Issue
Need to re-add firmware package to EBO for SmartX controllers and receive the error "firmware already exists"
Product Line
EcoStruxure Building Operation
Environment
- Building Operation Workstation
- Building Operation Multi-purpose Controller (MP-C)
- Building Operation Multi-purpose VAV (MP-V)
- Building Operation Room Controller (RP-C) - all
- Building Operation IP-IO
Cause
Cannot add a firmware package of the same revision if one is already in the firmware list.
Resolution
- Open the Control Panel within WorkStation and select Firmware Management
- Select the firmware package you want to delete and click the delete button