Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,209
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,841
  • TAC IA Series 1,823
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 330
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 148
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Activate 13
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 7
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Views
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 14
    • 15
    • 16
    • …
    • 507
  • Next »

How to upgrade a BAS system to Sigma

Issue BAS is obsolete how can it be upgraded to Sigma? Product Line Satchwell BAS & Sigma Environment Satchwell BAS 2800+ V2.9 Satchwell Sigma Cause BAS is obsolete but there is a defined path to upgrade the system to Sigma Resolution Upgrading must start from BAS2800+ v2.9 when upgrading to the latest version of Sigma.  Sigma not only allows for more features but also future proofs the system. Upgrade procedure can be found here Migration document (Sales support) can be found here Any BAS versions before BAS2800 + V2.9 please contact Product Support with the details.   The Sigma system is now out of its support period, consideration should be given to transitioning or upgrading to SpaceLogic - EcoStruxure Building Operation.
View full article
Picard Product_Support
‎2018-09-09 05:00 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-19 01:54 AM

Labels:
  • Satchwell BAS & Sigma
5479 Views

BMS Redundancy TVDA

Issue How to be redundant with your intelligent Building Management System (iBMS) Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell Sigma, Security Expert, TAC INET Environment Existing intelligent Building Management System Open Mind High Availability Solutions (Deprecated by manufacturer) everRun MX ztC Edge Cause In engineering, redundancy is the duplication of critical components of a system with the intention of increasing the system's reliability. To be redundant with an intelligent Building Management System (iBMS) would take on two possibilities. Have an alarm on critical points alerting personnel who move into action quickly replacing control boards or devices in the event of failure. Have secondary backup controllers which upon failure, which are used to control devices resuming functionality. This is accomplished through programming the BAS with event sequences triggered from alarms or flags noting the failure. Redundancy capabilities and feasibility are site specific. Ascertaining failure in boards, points, or devices is crucial to creating secondary measures to keep seamless processes going and resume with functions.   Error detection and correction with maintenance is often the best practice for preventing failure. Worn components are the leading cause of failure, followed by a lack of planning and consideration in the protection of electrical components through power surges or failures.   For the database, backups including automated backups for MSDE, SQL Express, and Full SQL are available. For further information on database backups and options, take a look at Microsoft SQL Management Studio. For Host Computer backups, look at adding a secondary computer which replicates the database and can capture transactions and messages should a failure with the primary host computer take place. Also work with the local IT department to keep machines up to date, safe, and clean of 3rd party applications which may interfere with integrity. Schneider Electric’s building management systems are designed such that building control continues even when controller to server communication is disrupted. The BMS server is home to a database of alarm and historical data, as well as system parameters and programs. When a server or its network connection fails, the collection of data from building controllers halts until the problem is resolved. For data critical applications, this solution provides an environment capable of preventing the data loss that results from these types of failures.  Although we do support its use with EcoStruxure Building Operation, Security Expert, Continuum, I/NET, Vista, Sigma, and I/A Series as a disaster recovery solution, we do not provide direct support for EverRun. Resolution For Open Mind High Availability Solutions guide please look at the following link; Open Mind High Availability Solution guide For everRun MX solution guide please look at the following link; everRun MX guide For ztC Edge solution guide please look at the following link; ztC Edge guide   
View full article
Picard Product_Support
‎2018-09-06 01:43 PM

Last Updated: Shuttle Bay DanielBergman Shuttle Bay ‎2024-10-24 11:11 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
  • Field Devices
  • Satchwell BAS & Sigma
  • TAC INET
5416 Views

Differences between IAC 400 and IAC 420 controllers

Issue What are the differences between the IAC 400 and the IAC 420 controllers? Product Line Field Devices, Other, Satchwell MicroNet, Satchwell Sigma   Environment IAC 400 IAC 420 Cause The IAC 400 controller is obsolete and its replacement is the IAC420. Resolution Hardware differences; The IAC 400 has 3 Temperature, 2 Analogue and 1 Digital input, where as the IAC 420 has 6 Universal inputs. Communications differences; The IAC 400 controller uses terminal 3 to earth the communications cable screening, on the IAC 420 the screening must be connected to a good earth and not terminal 3. Tables and offsets; Because the IAC 420 has different inputs that tables and offsets are changed, please review IAC Controllers - Tables and Offsets. IAC 400 Wiring details. For the full data sheet please click HERE.   IAC 420 Wiring details. For the full data sheet please click HERE.
View full article
Picard Product_Support
‎2018-09-10 11:46 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:56 PM

Labels:
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
5435 Views

Alarm delivery in StruxureWare: Sending Alarms to a Gmail recipient using the ES Email Notification.

Issue An Enterprise Server or Automation Server is unsuccessful at sending email notifications to a Gmail recipient.  Email messages from ES are marked as spam by Gmail SMTP service. Product Line EcoStruxure Building Operation Environment Building Operation Enterprise Server Building Operation Automation Server (AS-P, AS-B or AS) Building Operation Workstation Gmail Cause Unable to successfully configure the ES to send an Alarm Notification to a Gmail recipient. Resolution The following describes how the ES can be set up to use Gmail for Email delivery. 1. Log into the ES; designate the Sender E-mail address and E-mail Host properties. 2. Create a notification on the ES; set the destination E-mail address and type of alarms to be included. 3. Log into destination E-mail account; notice there don’t appear to be any E-mails received. Select the “More” dropdown. 4. Select the “SPAM” folder. 5. Navigate to the E-mail Selection Tab and choose all E-mails from the correct sender. 6. Select the “Not Spam” button and from now on all email notifications will be sent to your inbox! 1. Log into the ES; designate the Sender E-mail address and E-mail Host properties. 2. Create a notification on the ES; set the destination E-mail address and type of alarms to be included. 3. Log into destination E-mail account; notice there don’t appear to be any E-mails received. Select the “More” dropdown. 4. Select the “SPAM” folder. 5. Navigate to the E-mail Selection Tab and choose all E-mails from the correct sender (SxW). 6. Select the “Not Spam” button and from now on all email notifications will be sent to your inbox!
View full article
Picard Product_Support
‎2018-09-10 10:29 PM

Labels:
  • EcoStruxure Building Operation
5431 Views

PCT Intel Processor Virtualization Technology Issue

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue PCT client can't start properly with "Hardware virtualization is not enabled" error. Product Line EcoStruxure Building Operation Environment Building Operation Project Configuration Tool (PCT) (All Versions) Cause Hardware Virtualization is Disabled or not available for PCT Resolution  Install "Intel® Processor Identification Utility" then verify the status of "Intel® Virtualization Technology" from the Utility. Using the table below, you can see if your processor supports Intel® Virtualization(provided by Intel).  The above information can also be found on Intel® Virtualization Technology web page If Virtualization is disabled in BIOS then enable it from BIOS else identify other software utilizing the Virtualization and stop the application.  Use Win key or press the Windows Start button Type: cmd Select Run as Administrator  Verify command prompt window title bar is Administrator: Command Prompt Type: shutdown /r /fw/ /f  Press enter and the computer will shut down immediately forcing all applications to close (/f) and restart (/r) into firmware interface (/fw)   If the issue persists, the following article may provide the answer Knowledge Base article - PCT error Hardware-virtualization is not enabled-Please-enable.
View full article
Admiral StephenYang Admiral
‎2020-03-31 06:39 AM

Last Updated: Picard David_Purser Picard ‎2022-10-03 07:02 AM

Labels:
  • EcoStruxure Building Operation
  • Project Configuration Tool
5428 Views

Controller is online but downloads to the SP-C are failing

Issue Downloads to the Controller are failing. When reviewing the Download Server Diagnostic Window, numerous Failed to load DAT file error messages are seen. Failed to load DAT file. Path='C:\ProgramData\Schneider Electric\SecurityExpert\Download\5.dat". Error code = 80070002 ***** Invalid Controller (5) version 0 Product Line EcoStruxure Security Expert Environment Security Expert SP-C Cause The Firmware version in the Controller is not compatible with the version of Security Expert being used. Resolution Upgrade the Firmware in the Controller to the latest Firmware build. From the main menu, select Sites | Controllers. Right click on a controller, and select Update Firmware. Click the [...] button and browse to the supplied firmware (.bin) file. Choose which controller(s) to update by selecting the Include option. Only the selected controller(s) will be updated. Click Update to commence the firmware update procedure. The update can take up to 10 minutes per controller to complete. Once complete, the controller is automatically restarted and normal operation resumed.
View full article
Picard Product_Support
‎2018-09-10 10:47 AM

Last Updated: Kirk AdamSteele Kirk ‎2022-02-02 09:47 PM

Labels:
  • EcoStruxure Security Expert
5413 Views

Replacement of Satchwell "M 1201" Actuator forming part of combined Actuator / 2-port Valve Body assembly due to obsolescence.

Issue Satchwell “M 1201” Actuator forming part of combined Actuator / 2-port Valve Body assembly requires replacement. Environment Stand alone Satchwell “M 1201” Actuator forming part of combined Actuator / 2-port Valve Body assembly M 1201 Actuator 2-port Valve Body Cause Obsolescence of Satchwell “M 1201” forming part of combined Actuator / 2-port Valve Body assembly. Resolution There is no direct replacement for the "M 1201" Actuator and as a result both the "M 1201" Actuator and the 2-port Valve Body to which it is connected will also require replacement.  Replace Satchwell “M 1201” combined Actuator & 2-port Valve Body assembly with Schneider Electric MD10B-230 Actuator, LMD-MB Linkage Kit and Satchwell MB series 3-port Valve Body of appropriate size. Details of the original Satchwell “M 1201” combined Actuator & 2-port Valve Body assembly may be viewed here. Details of the replacement Schneider Electric MD10B-230 Actuator may be viewed here. Details of the replacement Schneider Electric LMD-MB Linkage Kit may be viewed here. Details of the replacement Satchwell MB 3-port Valve Body may be viewed here. N.B. Satchwell MB series 3-port Rotary Shoe Valve Body may be converted for use as a 2-port Zone Valve by means of the installation of a plumber’s plug in Port 3 Install plumber's plug in Port 3 of MB series 3-port Rotary Shoe Valve Body. Tighten plumber's plug sufficiently to ensure PN 10 rating of Valve Body is not compromised. It is possible that the "M 1201" Actuator may have been fitted with an Auxiliary Switch. If so then an MD-S1 Auxiliary Switch may be fitted to the MD10B-230 Actuator if required. Details of the MD-S1 Auxiliary Switch may be viewed here.
View full article
Picard Product_Support
‎2018-09-10 04:56 AM

Last Updated: Administrator CraigEl Administrator ‎2023-09-11 01:37 AM

Labels:
  • Field Devices
5489 Views

Documentation for WorkPlace Tech Tool software and associated controllers

Issue Where can I find the current documentation for the WorkPlace Tech Tool software, MNL LON controllers, MNB BACnet controllers and their associated specification data sheets? Product Line TAC IA Series Environment WorkPlace Tech Tool software I/A Series MNB BACnet family of controllers I/A Series MNL LON family of controllers Cause There is no single online source for the all the current documentation for the WorkPlace Tech Tool software, MNL LON controllers, MNB BACnet controllers and their associated specification data sheets. Resolution All documentation related to the WorkPlace Tech Tool (WPT, WPCT & WPFB) and related controller documents are installed to your computer when you install the WorkPlace Tech Tool software. At the time of release, the current version of each software manual, hardware installation manual (LON & BACnet), specification data sheet (LON, BACnet & Software) and the software release notes document is built into the software installation program. These documents are all accessible under the \WorkPlace Tech\Help folder on any computer where the WorkPlace Tech Tool software is installed. All documentation can be displayed from the list displayed by the WorkPlace Tech Help menu. This was done to insure that all WorkPlace Tech Tool users would have access to the version of all documents related to that specific release of the software. Since these documents are included in the installation package for any version of the WorkPlace Tech Tool software, you can download the latest WorkPlace Tech Tool installation file from The Exchange Download Center to get the complete set of documents. These documents are also available individually from the 'Publication Zone', accessible from the 'Links' menu on iPortal (https://iportal2.schneider-electric.com).
View full article
Picard Product_Support
‎2018-09-10 08:36 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-06 07:34 AM

Labels:
  • TAC IA Series
5432 Views

Configure Time Zone and UTC Offset settings so that time is synchronized across your system

Issue How to properly configure Time Zone and UTC Offset settings in Cyberstations and controllers. Product Line Andover Continuum Environment Continuum Cyberstation Continuum Controllers Cause There are a number of locations for time configuration settings, creating uncertainty as to what needs to be set, and where, to maintain the correct time in all devices. Resolution How to sync controller time with WS time with Server time. Set the correct UTC offset (time zone) in all of the below locations: Confirm Cyberstation(s) PC time zone (UTC offset) and regional settings are correct. [This has no effect on time synchronization but does have an effect on what time alarms and events are written to the database as well as when alarms will be delivered to Cyberstations] Confirm the SQL Server PC time zone (GMT settings) and regional settings are correct. [same as 1 above] In Continuum, the Workstations Device object's Time tab has the correct time zone setting (be aware this is in minutes, ex. GMT+10 = +600 minutes.) In Continuum, the Network folder has a setting for the time zone, this needs to be configured to the time zone the controllers are located. If GMT+10 then this gets set to +600. Note1: To synchronize controller time to Workstations time a program needs to be created in one WS that sets the Date object of the Netcontroller (IP level controller) with the lowest ACCnet ID. This controller will then push any time changes out to all other IP level controllers and down to its subnet controllers (i2’s or b3’s). See Time sync controllers to workstations for details on this. Note2: At 38 minutes past the hour the Netcontroller will push its time down to its subnet (aka Field Bus) controllers. Note3: When time is set in the Netcontroller with a reload of the controller, the UTC settings of the WS doing the reload, and the Network folder the controller is in, are accounted for and the controllers time is set with these UTC settings taken into account. When time is set with a PE program using the WS Date object, this does not take into account the UTC settings of the various locations and just sets the controller Date object to the exact value of the WS Date object. If the controller is in a different time zone than the WS setting its time, then it will now have the wrong time in it. To compensate for this, it is suggested that time offsets must be added to the Time Sync program to accommodate those networks in a different time zone than the WS. Other UTC setting locations and what these settings effect IP level BACnet Device UTC Offset The UTC offset value on the Time tab of the BACnet Device object is only used when the BACnet time synchronization method is being used to set time. This setting then follows the BACnet specification where it needs to be the negative value of the GMT setting. For example, if the BACnet device is in the GMT+10 time zone, then set this offset to -(10*60) = -600. Note4: If using the PE program method, the UTC offset value on the Time tab of the BACnet Device object does not change how time is set in the controllers. However, if the UTC offset value on the Time tab of the BACnet Device object is changed, it will change the current time of the controller to coincide with the new time zone until the time is set again in the controller, or the UTC offset value is removed. UTC offset in controller configuration Time Settings webpage This doesn’t change how the time of the controller is set. It is used to set the time of sent email messages when using the SMTP option on this controller.
View full article
Picard Product_Support
‎2018-09-11 12:00 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:55 PM

Labels:
  • Andover Continuum
5417 Views

Web Service addition Script Web Service

Issue Web Service addition Script Web Service Product Line EcoStruxure Building Operation Environment StruxureWare Building Operation site with release 1.2 or later Cause What are Web Services and how to add to my existing StruxureWare Building Operation site. How to add Script Web Service files and how to add to a project or site How to create values from Script Web Service Files How to add values to graphic that uses the values from Script Web Service Resolution Wikipedia: A Web Service is a method of communication between two electronic devices over the web (internet). W3C: A "Web Service" as "a software system designed to support interoperable machine-to-machine interaction over a network." Web Services: 1. are hardware, programming language, and operating system independent 2. Applications written in different programming languages and running on different platforms can seamlessly exchange data over intranet or the internet using Web Services 3. Web Service interfaces are supported in both the AS and ES 4. Like BACnet, Lon, and Modbus, you can create a Web Service interface.      EWS Interface - EcoStruxure Web Services      Script Web Service - Generic Consume via Script      Simple XML Web Service - Rest Generic Consume via Binding Tool (Web Service addition Simple XML Web Service)      SOAP Web Service - SOAP Generic Consume via Binding Tool (Web Service addition SOAP Web Service) This article explains adding Sunrise and Sunset for a particular location data using Script Web Service: -Select New...Interface...Web Service...Script Web Service This first example is for a Calculation program for Results=A+B -Enter the WSDL Service and Endpoint are auto-filled Not necessarily all the time IP Cameras -Script Web Services Interface: -Script Programs can bind to the web service with the "Webservice" declaration. -When the name bound service is typed and a "." is put after it, intellisense drop down will show the available methods WSDL file is brought into the database Drop down methods become available even if the URL of the WSDL is not -The web service capabilities can be used within the code for manipulation, data gathering, or whatever else. -Script Web Services Post and Gets -Script programs can send requests directly to a web service with the SendWebRequest keyword. -The syntax requires 5 specific arguments BaseURL - URL that will be processing the message Method - Method of processing the POST and GET (dictated by URL) Headers - Defines certain parameters that are meaningful to the URL (IsMobileApp:True;IsAndroidClient:True) Content-Type - Defined by the URL Message - What is actually being sent to the URL -Script Web Services - Considerations -Bindings to a web service require a recompile -Display of captured information will get localized   Next, Create a Script Program for Calculations Here is a simple script program which defines the calc and values The below shot is the values A=12, B=3, and the Results of the calculation. Below are the binding for the Script Calc program to the Values The below shot is the binding of the Calc program to the Script Web Service The results are a calculation in which we supply value A and B and the Script Web Service performs the calculation with results of 15.   We can change the value of A to from 12 to a value of 13 which Results in 16 as shown in the shot below.
View full article
Picard Product_Support
‎2018-09-10 01:41 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-07 11:39 PM

Labels:
  • EcoStruxure Building Operation
5404 Views

Report can not be displayed - The request failed with HTTP status 503: Service Unavailable

Issue When trying to open a report, you get an error message like below: Msg=DDL creation failed ex=Error creating DropDownddlTopCount The request failed with HTTP status 503: Service Unavailable Ex=ButtonRunReport The request failed with HTTP status 503: Service Unavailable   Product Line EcoStruxure Building Operation Environment Reports server Cause Cause 1: The Report Server Service is not started To check if this is the cause, open the report manager. If you get the error below, continue to resolution 1.   Cause 2: The Report Server Service takes too long to generate the report and thus times out The root cause should also be investigated. It can be a slow network connection, fragmented SQL database, antivirus software or memory limitation that is slowing the request to compile a report down. Resolution Resolution 1 Open "Reporting Services Configuration Manager" Start the server   Resolution 2 Increase the timeout for the report service Open Report Manager Click "Site Settings" Change the Report Timeout. Default is 1800 which is 30 seconds.   Check that the memory usage for the SQL server is not limited (Microsoft's How to: Set a Fixed Amount of Memory (SQL Server Management Studio)) Open SQL Management Studio Open the properties for the SQL Server Click "Memory" and check that the value is default (2147483647)   Reindex and defragment the SQL database e.g. using SBO Reports Agent Config.
View full article
Picard Product_Support
‎2018-09-11 03:45 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 03:57 AM

Labels:
  • EcoStruxure Building Operation
5397 Views

Convert Trane BCU (BMTW or BMTX) from BACnet/Ethernet to BACnet/IP for integrating to a Niagara R2 UNC

Issue Is there a way to convert a Trane BCU (BMTW or BMTX) from BACnet/Ethernet to BACnet/IP for integrating to a Niagara R2 UNC? Product Line TAC IA Series Environment Trane BCU (BMTW or BMTX) Niagara R2 UNC Cause There are two components required to change over the BCU from BACnet/Ethernet to BACnet/IP. Resolution A special serial cable is required to download the BCU with the new configuration. Below are the pin outs to make the cable:     Access to the Tracer Summit software. Here are the steps for running the BCUconfig.exe program to change over the BCU from Ethernet to IP: Open Windows Explorer and navigate to C:\Program Files\Tracer Summit\Bin Double-click on BCUconfig.exe Enter the information and select download. Note - This is where you must have the Trane serial cable. The BCU will reset. Now change the Connection type in the Tracer Summit software to IP connection: Open the Tracer Summit software and select Connect. The Site connection Wizard will appear. Select the BACnet/IP radio button. From the Ethernet Configuration window, select the 'open on startup' check box. Select the 'Use BBMD connection' from the BACnet/IP configuration window. Specify the IP address of the BBMD BCU and the UDP port which is the BACnet port. Select Finish.
View full article
Picard Product_Support
‎2018-09-07 12:45 AM

Last Updated: Administrator DavidFisher Administrator ‎2020-10-26 06:13 AM

Labels:
  • TAC IA Series
5374 Views

Sigma Client reports a "HTTP connection failed" error".

Issue The Sigma Client reports a "HTTP connection failed" error" when an attempt is made to start it. Product Line Satchwell Sigma Environment Satchwell Sigma release 4.05 and later Cause When the Sigma Client is started, attempts are made to make a connection to the Sigma Server, this connection fails and the Client cannot be started. Resolution There are a number of reasons why this error might occur, suggestions are listed below. 1.  Windows XP operating system - ensure that service pack 3 has been installed, and that all the Windows updates have been applied. 2. Windows 7 operating system - only Ultimate and Professional are supported. 3. Sigma Client/Server software must be installed by a Windows user with "Admin" privileges. 4. Windows Firewall must either have been switched off, or has "Exceptions" configured as explained in the Sigma 4.05 SP1 release note. 5. Check that the "SigmaSVR" service has been started. If this service cannot be seen, then this is an indication that the Sigma software has not been install by an "Admin" user, and the software must be reinstalled. 6. Corruption of the Windows "User" files has taken place. Create a new Windows user with "Admin" privileges. Log on to Windows as the new user and test the Sigma Client again. 7. If using a VMware image try rebooting the image. 8. SMART is being used and has a modem connected to the PC for uploading data. Ensure that the modem is fully functional. If not, the HTTP error can be caused. This was seen at Sigma: R4   Release 3.44.14. and Smart Task Manager  3.0.2.20. Added 26-07-2012 9. This may be because a proxy server is being used, eg on school networks. Log on to your PC computer with an administrator account. Open the "Start" menu and click on "Control Panel." Double-click on the icon labeled "Internet Options." Go to the "Connections" tab at the top of the window and then click on "LAN Settings." Make sure the box next to "Bypass proxy server for local addresses" is checked. Hit "OK" twice to confirm the new proxy port settings. Make sure the box next to "Bypass proxy server for local addresses" is checked. Hit "OK" twice to confirm the new proxy port settings. Added 25-09-2012. 10. This issue was reported from a School where Sigma 4.05 SP1 had been operating correctly for several weeks. The issue was traced to the Anti-virus software Sophos, which had received an update prior to the failure. Sophos had quarantined two Sigma dll files. To correct this issue both Sophos and Sigma were uninstalled. A later version of Sophos was installed, and then Sigma was reinstalled, this corrected the problem. Added 01-08-2013 11 - Sigma software installed when connected to a wireless network. The Sigma client will only connect to the server when the wireless connection is made. Uninstall Sigma, disable the wireless, enable the network card, and then reinstall the Sigma software. Added 03-10-2013 12. DELL PC, with firewalls and antivirus disabled and no wireless card fitted. There may be a service or an application running in the background as part of the vendors Windows platform makeup.Restore the same version of Windows, but without (where possible) any of the Vendors applications. Re-install Sigma. Added 16-05-2014 13. Check the port number in c:\sigma\bin\setupsvr.exe, the default is 8080. Added 19-05-2014 14. Flexera license software has been reported as a cause for receiving this error. Flexera license software uses port 8080, (IMADMIN.EXE). Stop Flexera and retry Sigma. Changing Sigma from port 8080 to 8081 could also provide a solution. Added 27-08-2014 15. The SBO PCS (StruxureWare Building Operation Project Configuration Server) also uses port 8080.This needs to be stopped or will conflict with Sigma and produce the HTTP error. Added 02-09-2014 16. Make sure any data is backed up from the installed Sigma system. Uninstall Sigma using Add/remove programs (Win XP) or Programs and features (Win 7). Wait for the Sigma un-install process has completely finish. Delete or rename the C:\Sigma folder to.......for example Sigma1. Re-install Sigma by using a right mouse click on the "SigmaSetup.exe" file and select  A new clean Sigma folder will be created during the install. Once completed reboot the computer. Check the SIgma server is running and run up SIgma. Added 01-10-22014 17. The HTTP error can also caused if the computer name contains extended ASCII or Unicode. For example a computer named "Pást" may fail, if the computer name is changed to "Past" this may correct the HTTP problem. Added 23-11-2021 18. On SE laptops, the McAfee firewall has been updated: Go to McAfee (under hidden icons) > right click 'Quick Settings' > 'Enable Firewall Timed Groups'. This will provide a 1 hour window to run Sigma, in the McAfee pop up window. add a reason e.g. Sigma.
View full article
Picard Product_Support
‎2018-09-07 04:21 AM

Last Updated: Sisko DavidChild Sisko ‎2021-11-23 02:13 AM

Labels:
  • Satchwell BAS & Sigma
5375 Views

1.8k Thermistor compatibility with Xenta controllers

Issue Certain Xenta controllers and I/O modules can accept 1.8k thermistor temperature inputs. Product Line TAC Vista Environment Xenta 121-FC Xenta 200 Xenta 300 Xenta 420A Xenta 450A Cause What is the temperature vs resistance curve of the 1.8k thermistors for Xenta 300? Resolution All Xenta controllers and I/O modules, except the Xenta 102-AX use the same 1.8k thermistor (type 1.8KA1). The following table shows details the Temperature vs. Resistance characteristics for this thermistor. Temp (°C) Minimum kΩ Nominal kΩ Maximum kΩ -50.0   60.87  63.88  67.03  -45.0   45.41  47.5   49.68  -40.0   34.23  35.68  37.2   -35.0   26.04  27.07  28.13  -30.0   19.99  20.72  21.47  -25.0   15.48  16.0   16.54  -20.0   12.09  12.46  12.84  -15.0   9.512 9.779 10.05  -10.0   7.541 7.733 7.929 -5.0   6.021 6.16  6.301 0.0   4.84  4.94  5.042 5.0   3.916 3.988 4.061 10.0   3.189 3.24  3.293 15.0   2.612 2.649 2.686 20.0   2.151 2.177 2.209 25.0   1.782 1.8   1.818 30.0   1.478 1.496 1.514 35.0   1.233 1.25  1.267 40.0   1.033 1.049 1.065 45.0   0.8698 0.8848 0.9001 50.0   0.7357 0.7497 0.7639 55.0   0.6251 0.638 0.6511 60.0   0.5334 0.5453 0.5573 65.0   0.457 0.4679 0.479 70.0   0.3931 0.4031 0.4132 75.0   0.3395 0.3485 0.3578 80.0   0.2942 0.3025 0.311 85.0   0.2559 0.2634 0.2712 90.0   0.2233 0.2302 0.2373 95.0   0.1956 0.2019 0.2083 100.0   0.1718 0.1775 0.1835 105.0   0.1514 0.1566 0.1621 110.0   0.1338 0.1386 0.1436 115.0   0.1186 0.123 0.1276 120.0   0.1054 0.1095 0.1136 125.0   0.094 0.0977 0.1015 130.0   0.084 0.0874 0.0909 135.0   0.0753 0.0784 0.0816 140.0   0.0676 0.0705 0.0735 145.0   0.0609 0.0635 0.0663 150.0   0.0549 0.0574 0.0599
View full article
Picard Product_Support
‎2018-09-06 02:18 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-30 11:25 PM

Labels:
  • TAC Vista
5385 Views

AET basic troubleshooting steps

Issue The functionality of the different tools and/or software does not operate as expected. Issues can appear related to controller functionality or possibly issues with how the standard programs work.  Product Line EcoStruxure Building Operation Environment Automated Engineering Tool (AET) Project Configuration Tool (PCT) EcoStruxure Building Operation (EBO) Cause When the latest versions of software and firmware are not being used, previously identified issues can cause problems with downloads or the operation of controllers. In other situations, it is possible that the proper steps or tools are not being used correctly. This could require further instruction and information.  Resolution In most situations, the troubleshooting steps below will address a majority of issues encountered while working with the AET and the standard applications. EBO software and SmartX firmware being used should be at the latest version Between updates and fixes to the software/firmware, you should be using the latest versions found on the Exchange.  AET software should be up to date Between updates and fixes, make sure you are using the latest version of the AET software which can be found on the Exchange.  AET templates should be up to date You can reference the AET Quick Help - Downloading AET Templates video or the SmartVAV: Software Engineering Process document for further direction.  Understanding the proper way to use the Automated Engineering Tool There exist a number of AET Quick Help Videos available on the Community to help with AET user skills. If there are any topics not covered in a video that you are searching for, be sure to leave a post with the new video idea.
View full article
Administrator Cody_Failinger Administrator
‎2019-11-27 07:23 AM

Last Updated: Administrator CraigEl Administrator ‎2023-07-12 06:58 PM

Labels:
  • Automated Engineering Tool
  • EcoStruxure Building Operation
5368 Views

Controlling distribution of license modules in Vista 5

Issue When running TAC Vista in a Network environment, there are several ways of setting up the license system. Sometimes, TAC Vista nodes (Vista users) "steal" license modules for each other. Environment Vista in network Flexnet license Cause When various TAC Vista systems are pointed to the same license server, one server can take or "steal" e.g. an OPC Client license which another server should use. Resolution For a complete explanation about the license system and how to setup the system and control licenses, refer to this video. A useful tool to use is the Options file, with the .opt file extension. Located in the License files folder, its easily monitored in a text editor, and could be used for Reserving or Excluding license modules for other TAC Vista nodes. Other features available for the Options file can be found in the Flexnet Licensing End User Guide. 1: Make a file called taclic.opt and place it in the same directory as the license files. 2: Edit the file with notepad and make the reservations you need. The syntax for each line in the file is "command amount feature HOST host". The feature names can be seen in the license files. Here is an example on how to reserve an OPC Client license for a PC called "BMS_SERVER_1" RESERVE 1 Vista.Server.OPCClient HOST BMS_SERVER_1 3: Restart the license server.
View full article
Picard Product_Support
‎2018-09-10 04:32 AM

Labels:
  • TAC Vista
5381 Views

[Dev File] Xenta 5/7/9xx Modbus RTU Integration to Cummins ModLon 2 Gateway

Issue Integration to the Cummins ModLon 2 gateway with the Xenta 500 / Xenta 700 / Xenta 900 and Modbus RTU Product Line TAC Vista Environment Xenta 511, 527, 701, 711, 721 (5.1.5 up) Xenta 731, 913 (all versions) XBuilder Cummins ModLon 2 Gateway Cause Disclaimer: This device template is intended to provide a starting point for an integrator, and is in no way written to be the mandatory points list for your integration effort. Product Support Services-Dallas has written this device template in an effort to give our customers a starting point and solid example of how to develop a device template for the above product. The integrator will be responsible for any additions or modifications to this device template. Please report any problems to PSS Dallas at product.support@buildings.schneider-electric.com Resolution Please us the following .dev files as a starting point and a guide to the integration. This .dev file contains a set list of registers that PSS assumed would be seen as critical and important to the integration process. If any other data is needed please see this supported document to make the necessary changes. One generator: .dev file Two generators: .dev file   To use these files in Xbuilder please follow these steps: Extract the .dev file from the .zip file in the link above, and place it on your harddrive. In Xbuilder, right click on the Modbus Master device and chose Add Device Browse to the needed .dev file and choose Open. Rename the newly added device to a unique name within the Modbus Master network.
View full article
Picard Product_Support
‎2018-09-07 03:33 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-11 08:15 PM

Labels:
  • TAC Vista
5379 Views

Infinet and MSTP bus troubleshooting

Issue Troubleshooting steps for the Infinet and MSTP bus. Product Line Andover Continuum, EcoStruxure Building Operation Environment Continuum SmartStruxure RS-485 Infinet BACnet MSTP Cause Methods are needed to troubleshoot the Infinet and MSTP bus Resolution This is not a comprehensive list of all methods for troubleshooting, but a starting point. The Infinit-mstp troubleshooting document is available here. NOTE If BACnet MSTP devices do not support COV subscriptions, then care must be taken when reading values (eg EBO trends or alarms) as excessive traffic can be created that overwhelms the communication bus. For example, if 30 non-COV BACnet devices have EBO alarms (or EBO change of value trends) bound to 4 objects in each controller, this will create 240 packets (reads/replies) that will be attempted every "Minimum polling Interval". This is likely to fill the MSTP bus bandwidth  
View full article
Picard Product_Support
‎2018-09-10 12:30 AM

Last Updated: Dave_Shore Schneider Alumni (Retired) ‎2023-06-08 07:27 AM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
5323 Views

Getting javax.baja.xml.XException: Error parsing value error message when attempting to add a new driver network to the I/A Series G3 station's Drivers container.

Issue Getting javax.baja.xml.XException: Error parsing value error message when attempting to add a new driver network to the I/A Series G3 station's Drivers container. Drag and Drop - drag network container from palette and drop onto the Drivers container Copy and Paste - copy network container from palette and paste into the Drivers container Drivers Manager (New selection) - wizard to add new driver Error details displayed:  com.tridium.fox.session.ServerException: javax.baja.xml.XException: Error parsing value [38:4] Environment Enterprise Network Server, ENS, ENC, JACE Cause The module associated with the driver has not been installed in the local modules folder or remote station. Resolution Enterprise Network Server Stop Workbench Copy the missing module directly into ~\modules directory for the version of I/A Series G3 being used. Restart Workbench ENC or JACE Open the platform for the ENC/JACE Install the module using the Software Manager. A station reboot may be required.
View full article
Picard Product_Support
‎2018-09-11 04:31 AM

Labels:
  • TAC IA Series
5328 Views

Discovering Lon Devices in SmartStruxure

Issue How to discover MNL Lon devices or other Lon devices in an SmartStruxure Automation Server. Product Line EcoStruxure Building Operation Environment Building Operation Workstation Building Operation Automation Server Cause Use the below instructions when you need to find all Lon devices on a Lon network. Resolution To discover a LonWorks device In WorkStation, in the System Tree pane, select the server that is connected to the device you want to discover. Click the Device Discovery view. In the Select device type box, select LonWorks. Select the Devices folder. Right click on the Devices folder and take "Scan network for devices" In the Device Discovery view, ensure that the LonWorks device is displayed in the Devices folder. This may take up to 5 seconds. Drag the discovered device to the System Tree pane: Drag to an existing device to associate it with the discovered physical device. Drag to the LonWorks network to create the device.   NOTE: You cannot drag a standard MNL LonWorks device to the System Tree pane if the discovered device is in an unconfigured state For more information, refer to the Creating and Configuring a LonWorks Network with MNL LonWorks Devices [102423].pdf document 
View full article
Picard Product_Support
‎2018-09-11 02:56 PM

Last Updated: Janeway Jonas_Brissman Janeway ‎2022-03-17 02:39 AM

Labels:
  • EcoStruxure Building Operation
5315 Views
  • « Previous
    • 1
    • …
    • 14
    • 15
    • 16
    • …
    • 507
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of