Creating a failure recovery option for Scheduled Reports
  • Creating a failure recovery option for Scheduled Reports
  • Derrick_Ratliff
    Derrick_Ratliff
‎2018-09-11 07:46 AM
Web Reports
By default, reports will attempt to run at their scheduled time without accounting for failure recovery.
  1. Open Windows Server manager
  2. Expand Configurations
  3. Expand Task Scheduler
  4. Select the Task Scheduler library
  5. You will see a list of tasks which include all Scheduled Reports
  6. Browse to a Report Task
  7. In the Select Item Pane, click on Properties
  8. On the Setting Tab, check the box for "If the task fails, restart every"
  9. Change other settings as desired
  10. Click Ok.
  11. For additional logging, you can also look under the Action Pane to Enable logging for all tasks.