We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.

"Login Failed - Could not connect to fox server. Check that fox and web SSL settings match or try connecting using https."

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "Login Failed - Could not connect to fox server. Check that fox and web SSL settings match or try connecting using https."
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • sesa116873_brid
    sesa116873_brid
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
5943 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"Login Failed - Could not connect to fox server. Check that fox and web SSL settings match or try connecting using https."

Picard Product_Support
‎2018-09-11 01:18 PM

Issue

Getting error message: “Login Failed - Could not connect to fox server. Check that fox and web SSL settings match or try connecting using https.” when trying to connect to G3 station via a web browser.

Product Line

TAC IA Series

Environment

In Niagara G3, Version 3.7.106

Cause

Security setting for the Web browser and Fox Service do not match, or the FOX or FOXS port is being blocked.

In Niagara G3, Version 3.7 and later, users can set up SSL for both HTTP and FOX connections. The intention is that, when using the applet, SSL settings for HTTP and FOX must match (i.e. HTTPS/FOX or HTTP/FOXS are not allowed).

In Niagara G3 3.7 update1 and earlier, users can connect to the applet using the invalid HTTPS/FOX combination. In addition, when loading the applet while using HTTP/FOXS, users are redirected back to the login screen with no error message.

In NiagaraAX 3.7 update2 and later, users attempting to use the applet with an invalid HTTPS/FOX or HTTP/FOXS connection will be redirected to the login screen. An error message will appear indicating what went wrong.

The Web and Fox settings do not match. They must be set to either HTTP/FOX or HTTPS/FOXS.

We’ve found that there is a condition where the error message still displays even though both Fox Service and HTTP match. Reason being is during login to a station via web browser, a check is performed to determine if the Fox Service match the HTTP setting be used. If accessing via HTTP, then port 1911 (FOX) is checked. If accessing via HTTPS, then port 4911 (FOXS) is checked. We found that the corresponding, FOX or FOXS, port were not opened. 

Resolution

Open the needed FOX or FOXs port:
Depending on if HTTP or HTTPS is used, the correct port must be opened for the corresponding FOX or FOXS connection. Port 1911 needs to be open if using HTTP/FOX connections, and if using HTTPS/FOXS, port 4911 needs to be open. Port need to be open to bidirectional TCP traffic.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 17571
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore