Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,855
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 478
    • 479
    • 480
    • …
    • 509
  • Next »

ERROR: Template or User record is either corrupt or not supported when sending templates to biometric readers

Issue ERROR: Template or User record is either corrupt or not supported when sending templates to biometric readers Environment Bioscript V-Station integration Cause Enrollment reader's template type different from readers template types. Resolution Make sure the template type at the enrollment reader is the same as the template types in the other readers
View full article
Picard Product_Support
‎2018-09-06 09:38 AM

Labels:
  • Andover Continuum
901 Views

Users get wrong Access Level when importing users into SP-C Web controller

Issue If you import Users via a CSV with multiple Access Levels, some of the Users can have the wrong Access Level attached to their profile. Product Line Security Expert Environment Security Expert WEB Controller v4.00 314 I100 and later Cause The issue seems to occur only if the Access Level with the longer name is read in first, and then the shorter name. Example: "Access Level" will come before "Access Level Main" Resolution Within the CSV, sort the CSV by the Access Level column to ensure that the shorter name comes first.
View full article
Commander JonGreen Commander
‎2020-05-12 06:00 AM

Last Updated: Guinan AdamSteele Guinan ‎2020-05-19 10:14 PM

Labels:
  • EcoStruxure Security Expert
945 Views

Removing firmware from SmartX upgrade list

Issue Need to re-add firmware package to EBO for SmartX controllers and receive the error "firmware already exists" Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Multi-purpose Controller (MP-C) Building Operation Multi-purpose VAV (MP-V) Building Operation Room Controller (RP-C) - all Building Operation IP-IO Cause Cannot add a firmware package of the same revision if one is already in the firmware list. Resolution Open the Control Panel within WorkStation and select Firmware Management Select the firmware package you want to delete and click the delete button
View full article
Commander JonGreen Commander
‎2020-03-18 09:19 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2020-03-19 06:32 PM

Labels:
  • EcoStruxure Building Operation
944 Views

Error: Failed to replace dbexporter when installing ES 1.5

Issue Error: Failed to replace dbexporter when installing ES 1.5. The error appears when files are being copied to machine. Environment ES Cause Other instance of ES running. Resolution Go in Control Panel\Administrative Tools\Services and make sure there is no Enterprise Server service running.
View full article
Picard Product_Support
‎2018-09-06 09:30 AM

Labels:
  • EcoStruxure Building Operation
902 Views

Creating a failure recovery option for Scheduled Reports

Issue Creating a failure recovery option for Scheduled Reports Environment Web Reports Cause By default, reports will attempt to run at their scheduled time without accounting for failure recovery. Resolution Open Windows Server manager Expand Configurations Expand Task Scheduler Select the Task Scheduler library You will see a list of tasks which include all Scheduled Reports Browse to a Report Task In the Select Item Pane, click on Properties On the Setting Tab, check the box for "If the task fails, restart every" Change other settings as desired Click Ok. For additional logging, you can also look under the Action Pane to Enable logging for all tasks.
View full article
Picard Product_Support
‎2018-09-11 07:46 AM

Labels:
  • EcoStruxure Building Operation
907 Views

Replacement part for RYB-922-11 repair kit

Issue  RYB-922-11 is no longer available and needs to be replaced Environment RYB-922-11 Repair Kit for VB-922x-0-4-11 Cause repair kit no longer available Resolution There is no replacement for this kit. The customer will have to replace the valve body which probably will be the VB-7223-0-4-11 but verify which valve the customer has. Also since this new valve has a different stroke the customer will need to replace the actuator and linkage kit to ones that are used on the VB-7000 series valves.
View full article
Picard Product_Support
‎2018-09-06 09:22 AM

Labels:
  • Field Devices
900 Views

Replacement part for 64-061-31 valve

Issue  64-061-31 is no longer available and needs to be replaced Environment 64-061-31  TAC valve TAC DWV - PN 6 DN 32  Cause valve no longer available Resolution This old TAC Valve is no longer in production, Schneider Electric do not have any PN6 valves. It's mainly Germany/Austria that uses PN6 valves. Dimensionally they are the same as PN16 valves, the main difference is the wall thickness but in all practical terms it costs more to have two separate tools for each valve PN hence why Schneider and 90% of other suppliers just have PN16 even though they may only ever be used under 6 bar static pressure. As a replacement flanged valve, DN32, the V211 valve is suggested
View full article
Picard Product_Support
‎2018-09-06 09:17 AM

Labels:
  • Field Devices
951 Views

Shrink the SQLite event and trend databases

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue In some cases the event and trend database can grow really big although not all the space in the files is used Product Line EcoStruxure Building Operation Environment SQLite Building Operation Enterprise Server Cause Frequent inserts, updates, and deletes can cause the database file to become fragmented - where data for a single table or index is scattered around the database file. Running VACUUM ensures that each table and index is largely stored contiguously within the database file. In some cases, VACUUM may also reduce the number of partially filled pages in the database, reducing the size of the database file further. Read further information here: https://www.sqlite.org/lang_vacuum.html Resolution Stop the Enterprise Server Open SQLiteStudio (link to download) Select "Databases" --> "Add database" Select the event.db or trend.db file from the "historical" folder of the SmartStruxure database folder Execute the following command: vacuum;
View full article
Picard Product_Support
‎2018-09-11 11:41 PM

Last Updated: Administrator CraigEl Administrator ‎2023-05-28 06:14 PM

Labels:
  • EcoStruxure Building Operation
901 Views

Unable to control an I/NET DO object from a TGML graphic in HTML5

Issue Unable to control an I/NET DO object from a TGML graphic in HTML5, works in Workstation and Java based webstation Environment WebStation Cause The data type may not be correct.  The value should be written to PvControl as either a 0 or a 1.  If this is set as a string data type, Workstation can correct for this error, but HTML5 is less forgiving. Resolution locate the line of javascript where you write the value to the bind. this is typically a setValue(bind, value) function. bind = the full bind name of the pvControl binding. value = the value that is intended to be written to the pvControl bind. One line before the setValue command, enter the line " parseFloat(value)"  - This will convert that value to float. If the value is a 0 or a 1, the setValue command will now correctly set the I/NET value.
View full article
Picard Product_Support
‎2018-09-06 09:05 AM

Labels:
  • EcoStruxure Building Operation
914 Views

VStation unable to run.

Issue Getting an error when trying to launch Run_RunBioAdmin. Unhandled exception has occurred in your application. If you click Continue, the application will ignore and attempt to continue. I you click quit the application will close immediately.  InvalidArgument=Value of '255' is not valid for 'SelectedIndex'.  Parameter name: SelectedIndex. Environment Continuum 1.94 and above. Cause The database got corrupted and needed to be cleared out and restarted. Resolution To resolve this the following steps need to be done: Open up SQL Connect to the db and then Continuumdb Open up the Tables and expand it Look for VStationSysConfig Run a query to delete the rows in it and then restart VStation again.
View full article
Picard Product_Support
‎2018-09-06 09:01 AM

Labels:
  • Andover Continuum
912 Views

UC, MR, and ASC controllers do not use the minimum trip and close command

Issue Which controllers do not use the minimum trip and close command? Environment UC, MR, or ASC Cause The editor lets you enter a value in the minimum trip and close field; however, the UCI, MRI, MCI, or I/Site Lan replaces the entered value with the default value of "0" when it is downloaded to the UC, MR, or ASC. Resolution The minimum trip and close parameters are not used for Unitary Controllers (UC), Micro Regulator (MR), or Application Specific Controllers (ASC) output commands.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
945 Views

Special consideration for 08 and 09 DI\DA points on a 7910A and 7920 DPU

Issue Can I use the 08 & 09 DI\DA points on a 7910A and 7920 DPU as internal points? Environment 7910A DPU 7920 DPU Cause These points are dedicated points and cannot be used for any other purpose. Resolution The 08 & 09 DI\DA points on a 7910A and 7920 DPU: Cannot be used as internal points Cannot have calculation extensions
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
944 Views

Use local CPH on a stand-alone MR-VAV-AX

Issue How to make local CPH work on a stand-alone MR-VAV-AX. Environment MR-VAV-AX Cause Even after you select local-CPH in the parameters and connect a contact to the local cph point, the unit probably won't switch modes without further modification. The application is looking for a zero for one mode and something above 1 for the other. Problem is that the factory calibration of the inputs can only be done to within 1 or 2 counts. With the standard conversion coefficient of 5 and 0, you'll still see a value of 5 or 10 for a shorted input. Changing the conversion coefficient wouldn't help because you need an absolute zero. Resolution Even though this is for stand-alone use, you need to connect the unit to an MCI or ISITE Lan. You can leave the address at 0 and set address 0 to MR or ASC in the MCU configuration. Open the ASC editors and update MCI for address 0 and check the point value for local cph with that input shorted. If it doesn't read 0, proceed. Next select Edit, Controller, MR functions. Highlight 0 and hit the Hardware button. These M and Bs are here as a result of the factory calibration. Reduce the B on input 02 (3rd entry down) by one or 2 or even 3 so that the local cph input reads 0 when shorted. When your done with the first one, you can plug in the rest and use the same MCI database provided you leave them all at 0.
View full article
Picard Product_Support
‎2018-09-06 03:30 PM

Labels:
  • TAC INET
923 Views

Difference between DPU EPROM rev 2.21 and 2.22

Issue What are the differences between DPU EPROM rev 2.21 and 2.22? Environment DPU EPROM Cause On the 2.22 rev, one problem was corrected and an enhancement included. Resolution The problem was when using first key auto-unlock, the software would show the door as unlocked, when the first valid read had not yet unlocked it. It now remains in the secure mode in software until the first valid read. The enhancement is that when a DPU is operating on back up battery power, the power led will now flicker to indicate the change from commercial power.
View full article
Picard Product_Support
‎2018-09-06 03:29 PM

Labels:
  • TAC INET
933 Views

DPU offline, but the other DPUs appear to be operating except the transactions have stopped coming to the host.

Issue One of the established DPUs is now offline, but the other DPUs appear to be operating except the transactions have stopped coming to the host. Alarms and messages are still working. A DPU restore to the DPUs has been performed. QP has been checked, and the AC files have been repaired.. Environment DPU Cause In AMT, there is most likely a Failure to Download message. Resolution To correct the transaction symptom Go to the data directory of I/NET Look for a file named ACSAVE.TMC Delete it.
View full article
Picard Product_Support
‎2018-09-06 03:27 PM

Labels:
  • TAC INET
918 Views

ASC not communicating and sending lost/restored messages

Issue ASC that has stop communicating The site lost and restored messages coming from this controller. ASC has had communication problems in the past. ASC will not take downloads. Environment I/NET ASC Cause These communication errors could result in corruption of the ASC's NOVRAM. Resolution Clear the memory in the ASC by doing the following: Remove power from the unit Set DIP switches 6 through 12 to the "ON" position and restore power. Remove power again. Set DIP switches 6 through 12 to the "OFF" position and restore power. Remove power again and rest the switches to their normal configuration. Perform a ASC update.
View full article
Picard Product_Support
‎2018-09-06 03:27 PM

Labels:
  • TAC INET
927 Views

What is a Parent Point in a UC (Unitary Controller)?

Issue What is a Parent Point in a UC (Unitary Controller)? Environment Unitary Controller Cause Feature information Resolution A parent point is nothing more than the AO or DO point to which you add a UC extension: VAV, AHU, PID, FLT, or HPMP. The functioning of the extension is directly tied to the state of the parent point and the command pairing. Refer to TCON 209 or TCON237 for important details.
View full article
Picard Product_Support
‎2018-09-06 03:41 PM

Labels:
  • TAC INET
912 Views

Set up a two wire LTS80 Lini-Temp sensor on a 7740 and 7741 DCU

Issue Set up a two wire LTS80 Lini-Temp sensor on a 7740 and 7741 DCU. Environment 7740 DCU 7741 DCU LTS80 Lini-Temp sensor Cause Conversion coefficients must be set properly for correct reading of temperatures. Resolution For Fahrenheit: M = 0.17582 B = -279.4 For Centigrade: M= 0.09768 B = -173.0 Refer to TCON 097 for 10K resistor placement
View full article
Picard Product_Support
‎2018-09-06 10:54 PM

Labels:
  • TAC INET
974 Views

Using the Xenta 511, will value pages only show temperatures in Celsius? How do you get them to display in Fahrenheit?

Issue Using the Xenta 511, will value pages only show temperatures in Celsius? How do you get them to display in Fahrenheit? Environment XBuilder Cause Regional settings can be project wide or per point. Resolution When creating a new TAC Xenta 511 project, select to use US values. You can also select conversions to occur per object.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
931 Views

PCU Analog Outputs to transducers do not have consistent performance

Issue PCU Analog Outputs to transducers do not have consistent performance. The first voltage-to-pneumatic transducers installed worked fine. Additional transducers have been added; and now, none of the transducers operate properly. Environment PCU Voltage-to-Pneumatic transducers Cause The amperage or power draw limitations of the PCU have most likely been exceeded. Resolution Sum up the total current and / or power draw of all the transducers and compare this to the maximum current or power output of the PCU. Reduce the number of transducers to stay within the limitations.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
954 Views
  • « Previous
    • 1
    • …
    • 478
    • 479
    • 480
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of