"Error getting root folder name" when launching Personnel Manager

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • "Error getting root folder name" when launching Personnel Manager
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Alan_Wood
    Alan_Wood
  • AbeMeran
    AbeMeran
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1807 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

"Error getting root folder name" when launching Personnel Manager

Picard Product_Support
‎2018-09-06 01:55 PM

Last Updated: Administrator DavidFisher Administrator ‎2019-08-30 08:42 AM

Issue

Personnel Manager displays "Error getting root folder name" when launching.

Product Line

Andover Continuum

Environment

  • CyberStation
  • Personnel Manager (PIM)

Cause

At boot time, Personnel Manager queries the ContinuumDB to find the Root container by ID using the following SQL query:

SELECT uiname  FROM Dictionary WHERE objectidhi = 0 AND objectidlo = 536870913

 "Error getting root folder name" will be generated if PIM is unable to access the ContinuumDB or can not find the root object for any other reason.

Resolution

  1. The User account control slider on a Windows 7 PC will need to be moved all the way to the bottom.
  2. Check/resolve for database connectivity errors.
  3. Make sure Firewall settings are not preventing the PIM from getting to the SQL server.

    If the problem persists try the following:
     
  4. Check to see if Badgemanager.exe is starting. If not then a perform clean uninstall of EpiBuilder with the following steps:
    1. From Add/Remove programs (Programs and Features in Windows 7) Uninstall
    2. Run Regedit (Start > Run > regedit)
    3. Get a registry back by Right clicking on HKey_Local_Machine\Software\ImageWare Systems\EpiBuilder  and select Export and save the selected branch to a file location. This can be used to restore the registry key if necessary.
      Windows 7: HKey_Local_Machine\Software\WoW6432Mode\ImageWare Systems\EpiBuilder
    4. Right Click the same registry branch from step c and select Delete
    5. Reboot the PC
    6. Reinstall EpiBuilder by going to My Computer or Windows explorer, double click on C:\Program Files\Continuum\EpiBuilder\SDK\InstallEpiBuilder.bat
      Note: This runs very quickly
    7. Start Cyber and open a badge in Personnel Manager

If using a VBScript File to redirect communication between principal DB server to mirror DB server, coding may need to be updated.

Example:

x32 vs x64 bit coding differences

  • For x32:
    • strRegName = "HKLM\Software\Andover Controls\Continuum\Primary Database\Server"
    • strRegData = WshShell.RegRead(strRegName)
  • For x64:
    • strRegName = "HKLM\Software\Wow6432Node\Andover Controls\Continuum\Primary Database\Server"
    • strRegData = WshShell.RegRead(strRegName)
Labels (1)
Labels:
  • Andover Continuum
Tags (1)
  • Find more articles tagged with:
  • 4977
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore