Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Schneider Electric
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register

Contact Support

Close

Ask our Experts

Have a question related to our products, solutions or services? Get quick support on community Forums

Email Us

For Community platform-related support, please email us

New Community Ranking System
Our Community ranking system has recently been updated. You may notice changes in user rankings and receive system messages or notifications. If you have questions about how the new ranking works, please refer to the announcement post for more details (click here).

Locked Setpoint adjustment from SE8000 Room Controller

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 

Select a Country

Please select a country to continue with beta search.

  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Locked Setpoint adjustment from SE8000 Room Controller
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6893 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Locked Setpoint adjustment from SE8000 Room Controller

Product_Support
‎2018-09-10 02:08 PM

Last Updated: ContentModerator Explorer ‎2025-09-25 02:51 AM

Issue

Once the occupied cooling and heating setpoints are written from a BMS, the user is not able to change the setpoint from the room controller

Product Line

EcoStruxure Building Expert, EcoStruxure Building Operation

Environment

  • Automation Server
  • Enterprise Server
  • SE8000 Series Room controller
  • Viconics branding VT8000 Series
  • Multi Purpose Manager (MPM)
  • BACnet

Cause

By default, the occupied setpoint value is written to Room Controller with priority level 16 by the BACnet front end. Attempting to change the setpoint locally using the up and down arrows on the SE8000 Room controller will not be allowed since the Room controller uses the relinquish value internally (priority 17) which will be automatically overwritten by the BACnet front-end.

Resolution

The work around is to release the BACnet front-end control over the BACnet object using a LUA4RC script. The script can be uploaded using one of the following two methods:

1 - Uploader Tool

A USB cable is required to upload the script. The uploader tool can be downloaded from the Exchange

  • Download Script
  • Download Uploader Tool

 

2 - BACnet

The script can also be directly uploaded via BACnet using the "Description" field as shown in the image below

if (ME.AV92 == 6 or ME.AV92 == 7) then ME.AV39_PV[16] =nil ME.AV39_PV[10] =nil ME.AV40_PV[16] =nil ME.AV40_PV[10] = nil ME.AV92_PV[17] =0 end

Where,

  • ME.AV92 is the Keyboard value
  • ME.AV39 is the Occupied Heating Setpoint
  • ME.AV40 is the Occupied Cooling Setpoint

download (3).png

Using this method, the script can be uploaded to multiple SE8000 Room Controllers by following the steps in Bulk Lua4RC upload via BACnet (Mass upload)

For more information about Lua4RC, refer to the Lua4RC Programming Guide

Labels (2)
Labels:
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
Attachments
SE8000_patch for AS_to release SP to PV_17.txt
Tags (5)
  • Find more articles tagged with:
  • 18706
  • se8300
  • se8350
  • se8600
  • se8650
Was this article helpful? Yes No
88% helpful (7/8)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2026 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore