Forta actuator zero point check/adjustment on power up
  • Forta actuator zero point check/adjustment on power up
  • RyanSuar
    RyanSuar
‎2018-09-06 07:27 AM
Is there an option to disable the Forta actuator zero point check/adjustment on power up?
Schneider Electric Forta actuators
The Forta actuator running the zero point check/adjustment on power up is causing an issue in the control sequence of the plant.
It is not possible to disable the zero point check/adjustment on power up of the the Forta actuator by any configuration of the dipswitches. The function is coded into the actuator firmware.
  • Field Devices
Tags (5)
  • 19979
  • end
  • m1500
  • m400
  • m800