access Control Cause Is there a Guard Tour configuration or is there add-on software for Guard Tour with I/NET Access Control Resolution I/NET really does not have a Guard Tour add-on. It does not have a Guard Tour setting with the Access Control functionality.    What I would suggest however, is that you can run a report on an individual card, and this report could have the times at which the card was used. This could for example be the Guard card, and show that at specific times the Guard used the card. This also would apply to a Group such as Guards. I/NET does not have a Guard Tour add-on. It does not have a Guard Tour setting with the Access Control functionality.   However, a site can run a report on an individual card(s), and this report could have the times at which the card was used. This could for example be the Guard card, and show that at specific times the Guard used the card. This also would apply to a Group such as Guards.   Please find two custom reports for using with the above suggested scenario.  Custom Reports.zip which contains two reports: TAC_TransactionsIndividuals_dateIndivID_001.rpt TAC_TransIndiv_Date_IndivID_GroupName.rpt  
View full article
Picard Product_Support
‎2018-09-11 04:31 AM

Labels:
  • TAC INET
1301 Views

Archiving and SQL database size keeps growing

Issue Archiving and database size with FIFO not working Product Line TAC INET Environment I/NET site Cause dbo.Events keeps growing and presumably is not in FIFO mode (First In First Out) Resolution Note: Autogrowth is not used with TAC I/NET Seven or TAC Andover Continuum The size of the InetDB can be set through Microsoft SQL Server Management Tool:   By selecting the InetDB database properties you can set the Autogrowth setting via the Files page.  Under the Autogrowth column select the browse button as shown:   The Change Autogrowth setting by either disabling the Autogrowth check box or you can set Autogrowth to a Maximum File Size as shown:     The Autogrowth value now shows this setting is restricted to setting define in step 2.   Disabling Autogrowth allows the events to be removed from the table when the total size of the SQL database reaches the limitation set in the properties of the db. The table dbo.Events has all the current events and it should be the biggest. The dbo.currenteventdetail table keeps up with the current max events and the current minimum events. Lets say it is around a million (1,000,000) events and so the first event in this table would be 01 and the last would be the 1000000. If items are removed from the other table, the dbo.Events, then this other table, the dbo.currenteventdetails is off. This means we run the risk of losing those events that are not correctly numbered. Manually removing items from one table can have an impact on other tables and how this data is kept and archived. About archiving and shrinking the db, this is a function of SQL. SQL goes into a FIFO mode, which means First In, First Out. This keeps the db from getting to large. The archived records are designated as archived in the db and even though they are still (secretly) in the db, they will be out as soon as the db is over the capacity amount and the amount designated in the db.currenteventdetail table is the guide for what is current. The thing that keeps the db from getting to large is the archive is setup correctly and old data is archived. It is still available via Reports, but considered not technically in the db. That is what shrinks the db and keeps it from getting over size.    Note: Autogrowth is not used with TAC I/NET Seven or TAC Andover Continuum
View full article
Picard Product_Support
‎2018-09-11 05:13 AM

Labels:
  • TAC INET
2379 Views

How to get the modbus registers from a ICP7188

Issue How do you get the Modbus register list and communication values from a ICP7188 (SP7040) project. Have extracted files from ICP7188 (blue turtle) want to upgrade this to a Xenta 731 or 913, how can I read the current register configuration from this device. Environment ICP 7188 Cause Want to replace a ICP7188 "blue turtle" device with a Xenta 731 or 913 and need to now what the current Modbus configuration / registers are in the ICP7188 device. Resolution To retrieve the Modbus values from the ICP7188 (SP7040) project you will need two text files Cfg9100.txt and MAP9000.txt. from the original project. and the following files contained in this ZIP file SP7040. Note:  If you need to extract these files you can follow the instructions in the "ILink Commissioning Guide" PDF which is contained within the above ZIP file.  If you don't have the LinkTerm application detailed in this document you can download and install it from here. N.B: After extracting this LinkTerm.zip file there are two files with the extension '.rename', ISDEL and SETUP.  Both these extension must be renamed to '.EXE' and then you can follow the instructions is the above mentioned guide. After extracting the SP7040 ZIP file to a drive on your PC along with the two text files into the directory proceed with the following steps: 1. Open the TGT9100.xls file. Make sure you have Macros enabled in Excel. 2. Then select the Device Editor button.   3. This will move you to the System Device summary with a message indicating there is a mismatch of the configuration files. Select Yes too load the configuration files   This will populate the Table from the txt files copied earlier. 4. Now you can select the + button next to the Type heading 5. Then select the + button next to the Type heading to show the Modbus values for that device.   6. To view the communication setup select the + button next to the System heading as seen in the step 4 image.
View full article
Picard Product_Support
‎2018-09-11 04:00 AM

Labels:
  • TAC INET
  • TAC Vista
1432 Views

INET UDP port troubleshooting

Issue How to troubleshoot UDP IOServer can not communicate with Xenta Environment Xenta Server Ethernet Communication (UDP) Cause INET communicate with Xenta Server via UDP but sometimes another process are occupying the default port Resolution Refer to this guide
View full article
Picard Product_Support
‎2018-09-11 02:31 AM

Labels:
  • TAC INET
1775 Views

Fiber Optic Interface alternative from Westermo

Issue Alternatives to the FOI1 and FOI2 product which is discontinued and possible replacement using the Westermo ODW-730-F2 Environment Site using a Fiber Optic Interface on LAN (CLAN) or SCU Network (SubLAN) Cause Discontinuation of the FOI1 and FOI2 products which have been available for a number of years. Resolution The ODW appears to provide a very cost effective and versatile fiber optic interface for RS485 networks. The ODW is one of only a few RS485/Fiber interfaces that provide the redundant fiber network capability. Some notable features on the ODW-730-F2 include – -Dual Fiber Bus Configuration or Dual Fiber Redundant Ring Configuration -Local status contact output indicates fiber fault detection -LED indication of Local fiber fault condition (FL L) CH1 and CH2 LEDs indicate if failure is on incoming or outgoing fiber -LED indication of Remote fiber fault condition (FL R) Here the LED indicates when there a fault anywhere in the system. A summary of controller status points monitoring the Local fault detection would be reviewed to identify location of a fault. Current system operation is probably operating on the basis of the redundant ring. A second fiber fault will disable the ring system. In a bus configuration, you currently have lost some portion of the system communications. -Supports Asynchronous (SubLAN) and Synchronous (CLAN) protocols In the case of the synchronous CLAN interface, it is not reconstructing RS485 data quality. Any accumulated distortion on the copper cable segment is passed on to the data through the fiber and will arrive at the other fiber drops in the same condition, although amplitude will be replenished. You must insure you do not exceed copper cable distances and maintain compliance with recommended grade of cable while avoiding stubs and the distortion they produce. -Alternate Fiber Interface Options are supported two receptacles for plug-in fiber transceiver module purchased separately The lowest cost and most common interface is the MLC2. Each of the ODWs in this evaluation were configured with 2 of the MLC2 modules - MLC2 Multimode 62.5/125um or 50/125um 2km Fiber Length - SLC20 Singlemode 9/125um 20km Fiber Length - SLC120 Singlemode 9/125um 120km Fiber Length The ODW also supports the option of bidirectional fiber interface modules. These are more expensive options and currently used infrequently and are not discussed/evaluated here. -Powered by 24VAC (48-62hz), or 12 to 48VDC (supporting redundant DC) Power input is isolated from RS485 and Status port signals -RS485 port is isolated from power AND local ground The RS485 will take on the ground reference of the incoming RS485 signals. An oscilloscope examination of the RS485 data pins with no connection to other RS485 devices will show AC voltage on the RS485 pins (leakage to isolated circuit). A scope should only be examined with the RS485 port connected to the CLAN or SubLAN. Please find the attached pdf ODW FOI EVAL 120824.pdf for review. It proceeds through a sequence of differing configurations with the synchronous controller LAN and the asynchronous SubLAN.
View full article
Picard Product_Support
‎2018-09-06 11:50 AM

Labels:
  • TAC INET
2104 Views

Demand Control Information

Issue Demand Control Information Product Line TAC INET Environment I/NET Seven Cause Most issues with demand control will come from improper setup or lack of understanding of demand control processes. Resolution TCON 300 Technical Reference Guide is the best location for version specific information on  Demand Control.  Click here for the demand control sections of TCON 300 from version 2.43
View full article
Picard Product_Support
‎2018-09-06 12:14 PM

Labels:
  • TAC INET
1871 Views

Using either Card or KeyPAD PIN to gain access through door

Notice NOTICE COMPLEX PROCEDURE REQUIRED. The resolution of this article has many complex steps that may result in unforeseen results if not performed correctly. If you are at all unfamiliar with the requirements, please contact Product Support for assistance. Issue Want to access door with 'Card only' or 'PIN only' not both of them.   Product Line TAC INET Environment I/NET Seven Access Cause I/NET has two door mode schedules, Secure, the default setting, which provides access via card number or Secure with PIN, which requires card entry AND a PIN entry.   In this case it is possible to use either card or PIN to gain access if using specialized readers that support a Wiegand PIN output. Resolution It is possible to achieve this provided the PIN output from your card reader supports one of the supported card types of I/NET (i.e. 26-bit, 32-bit Wiegand etc) you can assign a "card number" (PIN) for each individual. The PIN pad will output the entered PIN in Wiegand format and I/NET will then treat it as a normal card entry. Once the PIN pad / card reader has been configured you simply enter this into the Individual editor as the card number card and it acts exactly the same as swiping a card. What this means is that the Individual can use either their card or PIN to gain access (if entered in this fashion). So provided you have a suitable reader / pin pad (such as the P-640 Patagonia Proximity Reader from Keypad Farpointe Data, Inc (www.farpointedata.com))- here are the steps to configure this to work: In the Door editor set the reader type to Wiegand 26-bit (or other) Configure the PIN Type to 26-bit The Door mode is either left blank (Secure mode) or configured as 'Secure' Configure your Tenant (Refer to note below regarding Large Card number usage) Add your individual; The individual will have to have two card numbers associated to them: The number associated to the card, The number associated with the PIN number - what not to get confused with is that this PIN number is NOT the PIN number associated (or shown) in the Individual editor. Large Card number usage: How to calculate the "card number" if using Large Card Numbers: The following two Excel spreadsheet calculators; 26-bit and 32-bit can be used calculate you the large card number. Enter the details (Facility Code / Card number) and the calculator produces the large card number in both decimal and hexadecimal. For example if you use Facility Code 26 and card number 255, the results would be 1704191 (Decimal) and 001A00FF (Hexadecimal). Alternatively I/NET also displays this 'large card' number in the Message column if added to the Transaction window - you can use this also to ensure you have everything wired and configured correctly. How to calculate the "card number" if using the Facility Code / Card number: Once the reader has been programmed with the facility code and this number entered into the Tenant Code of the Tenant editor. The PIN number assigned to the individual then becomes the 'card number’. So for the same example used above, the Facility Code used is 26 and card number 255, the Tenant editor will have the Tenant code configured as 26 and the Individual number (ID) of 255 is used - so no card number is entered into I/NET. This ties the card number to the Individual ID. This is important and the major difference between using large card numbers and facility codes.
View full article
Picard Product_Support
‎2018-09-10 11:31 PM

Labels:
  • TAC INET
2124 Views

I/Disc Part numbers

Issue I need to re-order IDisc Parts for a system Environment Any Windows OS and I/NET Software Cause I need to find the replacement Part Numbers for the Old I/Disc Systems Resolution The I/Disc (silver Disc) and the Plastic Fobs are not available on the Iportal Outside Vendor for the I/Disc Reader and the I/Disc (silver disc) and other accessories Outside Vendor for the I/Disc Wand  Third party vendor website with iButton
View full article
Picard Product_Support
‎2018-09-10 11:11 AM

Labels:
  • TAC INET
2257 Views

Code-Guard Scramble Pin Pad Reader Programming

Issue Code-Guard Pin Pad Reader Programming in I/Net Seven Product Line TAC INET Environment Any Windows OS Version and Any I/Net Seven Version Cause I need to program a "Scramble" Pin Pad Reader made by Code-Guard Resolution Here is a link  to programming the Code-Guard Pin Pad Reader in I/Net
View full article
Picard Product_Support
‎2018-09-10 06:14 AM

Labels:
  • TAC INET
1873 Views

For Belimo Tri-State motors with ASCs

Issue The Actuator is responding as though it is receiving a continuous signal from the ASC. Environment I/NET software all versions I/NET ASC controllers Cause The triac device on these ASCs have a bleed voltage value even though the signal is in the Off mode. Thus causing the motor to drive to one end of the stroke and stop. Resolution See Tech Tip No. G075 which describes a procedure to correct this issue.
View full article
Picard Product_Support
‎2018-09-10 05:12 AM

Labels:
  • TAC INET
1981 Views

Integrate a Datacard (ID Works) Video Badging system together with an existing I/NET Seven system.

Issue Integrate a Datacard (ID Works) Video Badging system together with an existing I/NET Seven system. Environment I/NET Seven ID Works Video Badging software version 6.5 All Windows version that are supported in the current I/NET Version of 2.42 and below Cause I/NET Seven and ID Works need to work as an integrated system. Resolution The attached White paper defines the necessary steps required to modify the ID Works to operate in the I/NET system. Note: if using 64bit OS such as Windows 7, a patch is required which makes ID Works 64bit. It is available from the 3rd party vendor. http://www.datacard.com/id-software-support-and-upgrades/id-works-identification-software
View full article
Picard Product_Support
‎2018-09-10 03:30 AM

Labels:
  • TAC INET
1679 Views

Conversion process for taking small numbers in I/NET Seven to Large numbers in I/NET Seven

Issue Conversion process for taking small numbers in I/NET Seven to Large numbers in I/NET Seven Environment I/NET Seven rev 1.12 and above Cause The card number of the Prox cards are larger than 24000 Resolution Sort the Individuals list according to the Individual Number. Find out the lowest number in the list. In this example number 1 is the lowest card number.   Look at the tenant editor to determine the Tenant Code/Facility code of the cards.   Go into the Door Editor and verify the Bit Format of the Cards. In this case it is a standard 26-Bit Format.   Verify in the door editor that the cards in this system are 26-Bit Wiegand. Then use the attached Excel spreadsheet (This is a ZIP File) to determine the Decimal number of the first card in the system (Card #1 Facility code 199) is 13041665. This number will become the source number in the Key card table.   Create a Key card table like below, using the Source # that was determined in Step #3 above. Please note the Target # must be equal to the value of the Lowest Individual Number.   Next unzip the supplied Windows SQL Script (BigCardConvert.exe). Please note that the SQL Script will ask for a Username and Password. These are the Username and Password used for the SQL in the DbCreate Editor. Once unzipped, double click the “EXE” file and this will convert all the existing card numbers into “Hex” numbers. After this process has completed, verify that the cards did in fact convert OK. Look at the lowest individual number the (“Source” card used the “Hex” and “Decimal” numbers) will be the same values determined in the Excel spread sheet. After verifying that all is OK, then delete the “Card Key Translation” table created to do this process.
View full article
Picard Product_Support
‎2018-09-10 03:12 AM

Labels:
  • TAC INET
1601 Views

Control a door using the "Door Code" feature

Issue Application is to open a door with a PIN Number instead of a card read. Environment I/NET Seven versions 2.4X and above. Cause The Customer is wanting to use a "PIN Only" function at a Pin Pad reader to gain access thru a door Resolution The following document describes the procedure controlling a door using the Door Code Feature. Door Code Setup Procedure.
View full article
Picard Product_Support
‎2018-09-10 03:03 AM

Labels:
  • TAC INET
1536 Views

Program an ADAA Modem for use with I/NET Seven

Issue What is the proper way to program an ADAA Modem for use on an I/NET Seven system? Environment I/NET Seven version 2.01 and above USR 56k Modems Cause Provide an ADAA modem on a site. Resolution Go to the Control Panel of the PC. Select Phone and Modem Options Select the Modem tab and the Properties button. Select the Advanced tab. Under Extra Settings, add the Extra initialization commands: ATZ Choose the Change Default Preferences... button Change the Data Connection Preferences under the General tab to: Port speed: 9600 Data Protocol: Standard ED Compression: Disabled Flow control: None Choose the Advanced tab Change the Hardware Settings to: Data bits: 8 Parity: None Stop bits: 1 Modulation: Standard For 9600 Baud US Robotics 56k Modem Strings, click here For 19200 Baud US Robotics 56k Modem Strings, click here
View full article
Picard Product_Support
‎2018-09-10 03:00 AM

Labels:
  • TAC INET
3742 Views

Custom Audio Files for I/NET Seven AMT

Issue Customize the alarms sounds that are set in the AMT configuration editor. Environment Any I/NET Seven Version Cause Change the default audio alerts for each routine, priority, or critical alarm. Resolution From the task bar, select the Alarms, Messages & Transactions window  Navigate on the menu bar to Edit > Configuration Under Audible alarms, browse to the desired sound file for each priority. If desired, custom alarm sounds are available for download here, (This is a ZIP) file.
View full article
Picard Product_Support
‎2018-09-10 02:12 AM

Labels:
  • TAC INET
1593 Views

Detailed I/NET alarm data in Vista alarm queue

Issue When integrating I/NET into Vista; by default I/NET alarms do not show the station name, link name, or device name (point name). Environment I/NET Seven Vista 4.5 and up Cause The settings on the $AlarmColumns object in Vista do not have the I/NET column fields checked by default. Resolution To customize the Vista alarm queue with the proper fields for I/NET alarms please follow these steps. Click on the root level TAC Vista object in the Vista tree. Right click on the $AlarmColumns object and choose properties. Check the desired boxes in the Columns fields. Note: The link name selection will display the I/NET link name that the alarm originated from. Example: Link 5 South Campus The station name field will display the I/Net station name that the alarm originated from. Example: AHU5 The device name field will display the physical point name programmed within the I/NET controller. Example: OA Damper The site field is only needed when using DLA (distributed link architecture) and will display the name of the DLA site Example: Site 1 North Campus
View full article
Picard Product_Support
‎2018-09-10 01:59 AM

Labels:
  • TAC INET
  • TAC Vista
1200 Views

Barcode Readers

Issue Customers wanting to use a Barcode Reader for door access Environment Access Control site wanting to use Barcode Readers Cause Barcode Readers often are a higher  Resolution I/NET The SCU is the best you could have so that makes it easier with memory requirements and so forth. Since you have the SCU, set it up for 26-bit Wiegand (2 parity bits and 24 data bits). It would look like this: e eeeeeeee eeeeooooooooooooo o That is a 1-bit starting bit, even parity, 8-bit facility code, site number, card number, 16-bit segment, and the 1-bit ending parity (26 bits all together). That is how many data bits the reader normally takes. 26-bit Wiegand is typical and most common. The true bits are the facility code, site and card number. The beginning and end is the parity. For more information, see TCON300, beginning on page 9-59. This is the key card translations section, and may be valuable in figuring out the solution to the bar code reader. Lastly, one idea is to contact a company called RFIDeas.com. They make a bar code reader that may be a solution. If the bar code reader is outputting a card number larger than 16 digits, convert it to 26-bits of Wiegand data (it can handle up to 64-bitWiegand). If it goes over 64-bit, they have a special firmware which allows up to 254 bits of wiegand data. With the SCU, the 26-bit is the standard. Code 128 is used to barcode INET products. The Cypressworld CVX-1300 is an alternate solution for connection between the I/NET SCU and the Barcode Reader. Continuum Code 39 is used to barcode the serial number on Continuum and Pelco boards.  Most readers can auto switch between these and other code types.  
View full article
Picard Product_Support
‎2018-09-10 02:33 AM

Labels:
  • Andover Continuum
  • TAC INET
2008 Views

IDisc Wand is no longer available from Schneider Electric

Issue IDisc Wand is no longer available from Schneider Electric Environment Any I/NET Software Program and Access Control Cause Customer cannot get the IDisc Wand from Schneider Electric Order Entry Resolution There is a third party supplier that handles a direct replacement unit. Click here for a PDF of the part number and cut sheet.
View full article
Picard Product_Support
‎2018-09-10 02:25 AM

Labels:
  • TAC INET
1295 Views

Calculate the memory usage of an MR controller

Issue Calculate the Memory usage of an MR controller Environment MR55 MR88 Any other MR that allows DDC development Cause Since the MRs have a limited memory allocation, you need to determine if you are getting close to the maximum allowed. Resolution Click here to download a zip file of an Excel spreadsheet that will help determine the memory used in the DDC system.
View full article
Picard Product_Support
‎2018-09-06 01:30 PM

Labels:
  • TAC INET
1202 Views

IDISCWAND - Alternative Availability

Issue Trying to find the IDISC Reader Part number IDISCWAND Environment I/NET IDISC Cause The model IDISCWAND tool is no longer an active product with Schneider Electric. Resolution The model IDISCWAND tool is no longer an active product with Schneider Electric. The following information describes how you can acquire the necessary components to form the IDISCWAND. The IDISCWAND is comprised of two component devices as follows - The hand held wand (602063-0002) the hand probe used to contact the IDISC buttons for reading and enrollment of the access control credential into the system. The wand requires an Adapter to allow system communications to the IDISC. The wand can be purchased from Maxim Integrated Products using the Maxim part number DS9092GT#. The second component is the RS232 communications port “Adapter” (602073-0010). The cable from the wand (shown above) plugs into the RJ11 port on the Adapter. The other end of the Adapter is a standard D-subminiature 9-pin RS232 connector. The D-sub end of the Adapter mates with the 9-pin RS232 communications port of the PC workstation (TAC I/NET Seven Host), or the RS232 port created with a USB to Serial port adapter. The Adapter can be purchased from Maxim Integrated Products using the Maxim part number DS9097U-S09#. The “#” symbol at the end of the two part numbers designates RoHS compliance and is the only version currently listed on the web site referenced below. Parts without the “#” would be functionally equivalent. The part number DS9092GT# Wand and DS9097U-S09# Adapter can be purchased from Maxim Direct at - https://www.maximintegrated.com/en.html Enter the part number in the “Price and Availability” search window to see price and lead time on the item, and place an order. View PDF document here.  
View full article
Picard Product_Support
‎2018-09-10 02:19 AM

Labels:
  • TAC INET
1309 Views
  • « Previous
    • 1
    • …
    • 25
    • 26
    • 27
    • …
    • 73
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore