What are the specifications for using a synchronous (Hayes) external modem in relation to I/NET Dial Applications?

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • What are the specifications for using a synchronous (Hayes) external modem in relation to I/NET Dial Applications?
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • RobertAndriolo
    RobertAndriolo

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2275 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

What are the specifications for using a synchronous (Hayes) external modem in relation to I/NET Dial Applications?

Picard Product_Support
‎2018-09-06 09:45 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2020-08-13 09:07 PM

Issue

What are the specifications for using a synchronous (Hayes) external modem in relation to I/NET Dial Applications?

Product Line

TAC INET

Environment

  • Synchronous (Hayes) external modem
  • I/NET Dial Applications

Cause

Dial up I/NET applications

Resolution

See TCON101, TCON213, TCON226 and TCON298 for more details

  1. PC, modem, and phone line must be connected and “ON”.
    • To program a modem, the modem must be direct connected to the PC
    • Connect the modem to an analog phone line only.
    • Remember the host needs a 78041 or a 78051 tap (not Embedded 4x)
    • Warning! Using a non-analog line will damage the modem!
       
  2. Make sure the correct modem driver is installed.
    • Add the modem hardware in Windows Control Panel
    • In the “Phone And Modem Options” editor, go to the “Modems” tab
    • Remove any profiles of modems that are not currently connected to the INET comm port.
    • If you are running Windows 2000, the “Microsoft H.323 TAPI Service Provider” should be the telephony provider highlighted under the “Advanced” tab, in the Phone And Modem Options Editor of Windows 2K Control Panel.
    • From the “Modems” tab, go to Properties / Diagnostics / and Query Modem. Go to Modems / Properties / General, and set the Maximum Port Speed at 9600.
    • Close Windows Control Panel
       
  3. View the modem’s Active and Stored settings:
    • Type “ATE1” to place echo to “On” mode
    • “AT&V” followed by the “Enter” key displays the settings the modem is using and the NOVRAM settings in profile “&Y0” and  &Y1
    • If the settings need to be changed then continue
    • Recommend “AT&F” to reset the modem to factory defaults.
    • The Host and Site modems use the same settings.
    • Both modems should be as follows:

      Active Profile: B1 B16 B30 B41 B52 B60 B70 B75 B80 E1 L2 M1 N0 P Q0 V0 W0 X4 Y0 &A0 &B1 &C1 &D3 &G0 &K3 &L0 &Q1 &R0 &S1 &T4 &U0 &X0 &Y0               S00:001 S02:043 S03:013 S04:010 S05:008 S06:002 S07:060 S08:002 S09:006 S10:014 S11:095 S12:050 S25:005 S26:001 S36:001 S37:009 S38:020 S46:002 S48:007
       
  4. Suggest you store the settings in both profiles of the modem’s NOVRAM.
    • “&W0” stores to “&Y0”
    • “&W1” stores to “&Y1”
       
  5. TAPs : EPROM(s) and BIN files need to be synchronous and INET rev compatible
     
  6. After following the preceding steps for the remote site’s modem:
    • Connect the modem to the Tap (or emulated Tap) and Analog Phone Line
    • Power-up the modem
    • Press the controller’s reset button or cycle the Tap’s power
    • Do NOT cycle the modem’s power
    • The “RD” and “SD” should flash after several seconds have past
    • After about 30 seconds the  “MR”, “AA”, and “TR” lights should be “On”
       
  7. Using I/NET, Dial the site. Make sure the host can:
    • Dial out (you can here the dial tone)
    • Handshake with the remote Modem
    • Maintain its connection to the remote modem (Neither modem inadvertently terminates call)
    • See the Controller(s) on the LAN
    • Actually connect to the controller(s)
    • View points in the summary screens

Warning! Using a non-analog line will damage the modem!

For Asynchronous ADAA, click here

Labels (1)
Labels:
  • TAC INET
Attachments
Tags (2)
  • Find more articles tagged with:
  • 984
  • RobertAndriolo20
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of