I/A Series G3 and N4 - Eliminating multiple Host ID on a single Microsoft Windows platform

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A Series G3 and N4 - Eliminating multiple Host ID on a single Microsoft Windows platform
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • RyanSuar
    RyanSuar
  • WaynePeters
    WaynePeters
  • Leo_Tantalo
    Leo_Tantalo
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
1 Like
2628 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A Series G3 and N4 - Eliminating multiple Host ID on a single Microsoft Windows platform

Picard Product_Support
‎2018-09-10 10:04 AM

Issue

The hostId for a computer running I/A Series G3 version 3.8u1 (or earlier) and N4 versions 4.2 (or earlier) may be changed from the result of a Windows update.

Product Line

TAC IA Series

Environment

  • I/A Series G3 
  • I/A Series N4 

Cause

The hostId is automatically generated upon first install of the software and stored within the registry.  The location of the G3 versions 3.8u1 or (earlier) and N4 versions 4.2 or (earlier) registry keys can be affected by a Windows update.
the G3 versions 3.8u1 or (earlier) and N4 versions 4.2 or (earlier) registry keys can be affected by a Windows update.The hostId is automatically generated upon first install of the software and stored within the registry.  The location of 
 
the G3 versions 3.8u1 or (earlier) and N4 versions 4.2 or (earlier) registry keys can be affected by a Windows update.

Resolution

I/A Series G3 version 3.8.213 (or higher) and I/A Series N4 version 4.3.58.18 (or higher) have been modified to guard against Windows updates to prevent hostId changes.  Installations of N4 4.3 and/or G3 3.8u2 will continue to operate normally and will not assume a new hostid after a Windows update.  All previous versions of Niagara could generate a new hostid after a Windows update, requiring a license replacement.
 
Schneider Electric recommends updating I/A Series G3 and N4 installations to the latest released software in order to maintain the latest security protection and to gain benefit from the latest features.  These builds are:
 
  • I/A Series 3.8 Update 2 (3.8.213 and later)
  • I/A Series 4.4 (and later)
 
Patch to address multiple Host IDs on a single Microsoft Windows© platform
 
A set of patch files have been created to stabilize the Host ID for cases where customers have not upgraded to the latest version of Niagara (see installation instructions below). Once these patches are applied to the older versions of Workbench the Host ID is stabilized and should not change if Windows updates are installed.
 
  • Note: This is a reminder that a 32-bit install will always generate a different host-id than a 64-bit install.
     
IMPORTANT NOTES REGARDING THE PATCHES
 
  • Patches are only supported for the latest update (maintenance) version for the relevant release.
  • Patches are not available for I/A Series G3 release 3.5 and earlier, or I/A Series N4 release 4.0 or 4.1.
  • Builds prior to G3 3.8.213 are considered unsupported. Customers applying these patches do so at their own risk.
  • Newer versions of Niagara (3.8U2 and 4.3) have introduced a stabilized method of managing the Host ID and do not require any patch.
  • The patches do not eliminate the issue of different Host IDs generated when installing 32-bit and 64-bit Niagara.

Installation Instructions
 
The Host ID patch file is available for download on the EcoBuilding Exchange Download website.  Login to the Schneider Electric EcoBuilding Exchange Download Center and enter G3 and N4 Host ID Patches in the search area or the filename of the zip shown below. 
 
Download the G3_N4_HOSTID_PATCHES.zip and unzip into a temporary folder. The archive contains 'nre.dll' for various versions of I/A Series G3 and Series 4.2 in a directory structure identifying them first by version and sub-directory identifying 64-bit or 32-bit Windows. The 4.2 folder also contains 'njre.dll' which will need to be copied only for 4.2 installations.  Follow these instructions:
 
  1. Verify the installed java version to be either 64-bit or 32-bit. Start a Niagara Command Line (Home>/bin/console.exe) from the desktop of the platform to be patched.
  2. From the Niagara Command Line execute the command: nre -version
  3. One of the listed items will be java.vm.name. If the text contains “64-Bit” then the installation is 64-bit otherwise the installation is 32-bit.
  4. Stop any running station using Workbench's Platform Application Director on the platform to be patched.
  5. Exit Workbench if running on the platform to be patched.
  6. From the Niagara Command Line ... /bin/console.exe execute the command: plat uninstalldaemon 
  7. Prior to replacement, save a copy of the existing nre.dll located in /bin folder. If Niagara 4.2 is being updated also save a copy of the existing njre.dll located in /bin folder.
  8. Copy the version appropriate and OS appropriate (64-bit or 32-bit) downloaded version of nre.dll file to the Home>/bin folder. If Niagara 4.2 also copy njre.dll to /bin folder. Overwrite the existing file(s).
  9. From the Niagara Command Line (/bin/console.exe) execute: plat installdaemon
  10. Start Workbench. 
  11. Open a platform connection to the patched platform.
  12. Using the Application Director, start the station.
 
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 19713
Was this article helpful? Yes No
100% helpful (2/2)

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of