VStation unable to run.
  • VStation unable to run.
  • Roger_Bently
    Roger_Bently
‎2018-09-06 09:01 AM
Getting an error when trying to launch Run_RunBioAdmin.
Unhandled exception has occurred in your application. If you click Continue, the application will ignore and attempt to continue. I you click quit the application will close immediately.
InvalidArgument=Value of '255' is not valid for 'SelectedIndex'.
 Parameter name: SelectedIndex.
Continuum 1.94 and above.
The database got corrupted and needed to be cleared out and restarted.
To resolve this the following steps need to be done:
  1. Open up SQL
  2. Connect to the db and then Continuumdb
  3. Open up the Tables and expand it
  4. Look for VStationSysConfig
  5. Run a query to delete the rows in it and then restart VStation again.