Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,860
  • TAC IA Series 1,828
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 335
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • ESMI Fire Detection 13
  • EcoStruxure Building Advisor 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 503
    • 504
    • 505
    • …
    • 509
  • Next »

SSC Fails to communicate

Issue After setting up an SSC controller, it does not come online even after multiple Resets and putting it into DFU Mode. Product Line Access Expert Environment Access Expert Windows Server 2012 Cause The device was previously set up, maybe at the office. Now, when taken out to site, it shows that it already exists on another instance. Resolution Open up the initial instance that it was set up on Right click and Delete the device Open up the new instance that it will be current on If already created, then communication should start automatically Once online, program accordingly
View full article
Picard Product_Support
‎2018-09-06 07:37 AM

Labels:
  • EcoStruxure Access Expert
2030 Views

How to setup custom ABA cards using Continuum NetController or ACX57xx

Issue Sites need guidance on how to setup custom ABA cards in Continuum. Environment CyberStation NetController I (CX99xx) NetController II (CX9680) AC1Plus IOU Module ACX57xx Cause The implementation of ABA cards in Continuum access control systems was designed to comply with the ISO 7811 ABA standard for magnetic stripe card. Because of this, the system only reads  one field (the PAN or Primary Account Number) from the ABA card, this field contains a number of up to 19 digits which is used as the card number. Continuum Custom ABA feature provides for maximum flexibility by allowing the 19 digit PAN field on track 2 of the mag stripe to be organized in sub fields such as site code etc. Resolution A summary of the steps to configure Custom ABA cards in Continuum is available through the CyberStation Online Help.  Open the help on the Continuum workstation and search for "Defining a Custom ABA String Format"          
View full article
Picard Product_Support
‎2018-09-11 05:35 PM

Labels:
  • Andover Continuum
2413 Views

Under objects such as Doors and Inputs what is the "Commands" option used for?

Issue Under objects such as Doors and Inputs what is the "Commands" option used for? Product Line Security Expert Environment Security Expert Cause Unsure how to use the Commands option showing in some of the objects options. Resolution These cannot be adapted for general use by installers/integrators. These are mostly used for controller instructions that have been included in the firmware but have not been built into the UI yet, as well as internal testing. Leave these alone unless you have a specific need and the instructions from Product Support on how to configure the command.
View full article
Picard Product_Support
‎2018-09-06 07:36 AM

Labels:
  • EcoStruxure Security Expert
1536 Views

Using a non-default SQL Server port with Continuum.

Issue Using a non-default SQL Server port with Continuum. Environment Continuum Workstation SQL Server Cause SQL Server has been changed from the default port setting and  confirgured with a specific static port for incoming SQL connections. Resolution Continuum doesn’t care if the SQL Server is using a default port or not. As long as the Database can be created/updated using the Database Initialization application it will work fine. This has not been tested or qualified but should work fine. After the port is changed, the user should perform the Database Update process to ensure that the connection can be made from Continuum to SQL Server and vice versa. Here’s a Microsoft article on how to change the SQL port. https://support.microsoft.com/en-us/help/823938/how-to-configure-sql-server-to-listen-on-a-specific-port
View full article
Picard Product_Support
‎2018-09-10 08:18 PM

Labels:
  • Andover Continuum
1503 Views

How to generate an invalid attempt alarm

Issue How to generate an invalid attempt alarm. Product Line Security Expert Environment Security Expert Cause It is not clear how an alarm for an invalid attempt at a Door is configured. Resolution The easiest way to setup an alarm to trigger when an invalid attempt is made at a reader is to trigger an Alarm off of the required Event. An example would be: Under Events create a new Event Filter, go to Event Types tab, un-tick "Include all event types" and add the events you want to monitor. In this case "User Door Group Not Valid At Door Using Access Level" should suffice as a start. To ensure you have the correct events you can create the event condition and confirm exactly what the event recorded is. Under Events create a new Alarm and set the Event Filter to the Event filter you created in step 1. Under Monitoring setup a Status Page that includes All Alarms (or alternatively is filtered for the specific alarms you want to see).
View full article
Picard Product_Support
‎2018-09-06 07:34 AM

Labels:
  • EcoStruxure Security Expert
1734 Views

Using the Save command in Plain English programs

Issue When the Save statement is used to save objects in a BCX4040 to the database. Steps to reproduce problem: Create an InfinityString object (Test.Str) with a manual array size of 1 in a BCX4040. Create a program in the BCX that sets the value of Test.Str[1] to 'Success' From command line, print the value of Test.Str[1] while the workstation is in OnLine mode. The value should = 'Success' From command line, print the value of Test.Str[1] while the workstation is in Offline mode.  No value should be returned as the value has not been updated in the database. Create a fallthrough/autostart program in the workstation with the following code: FIRSTLINE: Save \TestNet\TestACX\Test.Str -0 Goto StopLine STOPLINE: Stop From command line, print the value of Test.Str[1] while the workstation is in Offline mode.  The value should now = 'Success'.  Expected result: The value returned for Test.Str when the workstation is in Offline mode (Database value) should 'equal the value returned when the workstation is in Online mode (Live Value), i.e. = Success' Actual result: The Offline value of Test.Str[1] does not change and does not equal the value live value. The resulting ACC_Dump_Debug that is produced is found to have no contents. Product Line Andover Continuum Environment Continuum  Plain English Cause The following Plain English code does not accomplish a Save to Database. FIRSTLINE: Save \TestNet\TestACX\Test.Str -0 Goto StopLine The functionality of the Save command is not to perform a "Save to Database" operation. This is a functioning as designed. The Save command, which is equivalent to the Dump command, dumps the contents of the passed-in arguments (i.e. objects) to a file if provided Resolution Workaround: When a manual Save to Database is done on the object, the database value is updated with the current Live value.
View full article
Picard Product_Support
‎2018-09-06 07:34 AM

Labels:
  • Andover Continuum
1389 Views

Default List views are missing columns after being re-created with Continuum database initialization update database option.

Issue After a missing or deleted default list view is re-created using the Continuum database initialization utility; the list view does not contain any columns. Environment Cyberstation Cause This issue is caused by a Continuum defect issue that cannot be corrected at this time. QC#2222. Resolution There are several workarounds that can be used to resolve this issue. 1)      Columns can be manually added back to the list views re-created by the database update option. 2)      The default list views can be reimported from the DefaultListViews.dmp file in the Continuum folder.  This would overwrite all default list views there by losing any customization to existing list views. 3)      Individual list views can be imported from a dump file created from another Continuum Systems to provide pinpointed recovery of certain listviews.
View full article
Picard Product_Support
‎2018-09-10 12:55 PM

Labels:
  • Andover Continuum
1154 Views

Error when saving photo in Badge Manager: Invalid width/height -11

Issue After selecting a photo and trying to save it in the Image Enhancement screen, the error Invalid width/height -11 pops up.   Environment Cyberstation Cause This is caused by the resize box under the capture options being checked and the sizes being set to 0. Resolution This can be resolved by one of the following suggestions below:   Uncheck the resize box under the capture options Set the x: and y: options to something other than 0
View full article
Picard Product_Support
‎2018-09-10 11:41 AM

Labels:
  • Andover Continuum
1524 Views

License no longer appears in License Administrator after re-installing Open Minds HAS.

Issue After re-installing Open Minds HAS causes, the license no longer appears in License Administrator. Environment License Open Minds HAS 8.6   Cause Re-installing LifeKeeper may have affected License Administrator installation due to the Open Minds volume monitor. Resolution Re-install License Administrator. Licese will show and operate after re-installation.
View full article
Picard Product_Support
‎2018-09-06 07:32 AM

Labels:
  • EcoStruxure Building Operation
1284 Views

Supported web-browsers for Access Expert hosted instance

Issue It is not documented what web-browsers should be used with an Access Expert hosted instance. Product Line Access Expert Environment Access Expert hosted instance - V2 & V3 Cause It is necessary to know what web-browsers should be used with an Access Expert hosted instance. Resolution IE 11 or Google Chrome should be used to logon to an Access Expert hosted instance. Firefox is NOT a supported web-browser and should not be used. 
View full article
Picard Product_Support
‎2018-09-06 07:32 AM

Labels:
  • EcoStruxure Access Expert
1635 Views

How to configure heating on SE7600X

Issue Unable to turn the heat on SE7600X   Environment   SE7600 Cause Wiring issue or misconfiguration Resolution You may refer to the diagram below to avoid wiring mistakes. Do not forget  jumper J1 on terminals |RC |RH|     Configuration Two important parameters to configure for heating.   Number of heating stages.  Default value = 2 stages When selected the device will revert the operation of 2 stages thermostat to single stage operation or to modulating 0 to 10Vdc heating output: 0 = 0-10Vdc analog heating output (AO) 1 = 1 heating stage (W1) 2 = 2 heating stages (W1 & W2)   Fan control Default value = On When selecting on; the Terminal Equipment Controller in all cases will always control the fan (terminal G). Valid for On or Auto fan mode When selecting Off; the fan (terminal G), when heating stages (terminals W1 & W2) are solicited, will not be energized. The fan in this case will be controlled by the equipment fan limit control. Valid only for Auto fan mode.   On fan mode will leave the fan always on. For multistage models, fan control applies to W1 & W2 For heat pump models, fan control applies to W1 only (Emergency heat)
View full article
Picard Product_Support
‎2018-09-10 09:47 AM

Labels:
  • EcoStruxure Building Expert
  • Satchwell BAS & Sigma
1395 Views

Where can I find the details for UK and Ireland Smartstruxure or EcoStruxure partners.

Issue Locating partners Environment Partner SmartStruxure Building Operation EcoStruxure Building Operation Cause Require engineer to visit for maintenance, servicing, installation or advice. Resolution Click Here to be linked to the available UK and Ireland SmartStruxure / EcoStruxure partner list. Note: For Ireland, enter Belfast, and partners in Ireland will also be shown.
View full article
Picard Product_Support
‎2018-09-10 08:51 AM

Labels:
  • EcoStruxure Building Operation
1382 Views

Alarm Control Panel - Number of entries for Cause Note, Action Note and Checklist

Issue Alarm Control Panel - Number of entries for Cause Note, Action Note and Checklist  Environment SnartStruxure Building Operation Workstation 1.9 Cause The maximum number of entries that can be added for Cause Note, Action Note and Checklist are not indicated in available documentation.  Resolution There are no hard coded limits to the number of entries that can be added for the Cause Note, Action Note and Checklist
View full article
Picard Product_Support
‎2018-09-06 07:31 AM

Labels:
  • EcoStruxure Building Operation
1363 Views

I/A Series G3 and N4 - Eliminating multiple Host ID on a single Microsoft Windows platform

Issue The hostId for a computer running I/A Series G3 version 3.8u1 (or earlier) and N4 versions 4.2 (or earlier) may be changed from the result of a Windows update. Product Line TAC IA Series Environment I/A Series G3  I/A Series N4  Cause The hostId is automatically generated upon first install of the software and stored within the registry.  The location of the G3 versions 3.8u1 or (earlier) and N4 versions 4.2 or (earlier) registry keys can be affected by a Windows update. the G3 versions 3.8u1 or (earlier) and N4 versions 4.2 or (earlier) registry keys can be affected by a Windows update.The hostId is automatically generated upon first install of the software and stored within the registry.  The location of    the G3 versions 3.8u1 or (earlier) and N4 versions 4.2 or (earlier) registry keys can be affected by a Windows update. Resolution I/A Series G3 version 3.8.213 (or higher) and I/A Series N4 version 4.3.58.18 (or higher) have been modified to guard against Windows updates to prevent hostId changes.  Installations of N4 4.3 and/or G3 3.8u2 will continue to operate normally and will not assume a new hostid after a Windows update.  All previous versions of Niagara could generate a new hostid after a Windows update, requiring a license replacement.   Schneider Electric recommends updating I/A Series G3 and N4 installations to the latest released software in order to maintain the latest security protection and to gain benefit from the latest features.  These builds are:   I/A Series 3.8 Update 2 (3.8.213 and later) I/A Series 4.4 (and later)   Patch to address multiple Host IDs on a single Microsoft Windows© platform   A set of patch files have been created to stabilize the Host ID for cases where customers have not upgraded to the latest version of Niagara (see installation instructions below). Once these patches are applied to the older versions of Workbench the Host ID is stabilized and should not change if Windows updates are installed.   Note: This is a reminder that a 32-bit install will always generate a different host-id than a 64-bit install.   IMPORTANT NOTES REGARDING THE PATCHES   Patches are only supported for the latest update (maintenance) version for the relevant release. Patches are not available for I/A Series G3 release 3.5 and earlier, or I/A Series N4 release 4.0 or 4.1. Builds prior to G3 3.8.213 are considered unsupported. Customers applying these patches do so at their own risk. Newer versions of Niagara (3.8U2 and 4.3) have introduced a stabilized method of managing the Host ID and do not require any patch. The patches do not eliminate the issue of different Host IDs generated when installing 32-bit and 64-bit Niagara. Installation Instructions   The Host ID patch file is available for download on the EcoBuilding Exchange Download website.  Login to the Schneider Electric EcoBuilding Exchange Download Center and enter G3 and N4 Host ID Patches in the search area or the filename of the zip shown below.    Download the G3_N4_HOSTID_PATCHES.zip and unzip into a temporary folder. The archive contains 'nre.dll' for various versions of I/A Series G3 and Series 4.2 in a directory structure identifying them first by version and sub-directory identifying 64-bit or 32-bit Windows. The 4.2 folder also contains 'njre.dll' which will need to be copied only for 4.2 installations.  Follow these instructions:   Verify the installed java version to be either 64-bit or 32-bit. Start a Niagara Command Line (Home>/bin/console.exe) from the desktop of the platform to be patched. From the Niagara Command Line execute the command: nre -version One of the listed items will be java.vm.name. If the text contains “64-Bit” then the installation is 64-bit otherwise the installation is 32-bit. Stop any running station using Workbench's Platform Application Director on the platform to be patched. Exit Workbench if running on the platform to be patched. From the Niagara Command Line ... /bin/console.exe execute the command: plat uninstalldaemon  Prior to replacement, save a copy of the existing nre.dll located in /bin folder. If Niagara 4.2 is being updated also save a copy of the existing njre.dll located in /bin folder. Copy the version appropriate and OS appropriate (64-bit or 32-bit) downloaded version of nre.dll file to the Home>/bin folder. If Niagara 4.2 also copy njre.dll to /bin folder. Overwrite the existing file(s). From the Niagara Command Line (/bin/console.exe) execute: plat installdaemon Start Workbench.  Open a platform connection to the patched platform. Using the Application Director, start the station.  
View full article
Picard Product_Support
‎2018-09-10 10:04 AM

Labels:
  • TAC IA Series
2764 Views

Report Server Localisation

Issue Customers want to know how to localise their Reports Server  Environment SBO 1.9.3. Cause User may wish to change language on produced Reports etc.. Resolution Localisation of the Reports Server is currently not supported although there are plans to add this feature in a later revision.
View full article
Picard Product_Support
‎2018-09-06 07:31 AM

Labels:
  • EcoStruxure Building Operation
2030 Views

Badge Printing in Access Expert Version 3

Issue Unable to print a badge preview when designing a layout in Access Expert Product Line Access Expert Environment Access Expert Win8.1 Premise Hosted SQl 2012 R2 SQL 2014 Cause Operating system incompatibility with version 3. Version 3 only support Windows 8.1 and above. Resolution If the user is running Windows 7, the Preview will not work. Use a compatible OS, like Windows 10, and try again.
View full article
Picard Product_Support
‎2018-09-06 07:31 AM

Labels:
  • EcoStruxure Access Expert
1519 Views

Personnel Manager not operating correctly but Personnel Editor is fine

Issue Personnel Manager not operating correctly but Personnel Editor is fine Product Line Andover Continuum Environment Seen in Continuum 1.94 Cause Personnel Manager seems to run correctly but the Area names, Assigned and Unassigned data does not show correctly and cannot be modified. Blank spaces at the end of the Area Names or Alias cause the Peronnel data (Assigned and Unassigned Areas) to show incorrectly in Personnel Manager, but all correct in Personnel Editor. Resolution Remove the spaces at the end of the Area Names and Aliases Restart Continuum
View full article
Picard Product_Support
‎2018-09-06 07:31 AM

Labels:
  • Andover Continuum
1500 Views

Converting an Access Expert site from V2 to V3

Issue Needing to convert a site from V2 to V3. Product Line Access Expert Environment Win 8.1 and above Hosted Version 2 Version 3 Cause There are no directions on how to convert a Hosted Site on V2 to V3. Resolution When converting from V2 to V3 there are a few things that need to be verified first before attempting this action: Verify that the site does not have any SSC's that are configured as FN-4502, this information would have to be passed on prior to attempting the conversion by creating a case with your local country support group. Once the all clear has been given by product support, then the process can be started. Using two monitors bring up an instance on each for comparison Verify that all users, Access Levels, Schedules, Trigger and Procedures etc are in place Once confident, then connect to each SSC and change the Host IP name from the xxx.accessxpert.com to us.accessxpert.com Click on the View All Hardware Icon to see when the SSC comes online Once this happens, click on the Update firmware to get to the latest version downloaded to the controller When the device comes back online, verify that all the sub devices comes online as well If not then perform a Push Controller Database to the controller again When the controller comes online, all the subdevices should come online as well as Readers etc. At this point everything in V2 will become Unknown and can then be deactivated
View full article
Picard Product_Support
‎2018-09-06 07:30 AM

Labels:
  • EcoStruxure Access Expert
2398 Views

Enrollment Reader in Access Expert

Issue Need to a method to automatically enroll users into Access Expert? Product Line Access Expert Environment Premise Install Hosted Instance Cause Enrollment readers are not used in Access Expert.  Resolution When a card is read at the Door Reader, it will result in an "Access Denied/Card Pin Not Found" event being generated. This event can then be used to create a new user. Once this user has been created and added to the system, the card will become active and have access to the doors it's assigned to. 
View full article
Picard Product_Support
‎2018-09-06 07:30 AM

Labels:
  • EcoStruxure Access Expert
1895 Views

Locked in SmartXKiosk after first-time startup before a password has been set

Issue After starting up the SmartX Advanced Display for the the first time, the operator finds himself stuck in SmartXKiosk mode before having any chance to select a password/PIN code. Product Line EcoStruxure Building Operation Environment Advanced Display v1 Advanced Display v2 Cause SmartXKiosk has been selected as launcher. The first time the SmartX Advanced Display is booted up the operator is presented of a choice to use  SmartXKiosk or TouchWiz as launcher. If SmartXKiosk then is selected instead of TouchWiz the operator will enter SmartXKiosk without having set a password first. Resolution Request an unlock code (PIN) from your local support center, which will enable the operator to exit Kiosk Mode. Press the Home (Hardware) Button at the SmartX Advanced Display. This will enable you to choose launcher again. Make sure that "TouchWiz" is selected. Note: In the next release this will note be an issue, since you are forced to select "TouchWiz" at first use to proceed (if SmartXKiosk is selected, you will be prompted to choose again)
View full article
Picard Product_Support
‎2018-09-06 07:29 AM

Labels:
  • EcoStruxure Building Operation
1986 Views
  • « Previous
    • 1
    • …
    • 503
    • 504
    • 505
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore