Issue
Set up a two wire LTS80 Lini-Temp sensor on a 7740 and 7741 DCU.
Environment
- 7740 DCU
- 7741 DCU
- LTS80 Lini-Temp sensor
Cause
Conversion coefficients must be set properly for correct reading of temperatures.
Resolution
For Fahrenheit:
- M = 0.17582
- B = -279.4
For Centigrade:
- M= 0.09768
- B = -173.0
Refer to TCON 097 for 10K resistor placement