Replacement of Satchwell ALE series Linear Actuator by Schneider Electric M800 Linear Actuator due to obsolescence. (Actuator Selection)

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Replacement of Satchwell ALE series Linear Actuator by Schneider Electric M800 Linear Actuator due to obsolescence. (Actuator...
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
7553 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Replacement of Satchwell ALE series Linear Actuator by Schneider Electric M800 Linear Actuator due to obsolescence. (Actuator Selection)

Picard Product_Support
‎2018-09-07 06:43 AM

Last Updated: Crewman ContentModerator ‎2025-08-11 03:59 AM

Issue

Satchwell ALE series Linear Actuator requires replacement.

Product Line

Field Devices

Environment

  • Satchwell ALE series Linear Actuator installed on Satchwell MJF, MZ, MZF, VJF, VSF, VZ or VZF series Plug and Seat Valve Body. 
  • Actuator type :- ALE series. 

Cause

Obsolescence of Satchwell ALE series Linear Actuator.

Resolution

Replace Satchwell ALE series Linear Actuator with Schneider Electric M800 Linear Actuator and Linkage Kit :-  

Linkage kit to mount a M800 actuator to a Satchwell valve (MZ,MZF, VZ, VZF, VSF and MJF) = L2SV

Replace ALE Actuator with M800 + L2SV combined part number 880-0650-000

Replace ALE with Auxilary Switch kit with M800-S2 + L2SV combined part number 880-0651-000

Just linkage kit = 880-0124-000

Just M800 = 880-0310-030

N.B. 

Should the Satchwell ALE series Actuator include a wired Auxiliary Switch then the following Accessory should also be installed on the S-E M800 Actuator as appropriate :- 

S2 - Two independent 24 volt 4amp AC-1 rated SPDT Auxiliary End Point Switches. (880-0104-000)

 

Particular care should be taken when selecting an Schneider Electric Forta M800 Actuator to replace an existing Satchwell ALE series Actuator.

The Schneider Electric Forta M800 Actuator may be used to replace an existing Satchwell ALE series Actuator but it should be noted that where an existing Satchwell ALE series Actuator has been connected directly to a Satchwell Controller, an independent Transformer rated to provide the greater level of power required by a single Schneider Electric Forta M800 Actuator (50VA) will also be required. (e.g. Schneider Electric Transformer Type TR60)  

Where an existing Satchwell ALE series Actuator has been connected via an independent Transformer, it is possible that the Transformer may have been rated to provide the level of power required by a single ALE series Actuator (9.5VA) only.  

In such circumstances the existing independent Transformer may also require replacement by another independent Transformer, rated to provide the greater level of power required by a single Schneider Electric Forta M800 Actuator (50VA) (e.g. Schneider Electric Transformer Type TR60)

Details of the Schneider Electric M800 Actuator may be viewed here

Details of the Schneider Electric TR60 Transformer may be viewed here

Labels (1)
Labels:
  • Field Devices
Attachments
Tags (2)
  • Find more articles tagged with:
  • 4662
  • GaryMontague22
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore