On a SE7600 controller, is the nciSccModel snvt read-only or will it modify the controller's profile?  Customer has replaced the HVAC equipment such that the existing profile does not match up with the existing SE7600.
SE7600
VT7600
Mechanical equipment was replaced with a different design
The nciSccModel snvt does not modify the SE7600 profile.  It is a read-only.
A different model of controller is the best option for the new mechanical design.
An external solution may also work (i.e. the use of a relay).