Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,854
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 11
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 480
    • 481
    • 482
    • …
    • 509
  • Next »

Heat pump Control with Two stages Auxiliary heating

Issue Unable to use SE8650 to control heat pump with a two Stages Furnace (auxiliary heat) Product Line EcoStruxure Building Operation, EcoStruxure Building Expert Environment Building Operation Workstation Building Operation Automation Server SSL SE8000 Cause Only one output is available in the SE8650 for Auxiliary heating Resolution A simple solution would be to Wire both Furnace W1 and W2 to the SE8650 W1 terminal, and both will be on at the same time Both furnace stages will be activated as a single stage from the same output Or a more advanced option would be to use a LUA Script to control the second stage of Auxiliary heating. See the below example using the SE8650 UO11 terminal  
View full article
Lt. Commander Ramaaly Lt. Commander
‎2022-04-08 11:10 AM

on ‎2022-04-08 11:10 AM

Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
951 Views

After upgrading to 1.93 the Live Event Viewer will only show the Alias of the Door and not the Name even though the column is configured to show the Name

Issue Live Eventview not showing name after upgrade. Environment CyberStation Cause Unsure. Resolution The problem went away when the database was updated with enhanced alarm delivery turned on.  
View full article
Picard Product_Support
‎2018-09-06 10:52 AM

Labels:
  • Andover Continuum
918 Views

Get alarm "The digital signature does not match".

Issue Every time the trendlog data should be viewed an alarm saying" The digital signature does not match, values might not be reliable". How can we avoid this? Environment Vista 4.4.2 Cause In old Vista versions like Vista 4.4.x we had something called Digital signature to check that the data in the SQL database had not been tampered with. This have been taken away in later Vista version as it slowed down and caused problems with trendlogs. The alarm indicates that someone have done something in the SQL database and the digital signature does not match.   Resolution It is possible to turn off the Digital signature in the Vista server setup under the SQL tab and then restart the Vista server. Then Vista will not do this check and the alarm should not appear.
View full article
Picard Product_Support
‎2018-09-06 10:51 AM

Labels:
  • TAC Vista
922 Views

TAC Xenta 102-AX PlugIn gives error message in EBO

Issue Could not start the TAC Xenta 102-AX LonWorks PlugIn, due to an Error message. Product Line EcoStruxure Building Operation. Environment EcoStruxure Building Operation Workstation. TAC Xenta 102 AX Cause EcoStruxure Building Operation does not support online PlugIns, as LNS is running in the background, without any communication port.. If selecting to Synchronize (Upload or Download) you will get an error message. Resolution Select "Skip" synchronize.
View full article
Kirk MikaelKrantz Kirk
‎2021-11-23 11:27 AM

on ‎2021-11-23 11:27 AM

Labels:
  • EcoStruxure Building Operation
936 Views

Webstation - TGML picture does not show special character as åäö

Issue Some web browsers can not show special extended ASCII letters like åäö  Environment Vista Webstation Cause When logging in to webstation from a PC and the TGML can not show special characters this is because a temp file has not been downloaded correctly. Resolution In the TGML window there should be a refresh button, click it and the temp file should be downloaded permanently, this should make special characters work again.
View full article
Picard Product_Support
‎2018-09-06 10:46 AM

Labels:
  • TAC Vista
920 Views

VTRE sleeve direction

Issue When the valve is installed, it is impossible to see the direction of the sleeve Environment VTRE 7317039000 7317041000 7317045000 7317049000 7317053000 7317057000 7317061000 7317065000 7317067000 7317069000 Cause In order to know the position of the sleeve inside the valve, you need to know the relationship between the sleeve and the "cut" on the stem. Resolution The cut in the stem indicates the position of the sleeve. If the cut is at 3 o'clock, the port at 3 o'clock is closed.
View full article
Picard Product_Support
‎2018-09-06 10:41 AM

Labels:
  • Field Devices
905 Views

Unable to pass data to an Enterprise Server from a UNC

Issue Unable to pass data to an Enterprise Server from a UNC Environment R2 Niagara Cause bad subscription access denied 401 error Resolution Check address book and system properties.
View full article
Picard Product_Support
‎2018-09-11 01:38 AM

Labels:
  • TAC IA Series
900 Views

Showing Outdoor air temperature on STR350

Issue How to show the Outdoor temperature on STR350? Environment STR350 Cause By the use of the variable nviOutdoorTemp, it is possible to show the outdoor temperature on the STR350 device. The outdoor temperature will be shown when you press the selection button. Resolution Make a binding for the outdoor temperature to the variable nviOutdoorTemp on the STR350 device.
View full article
Picard Product_Support
‎2018-09-06 10:29 AM

Labels:
  • TAC Vista
913 Views

Forta series actuators with IP65

Issue Is it possible to order a Forta actuator with IP class 65? Environment Forta series actuator M400 M800 M1500 M3000 Cause Some environments are requiring a higher than normal IP rating. Resolution Unfortunately the design of the Forta actuators are only IP classed to IP54. No IP65 version is available. An additional weatherproof bag may be added to cover the actuator. However, such bags needs to be purchased from other sources as they are not part of our portfolio.
View full article
Picard Product_Support
‎2018-09-06 10:28 AM

Labels:
  • Field Devices
904 Views

Replacing a M15 actuator when mounted to a TRV

Issue Which actuator should be used as replacement to a M15 230V actuator that is mounted on a TRV Valve? Environment M15 TRV M9B Cause Currently used actuator is no longer available. Resolution Use M9B/230 (part no 8601020000) together with Linkage/mounting kit for Butterfly valve TRV, Item Number: 8600991000  
View full article
Picard Product_Support
‎2018-09-06 10:26 AM

Labels:
  • Field Devices
905 Views

What's the best way to restore a full SIGNAL database from version 4.4.1 (Windows 95/98) to version 5.0.0 (Windows XP)?

Issue Customer did a full backup of a SIGNAL 4.4.1 installation.  A full backup is data, bitmaps, and executable files.  The computer hardware was replaced along with the operating system to Windows XP 32-bit.  The customer has SIGNAL version 5.0.0. Environment SIGNAL Cause Computer hardware replacement Resolution There are a couple of ways to restore the database.  Here is a simple method: - Install SIGNAL 5.0.0 - Restore the full backup from version 4.4.1 (this step overwrites all the executable files of 5.0.0) - Re-install SIGNAL 5.0.0 (this last step will update all the executables back to version 5.0.0) The license file, signal.dcf, may need to be checked to ensure it is for version 5.0.0.
View full article
Picard Product_Support
‎2018-09-06 10:23 AM

Labels:
  • TAC IA Series
940 Views

LD-1 display program stopped working.

Issue LD-1 program was working, then suddenly stopped. Environment LD-1 Display Module Cause Corrupted InfinityString points. Resolution Deleted and recreated corrupted InfinityString points.
View full article
Picard Product_Support
‎2018-09-06 10:22 AM

Labels:
  • Andover Continuum
906 Views

What is the part number & price for a SmartStruxure/IA Series R2, SmartStruxure/Network 8000 or SmartStruxure/Signal?

Issue What is the part number & price for a SmartStruxure/Network 8000 driver or a SmartStruxure/Signal driver? Environment SmartStruxure Network 8000 Signal Cause Job estimating Resolution There is no Network 8000 driver or Signal as there is with I/A Series Niagara. The conversion process is performed at no cost when converting an I/A Series R2 database,  Network 8000 GCM or Signal to SmartStruxure via the "TAC I/A Series Conversions Projects" link on the iPortal2 web site.
View full article
Picard Product_Support
‎2018-09-06 10:21 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
919 Views

SE7xxxx Room Controller Password

Issue Unable to access the SE7xxx Room Controller configuration parameters menu - displays an error code. Product Line EcoStruxure Building Expert, Field Devices  Environment SE7xxx Room controller SE7000 Series Ex. Viconics branding VT7000 Series Cause The display shows an error code when used, this is indicating a password is required, an example of the error code may be 977 or 996. Resolution Contact your region's Customer Care Center for a temporary password. The error code which is unique to that controller will be required by the Customer Care Center to calculate the temporary password. Note for PSS; Check Internal article. 
View full article
Sisko DavidChild Sisko
‎2021-05-27 01:23 AM

on ‎2021-05-27 01:23 AM

Labels:
  • EcoStruxure Building Expert
  • Field Devices
952 Views

Unable to view PINs in the User screen if “Allow PIN Duplication” is checked

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Unable to view PINs in the User screen if “Allow PIN Duplication” is checked   Product Line EcoStruxure Security Expert Environment Security Expert Server Cause This is viewed as a Site Security Enhancement feature Resolution Disable both the "Require Dual Credential for Keypad Access" and "Allow PIN Duplication" options
View full article
Commander JonGreen Commander
‎2021-05-03 12:46 PM

Last Updated: Guinan RandyDavis Guinan ‎2021-05-03 12:46 PM

Labels:
  • EcoStruxure Security Expert
925 Views

Controller status not updating in "View All Hardware" window

Issue In Access Expert's 'View All Hardware' window, the status of controllers does not update. For example, controllers say 'Online' even though they are actually 'Offline' and vice versa. Live Monitoring window does not show disconnect/online events. Seq log shows error: Failed to Publish event.Moniker:MonikerItem {"Namespace":"MercuryServiceEvents","Nickname":"mercury:15-12-1"} Product Line Access Expert Environment Access Expert Premise Software Cause Enterprise Administrator group, under root, is missing permissions for Mercury service. Resolution Log into the Root instance, edit the Enterprise Administrator group, in the "Event Types" tab, make sure permission is granted to the Mercury Service and Mercury Commands
View full article
Captain AbeMeran Captain
‎2020-10-07 06:40 AM

Last Updated: Guinan RandyDavis Guinan ‎2020-10-07 06:43 AM

Labels:
  • EcoStruxure Access Expert
903 Views

Troubleshooting Heat Meter installations (also Cooling or Flow meter)

Issue Troubleshooting Heat Meter installations (also Cooling or Flow meter) Environment Heat cooling or flow meter installation Kamstrup Cause Troubleshooting Heat Meter installations (also Cooling or Flow meter) when there is a problem with the values being measured Resolution To aid Product Support please supply the following information 1. Sketch of the installation, including physical details of pipe size, lengths and bend details plus any local valves etc. 2. Schematic sketch showing positions of Boilers/Chillers, Pumps, meters and sensors. 3. Photo of the installation if possible 4. Details of the media, maximum/minimum temperature, nominal flow and system pressure 5. What BMS is connected to the meter? Running NOTE Were no flow or little flow is seen, there may be air within the system, even if the "Air in System" info is not given on the meter.
View full article
Picard Product_Support
‎2018-09-06 09:56 AM

Labels:
  • Field Devices
921 Views

Microsoft Licensing for SmartStruxure Report Server

Issue How many SQL client licenses to run SQL if SQL 2008 is used to run Report Server? When Report Server is installed, is there a connection between SQL and the Enterprise Server. Environment Report Server Licensing Cause Licenses must be purchased for supporting software (OS, SQL, etc). Resolution Because SQL and Report Server have to be running on the same machine, there is only one sequel user that requires licensing.  There is no connection between the Enterprise Server and SQL when Report Server is installed.
View full article
Picard Product_Support
‎2018-09-06 09:49 AM

Labels:
  • EcoStruxure Building Operation
922 Views

On a SE7600 controller, is the nciSccModel snvt read-only or will it modify the controller's profile?

Issue On a SE7600 controller, is the nciSccModel snvt read-only or will it modify the controller's profile?  Customer has replaced the HVAC equipment such that the existing profile does not match up with the existing SE7600. Environment SE7600 VT7600 Cause Mechanical equipment was replaced with a different design Resolution The nciSccModel snvt does not modify the SE7600 profile.  It is a read-only. A different model of controller is the best option for the new mechanical design. An external solution may also work (i.e. the use of a relay).
View full article
Picard Product_Support
‎2018-09-06 09:45 AM

Labels:
  • TAC IA Series
960 Views

Doors and Reader Expanders not transitioning from Continuum database to Security Expert

Issue The Continuum Database Transition Tool does not transition the doors even though they are present in the Continuum database being transitioned   Product Line Security Expert Environment Security Expert Server Cause Incorrect configuration of the Continuum Transition Tool Resolution In the 'Record Types' tab of the Continuum Transition Tool, there is a checkbox labeled 'Include Anti passback Programming' If the doors on the Continuum system are configured for anti-pass-back then the checkbox has to be ticked to match the Continuum configuration of the doors.
View full article
Captain AbeMeran Captain
‎2020-01-31 12:08 PM

on ‎2020-01-31 12:08 PM

Labels:
  • EcoStruxure Security Expert
996 Views
  • « Previous
    • 1
    • …
    • 480
    • 481
    • 482
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of