Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

A controller or controllers don't communicate reliably on an I/NET LAN

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • A controller or controllers don't communicate reliably on an I/NET LAN
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RobertAndriolo
    RobertAndriolo
  • sesa139513
    sesa139513
  • Tom_Poovey
    Tom_Poovey
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1203 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

A controller or controllers don't communicate reliably on an I/NET LAN

Picard Product_Support
‎2018-09-06 03:07 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2020-04-22 06:01 PM

Issue

A controller or controllers don't communicate reliably on an I/NET LAN, often somewhere in the middle of the network.

Product Line

TAC INET

Environment

I/NET Site

Cause

As the signal travels down the cable it is affected the "characteristic impedance" at a relatively constant amount. As the signal approaches the end of the network, that impedance increases to completely "open" at the end. According to Ohms law, the higher the resistance/impedance, the higher the voltage will be as the current is applied. Therefore the signal will gain enough energy to be reflected back up the cable as noise. The controller(s) that is (are) most affected are located at the point where the reflection from the end of the network arrive during the original signal.

Resolution

Placing a 120 - 180 OHM 1/2 Watt Resistor at both the physical ends of the Controller LAN will clamp those reflections since the resistor is fairly close to the characteristic impedance of most cables.

The Sub-LAN works differently than the Controller LAN, so DO NOT use a 120 - 180 OHM resistor on the Sub-LAN. Instead, use a 620 OHM resistor placed at both physical ends of the Sub-LAN.

The reason for this is that if you use a 120 - 180 OHM resistor at each end of the Sub-LAN wiring, you remove the bias needed by the "Mark-Space" signal on the Sub-LAN. The 620 OHM resistor is large enough to absorb some of the noise without messing with the Comm. However, you might notice a slight decrease in signal strength.

Also, refer to the article I/NET Controller LAN (C-LAN) Requirements for additional details. 

Labels (1)
Labels:
  • TAC INET
Tags (2)
  • Find more articles tagged with:
  • 1968
  • RobertAndriolo20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore