Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,838
  • TAC IA Series 1,821
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Advisor 12
  • EcoStruxure Building Activate 11
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 507
  • Next »

A curve block will not work as expected in a Menta application

Issue Even though the curve block is set to range between 0-100, the block just stays at a fixed output somewhere in the curve output range. Product Line TAC Vista Environment Vista Workstation Cause The curve requires the first entry of the X value to be the lowest value, and then the subsequent values to be larger than the previous X entry. Resolution Adjust the order of the XY entries on the curve block so the first entry in the X will be the lowest value. Example of Incorrect Curve Here is an example of a Curve that will not work. Note the first X entry is -2 and the last X entry is -6.  Example of Correct Curve To correct this curve, -6 is the lower number, so this should be the first X entry. Here is an example of the curve that has the correct X entry order.
View full article
Picard Product_Support
‎2018-09-07 02:29 PM

Last Updated: Spock PeterLarsen Spock ‎2025-05-05 05:45 PM

Labels:
  • EcoStruxure Building Operation
  • TAC Vista
1633 Views

Esmi Ultima Networking Troubleshooting

Warning Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.   Note: Always completely power OFF the panel whenever inserting or removing hardware in the panel. Issue Not able to see the network panels status, trouble messages, events, cause and effects etc. Product Line ESMI Fire Detection. Environment FFSULH1009. Cause Networking issues can significantly impact the performance and reliability of the Esmi Ultima system. This article provides troubleshooting steps to resolve common networking problems. Resolution The following network-related troubles can occur on the Esmi Ultima Fire Alarm Control Panel. See the detailed descriptions below for explanations on each trouble message.   Trouble Message Description Network Communications Trouble This event indicates there is no communication between this panel and its neighbor. This could be caused by a configuration error (such as using the wrong baud rate), a wiring error, or damage to the wires connecting the panel to its neighbor. If this trouble occurs on one link on the panel, then the panel is still in communication with other panels on the network. If this trouble occurs on both links on the panel, then the panel is no longer in communication with other panels on the network. Note: make sure remove the 0 ohm resistance from the network card. Unexpected Network Node This event indicates a panel has been detected on the network that is not in the configuration. This is a configuration error and should never occur once the network has been properly configured. Network Card Missing This event indicates that the panel is configured for networking, but there is no network card installed, or it is installed incorrectly. This trouble may also occur if the network card processor fails. Connection Error This event indicates that the panel has failed to get a meaningful result for the link impedance measurement. This may occur if stray leakage current enters the link wiring from elsewhere, or if there is a component failure or missing jumper on the network card. This event may also be shown when the network is disconnected or when the NET OUT + wire is disconnected. Network Panel Missing This event indicates that another panel is configured but has not been found on the network. This may occur if the missing panel is switched off or disconnected from the network. This fault will also occur if there is no communication between a panel and either of its neighbors on both links. In this case, the panel will show multiple instances of this trouble; one for each other panel on the network. Network Node Double Addressed This event indicates that more than one panel on the network has the same node number. This is a configuration error and should never occur once the network has been properly configured. Full Short Circuit Trouble This event indicates that a short circuit has been detected by the link impedance measurement. This indicates a wiring error, or damage to the wires connecting the panel to its neighbor. Full Open Circuit Trouble This event indicates that an open circuit has been detected by the link impedance measurement. This indicates a wiring error, or damage to the wires connecting the panel to its neighbor. The following two troubles are optional and are not included in the default firmware build. Partial Short Circuit Trouble This event indicates that the link impedance measurement has detected an impedance below the normally expected range. Partial Open Circuit Trouble This event indicates that the link impedance measurement has detected an impedance above the normally expected range.
View full article
Crewman Sandeep_Kumar006 Crewman
‎2025-05-05 05:54 PM

on ‎2025-05-05 05:54 PM

Labels:
  • ESMI Fire Detection
80 Views

Controller Health Status shows Ring-loop failure message

  Issue After transitioning TAC INET Access to Security Expert, SP-C health status shows the message "Ring-loop failure at reader expander".   Product Line EcoStruxure Security Expert, TAC INET Environment  Security Expert SP-C   TAC INET Access Control Cause This message indicates that the ring-loop connection is not made.  For the ring-loop connection, the opposite end of the INET subLAN must be connected to Reader 2 on the SP-C. Resolution This message can be ignored if an INET subLAN loop is not used. The Ring-loop Failure error can be avoided by running a jumper wire from Reader 1 pin D0 to Reader 2 pin D0, and another jumper wire from Reader 1 pin D1 to Reader 2 pin D1 on the SP-C that is hosting the INET subLAN If an INET subLAN loop is used, this message indicates a break in the ring loop.    Reference Guide I/NET Access Control Transition to EcoStruxure™ Security Expert (Hardware            Guidelines for Transitioning from I/NET Page 23)
View full article
Commander Hernan_Urueña Commander
‎2023-02-28 07:21 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2025-05-05 05:52 PM

Labels:
  • EcoStruxure Security Expert
  • TAC INET
977 Views

Esmi Ultima Network Card LED Status

Warning Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices. Issue Having issues with the panel's networking and unable to operate the touch screen or receive trouble messages on the screen. Product Line ESMI Fire Detection. Environment FFSULH1009. Cause The display touch screen may not be working. Resolution You can identify the current situation by checking the LED status as described below:    LED Status LED indicators provide diagnostic information to identify communication.   LED Label  Name  Color  Description LED 1 Heartbeat Red Identifies functional status. LED 2 Tx Comms Green A blinking green light indicates that the module is transmitting data. LED 3 Rx Comms Green A blinking green light indicates that the module is receiving data. LED 4 Trouble Yellow A flashing yellow light identifies an error condition. LED 5 Not In Use Green Not In Use LED 6 Not In Use Green Not In Use LED 7 Not In Use Yellow Not In Use LED 8 Comms for SPI Bus Green Communication present when flashing LED 9 Full Duplex Yellow Full duplex (on) half duplex (off) LED 10 Ethernet Speed Red 10MHz (off), 100MHz (on) LED 12 Communication Green Communication present when flashing   Refer to ESMI Ultima Networking Troubleshooting for further assistance with network related problems
View full article
Crewman Sandeep_Kumar006 Crewman
‎2025-05-05 05:42 PM

on ‎2025-05-05 05:42 PM

Labels:
  • ESMI Fire Detection
82 Views

How to move Infinet devices from one port to another in the same Automation Server

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue It is sometimes necessary to move a previously configured Infinet i2 device from one Infinet network to another in the same parent Automation Server. EcoStruxure Building Operation does not provide an automatic way to move an i2 device; it must be done manually. Product Line  EcoStruxure Building Operation Environment Building Operation Automation Server Cause Guidance on steps to move Infinet i2 device from one Infinet network to another in the same host Automation Server Resolution In this example, we are going to move multiple Infinet i2 devices from the Infinet network on COM-A to the Infinet network on COM-B.   Backup Make sure to make a backup of the Automation Server before attempting the steps below. This is in case there is a need to revert the changes for whatever reasons. Export Devices from COM-A From COM-A Infinet network, display a List View of the devices, making sure to have columns displaying the Infinet ID and Serial Number. Write down the Infinet IDs and Serial Numbers of the devices to be moved. In the List View, multi-select the devices to be moved, right click and perform an 'Export', leave the Export Reference Filter at default (Export). After successful export, right click on the selected devices again and delete them from COM-A Infinet network. Prepare COM-B for Import From COM-B Infinet network, display a List View of the devices, making sure to have columns for Infinet ID and Serial Number. Observe the Infinet ID column, and compare with the notes taken above of the moving devices' Infinet ID, for IDs that are already in use in COM-B, you will need to assign a new ID to the device moving from COM-A Infinet network to COM-B, update your notes to include an available ID on COM-B. (see example below of what the notes might look like)   Import Devices to COM-B ***  In the System Tree, select the COM-B Infinet network and perform an import of the XML file created via export above. Physically move the devices from COM-A Infinet to COM-B Infinet. When doing so, avoid introducing duplicated Infinet IDs into COM-B Infinet. Make sure to power down the devices you are moving, connect them to COM-B Infinet, and only then power up the devices. On power up, the devices perform an ID check and stay off the bus if they detect their IDs are already in use. Configure Devices in COM-B From COM-B Infinet network, display a List View of the devices making sure to have columns for Infinet ID and Serial Number. Right click each device moved from COM-A Infinet to COM-B Infinet, and select "Properties", in the "Advanced" tab, enter the appropriate Infinet ID and Serial Number for the device then click "OK". In the List View, right click the device from previous step again, select "Device->Commission", after successful commission the device should go ONLINE Final Steps After all the moved devices are online, you should download ALL (whether moved or not) the devices to have their programs recompile and rebuild their Import/Export tables. Fix any references that were lost due to devices changing Infinet network and Infinet ID *** NOTE Due to an issue that was corrected in EBO 6.x, import may fail with error "Invalid InfinetId", the workaround for this problem is to manually create the Infinet devices on the destination port using the appropriate name, serial number and Infinet ID, then do the import selecting the option to merge on conflict.
View full article
Captain AbeMeran Captain
‎2025-04-15 04:55 PM

Last Updated: Administrator CraigEl Administrator ‎2025-05-05 04:22 PM

Labels:
  • EcoStruxure Building Operation
226 Views

Esmi Ultima Touch Screen Calibration

Warning Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices.   Issue If you are having trouble with the screen operation, you may need to re-calibrate the touch screen. Product Line ESMI Fire Detection. Environment FFSULH1001. FFSULH1002. FFSULH1003. Cause During shipping, the touch screen calibration may become misaligned. Resolution To calibrate the touch screen, do the following: Hold down the function button on the back of the main PCB and press and release the reset button, continue to hold down the function button firmly until the calibration screen appears this can take up to a minute Once the calibration screen has appeared you will be prompt with 5 crosshairs which you must press in turn. Note: Please note when pressing these crosshairs ensure you use your hand as it has been known to cause issues using tools or stationery as pointers
View full article
Crewman Sandeep_Kumar006 Crewman
‎2024-11-20 07:42 PM

Labels:
  • ESMI Fire Detection
320 Views

Error 'Domain Controller version too low' encountered when logging into an AS-P

Issue It is not possible to login to an Automation Server and it fails with the error "Domain Controller version too low' for certain users. Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Cause Remnants of an EcoStruxure Building Operation domain exist in the controller where it has not been removed completely and it is set as the Default Logon Domain. Resolution Login with Administrative Rights: Use a user account with Administrative rights in the Local or another domain explicitly using the Domain name. Delete Partial Domain: Once successfully logged in, delete the offending partial domain. Retry Login: Attempt to log in again. Additional Information: Ensure that the domain is completely removed to avoid future login issues. Verify that the Default Logon Domain is correctly set after removing the partial domain.
View full article
Admiral GavinHe Admiral
‎2025-05-02 07:50 PM

on ‎2025-05-02 07:50 PM

Labels:
  • EcoStruxure Building Operation
93 Views

Protocol Used for SNMP Traps in EcoStruxure Building Operation

Issue Are SNMP traps in StruxureWare Building Operation sent using UDP or TCP? Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause Simple Network Management Protocol (SNMP) is an Internet-standard protocol for managing devices on IP networks. Need to know if SNMP messages are sent over TCP or UDP. Resolution SNMP traps in EcoStruxure Building Operation are sent using the UDP protocol.   Additional Information: UDP (User Datagram Protocol) is a connectionless protocol that allows for low-latency communication, making it suitable for SNMP traps which require quick delivery without the overhead of establishing a connection. TCP (Transmission Control Protocol), on the other hand, is connection-oriented and ensures reliable delivery of packets, but it is not used for SNMP traps in this context.
View full article
Picard Product_Support
‎2018-09-06 09:02 AM

Last Updated: Administrator CraigEl Administrator ‎2025-05-02 07:41 PM

Labels:
  • EcoStruxure Building Operation
1266 Views

Port logging functionality to log BACnet MS/TP traffic

Issue Need to use the Automation Server port log to view BACnet MS/TP communication Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause Need to capture BACnet MS/TP traffic for troubleshooting. Resolution In EBO 2024 (V6.0) and higher, there is an integrated packet capture feature available in EBO Servers with BACnet Interfaces. This feature allows users to create packet captures that record the BACnet messages that are visible to the EBO Server’s BACnet/IP and BACnet MS/TP networks. Refer to: Packet Captures in EcoStruxure Building Operation
View full article
Picard Product_Support
‎2018-09-06 08:43 AM

Last Updated: Kirk Mahmoud_Sayed Kirk ‎2025-05-02 02:09 AM

Labels:
  • EcoStruxure Building Operation
1654 Views

Capture a SEAL log

  Issue How can I troubleshoot communication issues between SEAL app and EBO server? Does the SEAL app provide a detailed log for troubleshooting communication issues between the app and the EBO server? Product Line EcoStruxure Building Operation Environment Building Operation Automation Server Building Operation Enterprise Server Ecostruxure SEAL Cause When troubleshooting SEAL communications issues to an EBO server, it may be helpful to get deeper information about the communication between the server and the SEAL application. To do this the following lines can be added to the appsettings.json application settings file as described below in the resolution Resolution Browse to C:\Program Files\Schneider Electric\SEAL Open the file appsettings.json. Depending on your user rights, you may need to copy and edit this file in another folder Go to line 26. After the closing brace }, enter a comma ,  Paste the following: "Serilog": { "Using": [ "Serilog.Sinks.File" ], "MinimumLevel": { "Default": "Information", "Override": { "Microsoft": "Warning", "Microsoft.Hosting.Lifetime": "Information", "SE.SEAL": "Debug", "SE.SEAL.Web.Auth": "Verbose" } }, "WriteTo": [ { "Name": "File", "Args": { "path": "%LOCALAPPDATA%/SEAL/logs/SEAL.txt", "rollingInterval": "Day", "shared": true } } ], "Enrich": [ "FromLogContext" ] }   Save the file. Try logging into the SEAL app and connecting to the EBO server Save the log found under: %LOCALAPPDATA%/SEAL/logs/SEAL.txt Restore the appsettings.json file to its original state.   Attached to this article is a ready-made file for use. Move the original file to another folder Place the attached file in C:\Program Files\Schneider Electric\SEAL After saving the logs, delete the attached file Move the original file back to its original location   In addition to this, it is always recommended to take an event view - Application log
View full article
Lieutenant Katha Lieutenant
‎2025-04-24 04:47 AM

Labels:
  • EcoStruxure Building Operation
144 Views

Adding LoytecSrv (Loytec NIC) as a dependency to Enterprise Server

Issue Configured Loytec LConfig application as a service but still do not get communication from the LonWorks Network. Not able to get Service pin from LON devices connected with Loytec NIC from Enterprise Server Product Line EcoStruxure Building Operation Environment Enterprise Server 1.1 Loytec NIC852 (LConfig Tool) Windows 7 Cause LConfig tool version is too old. The LConfig tool, even if set to start as a service, also still needs to start before the Enterprise Server (ES), otherwise the Enterprise Server fails to establish its connection with the LonWorks interface. For information on how to set LConfig to run as a service refer to Not able to get Service pin from LON devices connected with Loytec NIC from ES. Resolution To rectify the cause 1, click here to verify if the LConfig version is the most recent one. If not please download the most recent NIC - LOYTEC Network Interface Software. To rectify the cause 2, you must set the Loytec (LConfig) application service to be a dependency of the Enterprise Server (ES), to do this follow these instructions: Using RegEdit (or similar) edit the Registry Key: HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\services\StruxureWare 1.1 Enterprise Server NOTE: For SmartStruxure version 1.3 and above, go to path: HKEY_LOCAL_MACHINE\SYSTEM\CurrentControlSet\services\Building Operation 1.3 Enterprise Server Locate and edit the DependOnService string Add the text LoytecSrv (service name for the LConfig application). Close the editor and reboot the PC Note: When running the LConfig as a service the LConfig Tool is not available from the System Tray and must be started from the program shortcut, located under Start > Programs> LOYTEC Network Interfaces> LConfig As a quick visual check, to see if configured correctly, you can perform a LonWorks Device Discovery on your Enterprise Server, this will show the NIC which has been defined with a red box (see image below). If these are all blue then you will not be able to receive any communications from your devices. Also remember if using the Loytec LIP devices that these should be configured in Smart Mode.
View full article
Picard Product_Support
‎2018-09-10 10:57 AM

Last Updated: Guinan RandyDavis Guinan ‎2025-04-22 06:40 AM

Labels:
  • EcoStruxure Building Operation
2044 Views

Capture a Smart Connector trace log in EBO/SBO

  Issue How can I troubleshoot a communication issue with the Smart Connector. Is there a log available within the AS or ES that shows the Smart Connector communication. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server Building Operation Enterprise Server Cause When troubleshooting Smart Connector issues in an AS or ES it can be helpful to see the communication between the Server and the Smart Connector device to help identify this issue. The trace log within both server types is available and is configured as described below in the resolution. Resolution Open Workstation and navigate to [AS/ES name]/System/Modules/Trace/Loggers/nsp/nsp.csc/nsp.csc.CWSServer. Right-click "nsp.csc.CWSServer" and choose Properties. Under Level, change from "Information" to "Trace", then click ok. Let it run a few minutes. If there are some user input needed to recreate the Smart Connector issue, then perform these steps now. Retrieve the log by right-clicking [AS/ES name]/System/Modules/Trace/TraceSettings and choose Trace settings->Get trace log.  Save the log file. Once debugging is complete remember to change log level back to "Information" (reverse of step 3). Note: If the ES or AS is reset, i.e. cold started or warm started, the log level will return to 'Information', so if further increased logging is required, the procedure will need to be repeated. Note2: This option is only availabe for EBO version 6.02 and onwards
View full article
Spock PeterLarsen Spock
‎2025-04-16 07:59 AM

on ‎2025-04-16 07:59 AM

Labels:
  • EcoStruxure Building Operation
819 Views

Recover an I/NET Controller's DCU Password

Issue I have an I/NET Controller with a forgotten DCU password. How can I recover it? Product Line TAC INET Environment I/NET Seven Site Cause A DCU password was set on the I/NET Controller and has been forgotten. Resolution Send an email to your local support. Include a copy of the current save file for the controller in question. Support will advise you on the password. Recommendation: For future use, either remove any controller passwords or record them in a secure location where they can be retrieved easily.
View full article
Picard Product_Support
‎2018-09-06 03:09 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2025-04-15 11:14 PM

Labels:
  • TAC INET
2360 Views

Required firewall exceptions for EcoStruxure Building Activate and Flex Server.

Issue There is a need to identify the Ports, URLs and Static IPs which must be open through customer's firewall for EcoStruxure Building Activate Flex Server and Partner Portal Product Line EcoStruxure Building Activate Environment EcoStruxure Building Activate Flex Server EcoStruxure Building Activate Partner Portal Cause Ports, URLs and Static IPs list needed to create firewall exceptions for EcoStruxure Building Activate Flex Server and Partner Portal in order to keep them functioning correctly. Resolution Below are the list of ports, URLs and static IPs that must be open through a site's firewall/network: URL Port Protocol Usage https://sentry.zenatix.com 443 TCP Allows the gateway to upload error logs and diagnostics. https://router.zenatix.com 443 TCP Allows the gateway to download Linux & Python updates from the Zenatix Server. Regularly polls the Zenatix Server to check internet connectivity. https://timesync.zenatix.com 9090 TCP Time server allows the gateway system & gateway clock to remain synchronized with Zenatix Server. https://gitlab.zenatix.com 443 TCP Used for troubleshooting to update the gateway codebase from the Zenatix Server. https://telemetry.zenatix.com 443 TCP Used for sending IoT device data and gateway health data to the Zenatix Server. https://emgx.zenatix.com 8883 TCP Used for communication between gateways and Zenatix cloud services for getting configuration or alarms from Zenatix Server to gateway and vice versa. 54.169.200.193 1194 UDP Allows Zenatix to remotely access and do API calls to the gateway through OpenVPN. https://mender.zenatix.com 443 TCP Used to download firmware updates to gateway from Zenatix Server.  
View full article
Ensign Mukesh_Sangwan Ensign
‎2025-04-15 05:12 PM

Last Updated: Administrator CraigEl Administrator ‎2025-04-15 05:25 PM

Labels:
  • EcoStruxure Building Activate
235 Views

EBO Cloud Connectivity Certificate Errors

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Validation of SSL Certificate does not work Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Enterprise Central Building Operation Space-Logic Server (AS-X) Cause Cloud Connectivity makes use of the Baltimore CyberTrust Root Certificate for communication to the cloud, and often this certificate is not updated due to lack of maintenance routines on the Windows Server. Resolution Run Windows Update: On the server running the ES/EC, run Windows Update and make sure the Operating System is updated to the latest maintenance version available. Manually update certificate:  On the server running the ES/EC, go to https://curl.se/docs/caextract.html using a web browser and follow the instructions to download a collection of the most commonly used certificates on the web that are up to date. Click on the start-menu, type in ”certmgr” and press enter. Navigate to Trusted Root Certification Authorities/Certificates Under Trusted Root Certification Authorities, right-click the Certificates folder and select ”All Tasks > Import…” Follow the guide, click ”Next” and then locate the file you downloaded in Step 2a (make sure you filter to All Files). Click ”Next” on all steps and then click ”Finish”.
View full article
Lieutenant JG LocNguyen Lieutenant JG
‎2025-04-15 04:35 PM

on ‎2025-04-15 04:35 PM

Labels:
  • EcoStruxure Building Advisor
  • EcoStruxure Building Expert
  • EcoStruxure for Retail - IMP
218 Views

Mixing Low and High voltage on same side of an CRS-HH-REL-10

Warning Hazard of Electric Shock: Remove all power from all devices before removing any covers or doors of the system. Disconnect power at the device and at the power source. Electrostatic Discharge Required: Always discharge static electricity from your person by touching metal prior to handling any hardware. Failure to do so may result in damage to devices. Issue Why is it recommended to not mix high and low voltage connections on the same side of an CRS-HH-REL-10? Product Line EcoStruxure Building Operation. Environment Building Operation Room Controller (RPC) 24 V Building Operation Room Controller (RPC) 230 V Cause According to the documentation, it is not recommended to mix high and low voltage connections on the same side of the device.   Resolution There must be a minimum distance between terminals connected to High Voltage and terminals connected to Low Voltage of at least 5.5 mm to prevent the chance of voltage creep between the terminals.
View full article
Kirk MikaelKrantz Kirk
‎2025-04-14 04:20 PM

on ‎2025-04-14 04:20 PM

Labels:
  • EcoStruxure Building Operation
235 Views

Unable to add an Automation Server underneath an Enterprise Server

Issue One of the following error messages are displayed. Internal server error Server already part of a system Product Line EcoStruxure Building Operation Environment Building Operation WorkStation Building Operation Server Cause Version Mismatch: The Automation Server is either not the same version as the Enterprise Server or it is still connected to a different Enterprise Server. If the Automation Server is still connected to another Enterprise Server then it must be detached before it can be added underneath a new Enterprise Server. User Permissions: In some instances, the User Permissions "System Address" is not added to the user account that is attempting to add the server.    Resolution If you are given an error that states "Domain: Internal Server Error" then you need to download the same version of firmware to the AS that is installed on the ES. Resolution #1: Detach the Automation Server Log in to the Automation Server.   In the system tree pane, right-click on the automation server and go to Advanced > Detach server.   The Disconnect Automation Server window will open; click yes.   The Automation Server is now detached and can be added to an Enterprise Server. Resolution #2: Verify User Permissions Check a current backup using the SBO xbk Analyzer and verify the number of servers listed under Reports>Servers Log on using the default admin account and see if these servers exist. Detach the server(s), as described above. If the secondary user still requires permission to add and see ALL servers: Go to the user and select the Permissions tab Ensure the ES path is selected Click on the Add System button (identified with the arrow) Enable all options to allow read/write, create etc.  Save these changes and log off and back on with this user to see the changes. This user should now be able to add/see ALL servers.
View full article
Picard Product_Support
‎2018-09-06 12:09 PM

Last Updated: Administrator CraigEl Administrator ‎2025-04-09 08:22 PM

Labels:
  • EcoStruxure Building Operation
6717 Views

AS-P, CPU Temperature

Issue What temperature limit should the CPU Temperature stay within? Product Line EcoStruxure Building Operation. Environment Building Operation Automation Server Premium Building Operation Automation Server Bundled Cause From EBO version 3.2, the CPU Temperature is added. Resolution The CPU temperature parameter displayed in the UI property dialog Automation Server Properties – Basic Tab is intended for internal debugging purposes only. Users are not required to monitor or take action based on this value, as there is no specified maximum CPU temperature level that requires user intervention or indicates potential CPU performance degradation.  
View full article
Kirk MikaelKrantz Kirk
‎2025-04-09 05:59 AM

on ‎2025-04-09 05:59 AM

Labels:
  • EcoStruxure Building Operation
259 Views

Considerations restoring an AS-P backup using PCT

Issue The instance values the Function Block program had when the backup was taken is lost when the backup is restored in an AS-P running in PCT. Product Line EcoStruxure Building Operation Environment Building Operation Project Configuration Tool (PCT) Cause When the program is first initiated, the values for it is written to the database. If the “Program executions” Is turned off, the instance values the program had when the backup was taken is not read. Hence the values are set to 0.   On a real AS-P, a Cold start is performed after the restoring of the backup. When restoring a backup on an AS-P in PCT, one or two cold starts are done, followed by an additional warm start at least for the PCT 2. Resolution To get the instance values from the backup when it is restored, the “Program execution”/”Enable program” In PCT should be turned on before the restore is done.   Since a warm start is done for the PCT, the issue regarding Retain level vs. FB Backup property needs to be taken into consideration. https://ecostruxure-building-help.se.com/bms/Topics/show.castle?id=15741&locale=sv-SE&productversion=7.0&a=1
View full article
Janeway Jonas_Brissman Janeway
‎2025-04-09 05:58 AM

on ‎2025-04-09 05:58 AM

Labels:
  • EcoStruxure Building Operation
254 Views

Niagara N4.15 Mobile Profile Removal

Issue Removal of the Mobile Profile in N4.15 Product Line TAC IA Series. Environment I/A Series N4.15 Jace I/A Series N4.15 Enterprise Server Cause The Niagara Mobile Profile has been removed from Niagara 4.15 Resolution Since the Niagara Mobile APIs were deprecated and replacements provided in N4.6,  Niagara Mobile has been removed in N4.15. The standard HTML5 Hx Profile is mobile friendly and users configured with the BDefaultMobileWebProfile will automatically be switched to the HTML5 Hx Profile. When you start up a N4.14 station in a N4.15 environment for the first time and it was configured for using the mobile profile, you should see this warning:   "WARNING [14:06:11 22-May-24 EDT] [web] Support for the "Default Mobile Web Profile" has been removed. Users with this profile have been switched to the "Html5 Hx Profile".
View full article
Guinan RandyDavis Guinan
‎2025-04-09 05:54 AM

on ‎2025-04-09 05:54 AM

Labels:
  • TAC IA Series
144 Views
  • « Previous
    • 1
    • 2
    • 3
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of