I/NET Controller LAN (C-LAN) Requirements
  • I/NET Controller LAN (C-LAN) Requirements
  • RobertAndriolo
    RobertAndriolo
‎2018-09-06 03:21 PM
Last Updated: Picard RobertAndriolo Picard ‎2020-04-22 05:59 PM
  • What are the cable requirements?
  • What is the maximum wire length?
  • When do I add a repeater?
  • What is the maximum number of repeaters allowed?
TAC INET
I/NET Controller LAN, C-LAN
Incorrectly run controller LAN wire can cause communication issues between I/NET controllers and hosts.
  • C-LAN should be run using:
    • Two wire, twisted pair, shielded cable
    • 24 AWG (0.206 mm2) or larger
    • 30 pF/ft. or less between conductors
    • 55 pF/ft. or less conductor to shield
    • 80 - 150 ohm impedance
  • The maximum controller LAN length is 25,000 feet (7,620 meters) assuming 4 repeaters are used.
  • A repeater should be installed:
    • To segment every 32 controllers
    • Or if the LAN length exceeds 5,000 feet (1,524 meters).
  • The maximum number of repeaters allowed is 4.