Collect logs from an Automation Server

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Collect logs from an Automation Server
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
3 Likes
9945 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Collect logs from an Automation Server

Picard Product_Support
‎2018-09-06 02:52 PM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:56 AM

Issue

When troubleshooting server issues, it can be helpful to look at the logs that are recorded within the Automation Server.

Product Line

EcoStruxure Building Operation

Environment

  • Building Operation Automation Server 
  • Building Operation Automation Server Premium
  • Building Operation Automation Server Bundled

Cause

Within the Automation Server logs are many records that are logged as a part of normal operations and unexpected events.

Resolution

Automation Server:

Automation Server error logs can be retrieved using Workstation, Device Administrator, or WebStation. Device Administrator can be used in case of crash information is required, ex. dump files, or if the Automation Server is not accessible via WebStation or WorkStation.

  • Workstation:
    1. Connect to EBO system with EBO WorkStation.
    2. Select the target Server 
    3. Expand the System folder
    4. Expand the Modules folder
    5. Expand the Trace folder and see Trace Settings
    6. For EBO 3.1 or higher,
      1. Double-click both Trace Log and System Log to open separately Logs01.png
    7. For EBO 3.0 and lower, including SBO 1.x
      1. Right-click in Trace Settings
      2. Select Trace Settings in the menu
      3. Select Get System Log
      4. Repeat to select Get Trace Log Logs02.png
  • Device Administrator:
    1. Follow this WebHelp article: Getting Automation Server Debug Information
    2. If requested to retrieve a core dump, use this method to retrieve the Device Administrator Debug Information zip file. Then perform the following to make sure the zip file contains a core dump with a relevant timestamp for the event being investigated.
      1. Open Zip
      2. Open the folder containing the server name and IP address
      3. Open Server folder
      4. One should see file(s) with filename in this format core_dump_<Serial Number>_nsp_servers_<Timestamp>.tgz
  • WebStation:

EBO 4.0 (2022) and higher

      1. NOTE: You may have to enter Private Browsing mode to disable extensions, as you may see a blank page when viewing logs.
      2. Ensure credentials used are for a local 'admin' user or have access to the ~/System folder of the EBO Server you are connected.
      3. Click the 3-bar menu to navigate
      4. Select System, then Modules, then Trace
      5. One will see System Log and Trace Log in the menu, and clicking on System Log or Trace Log will open them in a new tab. NOTE: Please be patient as it may take some time to transfer the file.
      6. Once you see text in the tab, right-click on a blank area and select Save Page As... (Firefox) or Save As... (Chromium-based browser). It should recommend saving as SystemLog.txt or TraceLog.txt automatically; however, to be helpful, please add the EBO Server Name and Date to the filename.

EBO 3.2 and earlier

See the Webhelp Topic on collecting these logs from Automation Servers: Viewing and Downloading Automation Server Log Files. This process is now similar to that described above for WorkStation.

 

        1. Credentials used to log in must be a member of a group that allows the policy of Web Configuration: Allow members to access Automation Server Web Configuration.
        2. Launch a web browser that is compatible with the installed EBO version as mentioned Webstation Specification Sheet.
        3. Type the IP address of the automation server to open the Webstation.
        4. Log into the Automation Server.                  WebStation Logon.jpg
        5. Once logged into the Automation server, go to the Settings menu in the top right corner and click on Device Configuration.WebStation Device Configuration.png
        6. Click on the Server Log tab to view the automation server's log files. To save a copy of the log to your PC, click on the Get all log files link.WebStation Server Logs.png
        7. The log files are compressed into a zip file and exported to downloads folder.AllServerLogsZip.png

Enterprise Server and Enterprise Central:

For more information, check this article: Error logs from the Enterprise Server and Enterprise Central - Communities

 

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (11)
  • Find more articles tagged with:
  • 11610
  • DavidPurser22
  • DavidPurser25
  • extract
  • HernanUruena25
  • how
  • MahmoudSayed22
  • PeterLarsen21
  • RobertAndriolo24
  • system
  • trace
Was this article helpful? Yes No
100% helpful (3/3)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore