Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,856
  • TAC IA Series 1,827
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 333
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • ESMI Fire Detection 13
  • EcoStruxure Building Advisor 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 249
    • 250
    • 251
    • …
    • 509
  • Next »

Issues installing SQL Server 2016 on Windows Server 2012R2

Issue Receiving message that KB2919355 must be installed when installing SQL Server 2016 on Windows Server 2012R2 Product Line Andover Continuum, EcoStruxure Building Operation, TAC Vista Environment Microsoft SQL Server 2016 Windows Server 2012R2 Cause To Install SQL 2016 on Windows Server 2012R2 you must have KB2919355 installed. Resolution To install KB2919355 you must first install KB2919442.  Once this patch is installed then you will need to install KB2919355.  After this patch is installed you will need to restart the server.  After the reboot you should be able to restart the SQL server install and complete it. Links for the required patches Download Windows update KB2919442 Download Windows update KB2919355
View full article
Picard Product_Support
‎2018-09-10 09:03 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2019-09-04 04:57 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • TAC Vista
1881 Views

Fiber cabling information for an Infilink i2210 and the B-link-F Series

Issue What are the fiber cabling specifications for an Infilink i2210? Product Line Andover Continuum Environment Infinet Infilink i2210 Mstp B-link-F Series Cause Fiber connections have specific parameters to work properly Resolution From the I2210 and B-link-F Series Installation Guides Fiber Optic cable: 62.5/125 duplex glass multimode fiber optic cable with ST-style connector Maximum attenuation allowable: 12 db For some additional information related to fiber optic terminology, see the following: https://arcelect.com/fibercable.htm
View full article
Picard Product_Support
‎2018-09-07 11:57 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-09-04 12:41 PM

Labels:
  • Andover Continuum
1533 Views

B-Link Repeater with EcoStruxure Building Operation

Issue Can B-Link repeaters be used with EcoStruxure Building Operation? Product Line EcoStruxure Building Operation Environment EcoStruxure Building Operation site release 1.xxx and higher Cause Need to add repeater(s) for EcoStruxure Building Operation Resolution For communication using RS-485, the versions of B-Link BACnet MS/TP Repeaters repeaters shown below were tested and passed for EcoStruxure Building Operation use. Part Number Description B-LINK-AC BACnet MS/TP Repeater, 120/240VAC B-LINK-AC-OP BACnet MS/TP Repeater, 120/240VAC, open class no enclosure B-LINK-AC-S B-LINK, AC, SMK B-LINK-DC BACnet MS/TP Repeater, 24VDC B-LINK-DC-OP BACnet MS/TP Repeater, 24VDC, open class no enclosure B-LINK-DC-S B-LINK, DC, SMK B-LINK-F-AC B-LINK, AC, FIBER B-LINK-F-AC-S B-LINK, AC, FIBER, SMK B-LINK-F-DC B-LINK, DC, FIBER B-LINK-F-DC-S B-LINK, DC, FIBER, SMK   Note the supported cable diameter in microns: 62.5/125. The first number, 62.5, refers to the diameter of the fiber cable's core. The second number, 125, refers to the diameter of the outside of the fiber cable's cladding. For more information see: BACnet b-Link MS-TP Repeaters - Andover Continuum - Specification Sheet b-Link Series - Andover Continuum - Installation Sheet Additional information about Fiber diameters from The Fiber Optic Association Fiber cabling information for an Infilink i2210 and the B-link-F Series
View full article
Picard Product_Support
‎2018-09-06 01:48 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-09-04 12:40 PM

Labels:
  • EcoStruxure Building Operation
4341 Views

Can not print TGML graphic from TGML editor

Issue Can not print a TGML graphic from the TGML editor, get error message, "Could not print string was not recognized as valid date time." Product Line TAC Vista Environment TAC graphic editor version 5.1.5 Cause A defect is written for this problem. Resolution This problem is fixed in TGML editor 5.1.6
View full article
Picard Product_Support
‎2018-09-06 10:37 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-09-04 08:21 AM

Labels:
  • TAC Vista
1152 Views

Invalid user name or password when creating a Continuum database on SQL Express

Issue When creating a new database an error pops up that indicates that the Windows login name or password is invalid. Product Line Andover Continuum Environment Continuum Windows XP Windows Vista Windows 7 Windows Server 2003 Windows Server 2008 Cause There is already a Continuum database created. Permissions for the Windows user are not allowing the database creation. Resolution Check to see if there are Continuumdev and ContinuumLog files in the folder. (Look for the folder path in database initialization) Use My Computer to navigate to that folder and see if the files already exist. If they do, copy them if needed and then delete them. Try the database creation again after that. The Windows user may not have the appropriate permissions as an admin Create a new local admin user and then login using the new login Try the database creation 
View full article
Picard Product_Support
‎2018-09-06 11:01 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-09-04 08:03 AM

Labels:
  • Andover Continuum
1685 Views

StruxureWare Building Operation Workstation cannot log on to Localhost:80

Issue StruxureWare Building Operation Workstation Logon fails when logging onto Localhost:80. Product Line EcoStruxure Building Operation Environment Windows 7 Windows 2008 Server Windows 2008 Server R2 Cause The line in the system Host file that defines the Localhost is commented out with a hash or pound sign (#). #127.0.0.1 Localhost Resolution Open Notepad. Right-click and select the option to "Open as an Administrator." Go to C:\windows\system32\drivers\etc and open host. Remove the # in front of 127.0.0.1 Localhost Save the file.
View full article
Picard Product_Support
‎2018-09-06 12:28 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-09-04 07:57 AM

Labels:
  • EcoStruxure Building Operation
2696 Views

Migrating Users from SP-C-WEB to Security Expert

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Require details on how to migrate Users from an SP-C-WEB to Security Expert. Product Line Security Expert Environment SP-C-WEB Security Expert Cause Have a site that has outgrown it's SP-C-WEB installation and is upgrading to Security Expert to expand. Resolution Door configuration and programming cannot be migrated from an SP-C-WEB installation to Security Expert, but the User database can be exported to a CSV file and then imported into Security Expert to help with the migration. Exporting User database from SP-C-WEB to CSV file From the SP-C-WEB user interface navigate to Users | User Search. In the User Search page on the top right (under date) is the Export button. Clicking the Export button will generate a .csv file of all User details. (See attached example Exported Users.zip) Editing User CSV file for importing into Security Expert The Security Expert User import requires the CSV file to be in a specific format: FirstName,LastName,FullName,Facility,Card,PIN,AccessLevel The rules for this format are that: Each field must have a value however the firstname/lastname can be omitted if the fullname is used and vice versa. The facility can be omitted if it is prepended to the card number and separated with a colon (eg 123:4567). If a matching Access Level is not found, a new access level is created. The PIN and Card must be unique for each user. The file cannot contain a header row. Some examples of correctly formatted data are: Joe, Stanley,Joe Stanley,123,4587,1418,Warehouse Staff Georgia, Smith,,123,4654,6884,Warehouse Staff ,,Billy Randall,123,4727,3492,Warehouse Staff Frank,Powell,,,123:4639,3160,Warehouse Staff Importing Users from a CSV File into Security Expert In the Security Expert Client navigate to Sites | Import Users to launch the Import Users Wizard. Browse to and select the CSV File you wish to import the users from, then click OK. Figure 1 - User Import Dialog The Users records are created and a message is displayed to indicate the action was successful.
View full article
Guinan AdamSteele Guinan
‎2019-02-24 09:57 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2019-09-03 09:01 PM

Labels:
  • EcoStruxure Security Expert
2333 Views

Automation Server Time Format for Schneider Electric Energy Online Query Tool

Issue Schneider Electric Energy Online Query Tool requires log data collected to be in 24 hours time format. Product Line EcoStruxure Building Operation Environment SmartStruxure Automation Server Cause The Automation Server time display format (24 hours or 12 hours) is dependent on the settings of the computer where the client application is installed. In StruxureWare Building Operation, this would normally be the WorkStation software. If the computer which the Workstation software is installed is set for 24 hours time format, then the AS date and time, Trend charts etc. will display the time in 24 hours format. Resolution The Query Tool documentation indicates that it gets data from the StruxureWare Building Operation server (in this case, an AS) and creates the required output format (CMEP, ERM or Vizelia). In this case, the Automation Server time format does not matter. It is the time format settings of the computer where the Query Tool is installed that matters. Ensure that the Query Tool computer time is in 24 hours format.
View full article
Picard Product_Support
‎2018-09-06 10:02 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-09-03 08:00 AM

Labels:
  • EcoStruxure Building Operation
1454 Views

Video Tutorial on How to Install and Configure the Continuum Reports Suite

Issue Procedure to Install and Configure Continuum Reports Suite Product Line Andover Continuum Environment Continuum Reports Suite Cyberstation 1.81 and above Cause Need to generate Continuum Reports using the Continuum Reports suite package Resolution
View full article
Picard Product_Support
‎2018-09-11 12:55 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-09-03 07:22 AM

Labels:
  • Andover Continuum
2200 Views

Master node in a Vista network.

Issue What is the role of the master node in a Vista network? Product Line TAC Vista Environment Vista server Cause In a network with several nodes (Operator units), one node is designated as the Master node of the database in the network Resolution The Master node is the node which contains the correct information about global objects. Information about global objects is controlled by the Master node, and if the information has changed, the other nodes (Slave nodes) will copy this information when they contact the Master node. So if the master is down the slaves cannot add/delete any global objects such as users. The other nodes will continue working normally even if the master is down.
View full article
Picard Product_Support
‎2018-09-06 01:18 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2019-09-01 09:13 PM

Labels:
  • TAC Vista
1066 Views

"Error getting root folder name" when launching Personnel Manager

Issue Personnel Manager displays "Error getting root folder name" when launching. Product Line Andover Continuum Environment CyberStation Personnel Manager (PIM) Cause At boot time, Personnel Manager queries the ContinuumDB to find the Root container by ID using the following SQL query: SELECT uiname FROM Dictionary WHERE objectidhi = 0 AND objectidlo = 536870913  "Error getting root folder name" will be generated if PIM is unable to access the ContinuumDB or can not find the root object for any other reason. Resolution The User account control slider on a Windows 7 PC will need to be moved all the way to the bottom. Check/resolve for database connectivity errors. Make sure Firewall settings are not preventing the PIM from getting to the SQL server. If the problem persists try the following:   Check to see if Badgemanager.exe is starting. If not then a perform clean uninstall of EpiBuilder with the following steps: From Add/Remove programs (Programs and Features in Windows 7) Uninstall Run Regedit (Start > Run > regedit) Get a registry back by Right clicking on HKey_Local_Machine\Software\ImageWare Systems\EpiBuilder  and select Export and save the selected branch to a file location. This can be used to restore the registry key if necessary. Windows 7: HKey_Local_Machine\Software\WoW6432Mode\ImageWare Systems\EpiBuilder Right Click the same registry branch from step c and select Delete Reboot the PC Reinstall EpiBuilder by going to My Computer or Windows explorer, double click on C:\Program Files\Continuum\EpiBuilder\SDK\InstallEpiBuilder.bat Note: This runs very quickly Start Cyber and open a badge in Personnel Manager If using a VBScript File to redirect communication between principal DB server to mirror DB server, coding may need to be updated. Example: x32 vs x64 bit coding differences For x32: strRegName = "HKLM\Software\Andover Controls\Continuum\Primary Database\Server" strRegData = WshShell.RegRead(strRegName) For x64: strRegName = "HKLM\Software\Wow6432Node\Andover Controls\Continuum\Primary Database\Server" strRegData = WshShell.RegRead(strRegName)
View full article
Picard Product_Support
‎2018-09-06 01:55 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-30 08:42 AM

Labels:
  • Andover Continuum
1723 Views

Continuum's "Helix YUV Codecs (remove only)"

Issue "Helix YUV Codecs (remove only)" shows up under Windows "add/remove programs" after Continuum is installed. What is this and is it part of Continuum? Product Line Andover Continuum Environment Continuum Cyberstation 2.02 and earlier Windows Cause A Continuum Cyberstation installation brings with it several additional programs in order to run properly. These can be seen in the "Add/Remove Programs" interface. These programs may remain installed even after an uninstall/upgrade of Continuum. Resolution Helix YUV Codecs is part of the Continuum installation. The installation file is "yuvcodecs-1.2.exe" located on the CD in "..\Continuum\ISSetupPrerequisites\{1D2652A6-D9B2-43ED-8009-987E762962A2}". The Codecs install is part of the SVG viewer program for WebClient graphics in Continuum 2.02 and earlier.  This was removed from the Continuum 2.03 installation. If desired, this program can be removed if it is no longer in use.
View full article
Picard Product_Support
‎2018-09-06 09:16 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-30 06:41 AM

Labels:
  • Andover Continuum
1835 Views

Cyberstation cannot find new BACnet devices

Issue A BCX4040 is brought online on the Infinity side, but the device cannot be found when running Find New BACnet Devices. Product Line Andover Continuum Environment BACNET Cyberstation Find New Bacnet Devices Cause BACnet is disabled in the BACnet preferences. Resolution Under BACnet preferences, set item #1 - Enable BACnet to true.
View full article
Picard Product_Support
‎2018-09-06 10:52 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-29 12:21 PM

Labels:
  • Andover Continuum
2310 Views

No login screen displayed when accessing a I/A Series G3 station via web browser

Issue When accessing an I/A Series G3 station via a web browser over an Ethernet connection, no login screen is displayed. The default home graphics page is displayed instead. Product Line TAC IA Series Environment I/A Series G3 station with web access Cause The station guest account is designed to allow web access to the station without the requirement for the user to log into the station.  When accessing the server station graphics via the web browser on the computer hosting the server station, the user credentials prompt is always displayed. When accessing the server station graphics via web browser from a different computer than the one hosting the station, no user credentials prompt will be displayed and the user will be automatically logged in and will have all rights defined for the Guest user account. Resolution Disable the "Guest" user account to prevent automatic login to the station via a web browser.
View full article
Picard Product_Support
‎2018-09-06 09:03 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-29 06:34 AM

Labels:
  • TAC IA Series
1216 Views

Cannot logon to MPM using the Administrator password

Issue An application package (VAV reheat VA2) downloaded from the Can2Go site is restored to an MPM. It is then not possible to log on to the MPM using the default administrator password. Product Line EcoStruxure Building Expert Environment MPM Can2Go package Administrator user Cause The default administrator password in the Can2Go application database is not the same as the default SmartStruxure Lite password. Resolution Use the following default credentials for Can2Go applications: User Name: Admin Password: can2go
View full article
Picard Product_Support
‎2018-09-06 09:32 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-29 06:29 AM

Labels:
  • EcoStruxure Building Expert
2461 Views

Potentiometer input on a Xenta programmable device

Issue Setting up a potentiometer or resistance input on a Xenta Programmable controller. Product Line TAC Vista Environment TAC Menta Xenta 280,300 and 400 Cause No input option is available for a potentiometer or resistance in a Xenta device Resolution A curve module can be used to create your own input lookup table, as shown below. Attached file Pot_To_0_100_R01.zip provides an example of this 10K potentiometer sample
View full article
Picard Product_Support
‎2018-09-11 01:21 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2019-08-28 05:29 PM

Labels:
  • TAC Vista
1596 Views

All values are zeros or X in Vista IV

Issue All values in a Vista IV workstation are showing 0s (zeros) or "X"ed. Product Line TAC Vista Environment TAC Vista IV Workstation OGC Graphics Cause If the Workstation is in Engineering Mode, no live values will be retrieved. Resolution Make sure the Workstation is in Operating Mode rather than Engineering Mode to retrieve live values.
View full article
Picard Product_Support
‎2018-09-06 03:10 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-28 08:32 AM

Labels:
  • TAC Vista
1508 Views

JPEG image added to a TGML graphic displays in Workstation but not WebStation

Issue JPEG image added to a TGML graphic displays in Workstation but not WebStation Product Line EcoStruxure Building Operation Environment TGML SmartStruxure WebStation Cause It is possible there is something in the JPEG compression used for a specific image file that does not allow it to display in a web browser. The majority of JPEG images will work fine. Resolution In Windows Explorer, right-click on the image file and select Open With Open with any image editing program more advanced than MS paint, for example, Microsoft Office Picture Manager Select File > Export (in some programs this may be under the Edit Menu) Any Export will force the file to re-compress. It may also be advisable to lower the quality of the JPEG export in some manner to ensure fast load times on the web. Save the file Edit the Graphic in the TGML Editor, click on the Content Property of the Image object Click on the "..." icon Select the newly compressed image file and click open Save the TGML graphic and view in Workstation and Webstation.
View full article
Picard Product_Support
‎2018-09-06 10:22 AM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-28 08:29 AM

Labels:
  • EcoStruxure Building Operation
1624 Views

Out of memory errors on B3 controllers

Issue When trying to reload a B3867 controller or add log arrays to existing points, a memory error is encountered. Product Line Andover Continuum Environment Continuum 1.xxx B3867 Cause A memory allocation defect that was found in the -V versions of the controller was fixed in drop 51 of the -V firmware. The same issue was resolved in drop 64, but was not listed in the release notes. Resolution Update the B3867 version to the drop 64 rev.
View full article
Picard Product_Support
‎2018-09-06 01:55 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-28 06:26 AM

Labels:
  • Andover Continuum
2370 Views

XIF file generated in TAC Xbuilder can not be imported into LonMaker

Issue Can't import Xenta Server (5XX/7XX/9XX) XIF file into LonMaker. Get error message "The conversion of the file [path to file] into a XFB failed. Please verify that the file is a valid XIF. The utility XIF32BIN can be used to verify the contents of the file." when importing XIF file in LonMaker Product Line TAC Vista Environment TAC XBuilder LonMaker Xenta 511, 527, 701, 711, 721, 731, 913 Cause If the sum of the all the characters in the names of the node objects that you add are exactly 60, XBuilder generates a faulty XIF file which will not work in LonMaker. Example of faulty XIF file: File generated by TAC XBuilder version 5.1.5, XIF Version 4 Copyright (c) 2000 by TAC AB All Rights Reserved. Run on 0000-00-00 00:00 90:00:13:47:00:06:04:C3 2 15 1 8 1 5 2 0 0 2 6 11 13 13 11 3 0 16 0 0 1 11 8 11 5 9 13 28 0 0 15 5 3 113 0 1 7 1 0 4 4 4 15 200 0 78125 0 0 0 0 0 0 0 0 0 0 0 90 0 240 0 0 0 40 40 0 5 8 5 12 14 15 * "&3.2@0,5Node_Object 5708,5Node_Object 5703,5Node_Object 5704 " The second-to-the-last line above (after the ") has 60 characters which adds an extra " in the line below, thus making it unusable. Resolution Open the Xenta Server project in TAC Xbuilder In the Network pane, expand the "SNVTs" folder Under "LonMarkObjects", add or delete one character in one of the node object names Right-click on the Xenta Server in the network pane and choose "Generate XIF file" Import the new XIF file into LonMaker
View full article
Picard Product_Support
‎2018-09-06 02:09 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-28 06:24 AM

Labels:
  • TAC Vista
1925 Views
  • « Previous
    • 1
    • …
    • 249
    • 250
    • 251
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of