"MutationEvent is not defined" Javascript error after browser update to Chrome/Edge v127 and Firefox v140

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "MutationEvent is not defined" Javascript error after browser update to Chrome/Edge v127 and Firefox v140
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • CraigEl
    CraigEl

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
3469 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"MutationEvent is not defined" Javascript error after browser update to Chrome/Edge v127 and Firefox v140

Administrator CraigEl Administrator
‎2025-07-06 08:02 PM

on ‎2025-07-06 08:02 PM

 

Issue

Using graphics in WebStation, “MutationEvents not defined” error messages and/or data in not shown correctly, after the web browser used is upgraded to latest versions.

 

CraigEl_0-1751852520938.png

 

Product Line

EcoStruxure Building Operation

Environment

  • EcoStruxure Building Operation WebStation
  • Google Chrome v127 and later
  • Microsoft Edge v127 and later
  • Firefox v140 and later

Cause

After upgrading to the latest web browser versions EcoStruxure Building Operation web-based user interface, WebStation, in all released and supported versions may no longer operate correctly when graphics are attempted to be displayed. The symptoms include, but may not be limited to, failure for graphics to show data correctly and error prompts such as “MutationEvents not defined” being shown.


As referenced in Mutation events will be removed from Chrome  |  Blog  |  Chrome for Developers, Google has deprecated these Mutation events and replaced them with a different function. Also as referenced in Firefox 140 for developers - Mozilla | MDN The MutationEvent interface and its associated events have been removed from Firefox build 140 onwards.

Resolution

Consolidation point releases are available for supported EBO versions to resolve these compatibility problems with the latest browsers. These releases are available to authorized Schneider Electric EcoXperts and employees only from the EBO Hotfix List in the EcoExpert Community and the Software and Firmware Center of the EcoXpert Extranet. Other customers should contact their local Schneider Electric EcoXpert or Schneider Electric office and arrange a service visit.

 

The issue is addressed in the following releases:

  • EcoStruxure Building Operation 3.2.4 : EBO 3.2.4.7003 (CP5) onwards
  • EcoStruxure Building Operation 4.0.5 : EBO 4.0.5.5001 (CP4) onwards
  • EcoStruxure Building Operation 5.0.3 : EBO 5.0.3.12005 (CP11) onwards
  • EcoStruxure Building Operation 6.0.3 : EBO 6.0.3.2001 (CP1) onwards
  • EcoStruxure Building Operation 7.0

Unsupported versions such as EBO 3.1 and earlier will not be addressed. Upgrading to the latest version of EcoStruxure Building Operation is strongly recommended to ensure full compatibility with current web browsers and to benefit from the latest features and security updates.

Labels (1)
Labels:
  • EcoStruxure Building Operation
Tags (1)
  • Find more articles tagged with:
  • CraigEllis25
Was this article helpful? Yes No
50% helpful (3/6)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.