SER8000 series room controllers communications options
  • SER8000 series room controllers communications options
  • CraigEl
    CraigEl
  • RyanSuar
    RyanSuar
  • RobertAndriolo
    RobertAndriolo
‎2018-09-11 06:27 AM
Last Updated: Administrator CraigEl Administrator ‎2022-08-11 07:49 PM
Integration to SER8000 room controllers via Modbus is required.
Currently, the SER8000 series room controllers communications options are Zigbee Pro or BACnet MS/TP. Refer to the SER8300 datasheet.
To communicate on Modbus RS-485, an option would be to use the multi purpose manager (MPM-UN) as a gateway device.
* Updated July 2015
As per Product Annoucement PA-00428, the SE8000 with firmware 1.3 can now act as a Modbus slave using the RS-485 port.
Labels (2)
  • EcoStruxure Building Expert
  • Field Devices
Tags (2)
  • 15817
  • protocols