XIF file generated in TAC Xbuilder can not be imported into LonMaker

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • XIF file generated in TAC Xbuilder can not be imported into LonMaker
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Product_Support
    Product_Support
  • HenrikTarpgaard
    HenrikTarpgaard

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2271 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

XIF file generated in TAC Xbuilder can not be imported into LonMaker

Picard Product_Support
‎2018-09-06 02:09 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-28 06:24 AM

Issue

  • Can't import Xenta Server (5XX/7XX/9XX) XIF file into LonMaker.
  • Get error message "The conversion of the file [path to file] into a XFB failed. Please verify that the file is a valid XIF. The utility XIF32BIN can be used to verify the contents of the file." when importing XIF file in LonMaker

Product Line

TAC Vista

Environment

  • TAC XBuilder
  • LonMaker
  • Xenta 511, 527, 701, 711, 721, 731, 913

Cause

If the sum of the all the characters in the names of the node objects that you add are exactly 60, XBuilder generates a faulty XIF file which will not work in LonMaker.

Example of faulty XIF file:

File generated by TAC XBuilder version 5.1.5, XIF Version 4
Copyright (c) 2000 by TAC AB
All Rights Reserved. Run on 0000-00-00 00:00

90:00:13:47:00:06:04:C3
2 15 1 8 1 5 2 0 0 2 6 11 13 13 11 3 0 16 0 0 1 11 8
11 5 9 13 28 0 0 15 5 3 113 0
1 7 1 0 4 4 4 15 200 0
78125 0 0 0 0 0 0 0 0 0 0 0
90 0 240 0 0 0 40 40 0 5 8 5 12 14 15
*
"&3.2@0,5Node_Object 5708,5Node_Object 5703,5Node_Object 5704
"

The second-to-the-last line above (after the ") has 60 characters which adds an extra " in the line below, thus making it unusable.

Resolution

  1. Open the Xenta Server project in TAC Xbuilder
  2. In the Network pane, expand the "SNVTs" folder
  3. Under "LonMarkObjects", add or delete one character in one of the node object names
  4. Right-click on the Xenta Server in the network pane and choose "Generate XIF file"
  5. Import the new XIF file into LonMaker
Labels (1)
Labels:
  • TAC Vista
Tags (1)
  • Find more articles tagged with:
  • 4573
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore