PCU Analog Outputs to transducers do not have consistent performance.
The first voltage-to-pneumatic transducers installed worked fine. Additional transducers have been added; and now, none of the transducers operate properly.
  • PCU
  • Voltage-to-Pneumatic transducers
The amperage or power draw limitations of the PCU have most likely been exceeded.
Sum up the total current and / or power draw of all the transducers and compare this to the maximum current or power output of the PCU. Reduce the number of transducers to stay within the limitations.
  • TAC INET