Issue
An application package (VAV reheat VA2) downloaded from the Can2Go site is restored to an MPM. It is then not possible to log on to the MPM using the default administrator password.
Product Line
EcoStruxure Building Expert
Environment
- MPM
- Can2Go package
- Administrator user
Cause
The default administrator password in the Can2Go application database is not the same as the default SmartStruxure Lite password.
Resolution
Use the following default credentials for Can2Go applications:
- User Name: Admin