INET DPU/SCU Transition Architecture - Controller LAN

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • INET DPU/SCU Transition Architecture - Controller LAN
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • AdamSteele
    AdamSteele
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1832 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

INET DPU/SCU Transition Architecture - Controller LAN

Guinan RobertAndriolo Guinan
‎2020-07-12 04:42 PM

Last Updated: Kirk AdamSteele Kirk ‎2020-07-15 04:24 AM

Issue

Sales literature shows the use of NV202, are these the only supported device and are these provided by Schneider 

INET- TransitionArchitecture_ppt.png

Product Line

TAC INET, Security Expert

Environment

  • Security Expert SP-C
  • I/NET Access Control Hardware  

Cause

The NetSys NV202 product was sourced to provide a solution for a large I/NET Site that had multiple 7798B / 7798C controllers communicating back to a single Xenta 527.  As these I/NET Controller LAN devices only communicate via RS-485, a method of using this existing RS-485 cabling to support the SP-C Ethernet connection needed to be sourced.  Tests were carried out to see their performance, which is provided in the resolution below. 

These devices are provided by NetSys and if necessary should be purchased directly through their distribution centers.  Documentation for this device is also provided on their website. 

Resolution

The following shows the tests, methods, and results performed with the NetSys NV-202 on a transition I/NET Database with over 25,000 users and over 5,000 doors.


Testing and Validation of proposed NV-202 based RS485 Network Replacement Solution

Test Equipment

  • 49 Netsys NV-202 devices and power supplies
  • 25 SP-C Controllers
  • Security Expert Software 4.2.251.19 installation on a PC with the following specification:
    • Processor Intel(R) Core(TM) i7-3820 CPU @ 3.60GHz
    • Installed RAM 16.0 GB
  • 240m Belden 9842 Twisted Pair cable PLUS 50 Ohm resistances for line length simulation to an equivalent run length of 840m
  • 100Mbps switch for interconnection of server PC and controller LAN

Test Scenario
30 NV-202 units and in the following network topology.

Figure 1: Test System TopologyFigure 1: Test System Topology
Method

  1. The Security Expert server was loaded with a database backup from an I/NET Transitioned Site, which was then modified to include:
    1. Connection to the SP-C’s on the IP range 192.168.1.200-192.168.1.224. by modifying existing real-world controller records to match (Database ID’s 149 onwards)
    2. Increasing the record load on each controller to the full set of users in the database (21,522) to be downloaded by adding an Access Level containing a door on each controller to each User
    3. A Status Page containing an All Events window
  2. All controllers were connected to the same 100Mbps switch as the test PC containing Security Expert
    1. The last controller in the daisy chain had one input wired into Relay 1 of the controller; this was used to validate input change timing.
  3. Download was forced to all controllers
  4. Timing for each required parameter (as noted in Figure 2) was measured using the final controller at the end of the cable run, having worst-case characteristics of bandwidth/latency due to maximum number of daisy-chained NV-202 devices
    Figure 2: Tested Timing ParametersFigure 2: Tested Timing Parameters

Results

  1. Command Response Time
    Manual commands (by right-clicking and selecting ‘Unlock Door’) were performed on the first door programmed on the SP-C. 25 activations were run and the worst-case results selected.
    Command response time is less than 2 seconds as stipulated. See Wireshark capture:
    Figure 3: Packet capture of a Manual Door Unlock command to the worst-case SP-C from Security Expert SoftwareFigure 3: Packet capture of a Manual Door Unlock command to the worst-case SP-C from Security Expert Software
  2. Status Changes Response Time
    Relay 1 of the SP-C was activated, which is wired to Input 1 of the same SP-C in order to close the input and trigger a status change. 25 activations were run and the worst-case results selected.
    Status Change response is less than 1 second stipulated.
  3. Door Status Changes response time
    Manual commands (by right-clicking and selecting ‘Unlock Door’) were performed on the first door programmed on the SP-C. 25 activations were run and the worst-case results selected.
    Door status change response is less than 1 second stipulated.
  4. Retrieve access data or user’s data
    Not applicable. This data is stored in the server database.
  5. Generate any single ad-hoc reports
    Not applicable, reports are generated by the server using data from the server database.
  6. Multiple access control levels
    Not Applicable to this test - Security Expert can store unlimited Access Levels, and associate any of them to a given User. Access Level/User quantity limitations are not affected by the NV-202.
  7. EOD download time:
    A Force Download operation was performed on the SP-C, and the time to completion recorded. 25 activations were run and the worst-case results selected.
    Maximum download time: 58 seconds per controller (noting 21,522 Users)
  8. Time synchronization – maintain synchronism
    Time update packets are successfully sent, Server and controller time maintained within 1 second.
  9. Time synchronization – accuracy
    Not Applicable to this test – time is updated periodically (not constantly) so not significantly affected by bandwidth or latency.
Labels (2)
Labels:
  • EcoStruxure Security Expert
  • TAC INET
Tags (1)
  • Find more articles tagged with:
  • RobertAndriolo20
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of