Out of memory errors on B3 controllers
  • Out of memory errors on B3 controllers
  • sesa116379_brid
    sesa116379_brid
‎2018-09-06 01:55 PM
Last Updated: Administrator DavidFisher Administrator ‎2019-08-28 06:26 AM
When trying to reload a B3867 controller or add log arrays to existing points, a memory error is encountered.
Andover Continuum
  • Continuum 1.xxx
  • B3867
A memory allocation defect that was found in the -V versions of the controller was fixed in drop 51 of the -V firmware. The same issue was resolved in drop 64, but was not listed in the release notes.
Update the B3867 version to the drop 64 rev.
Tags (4)
  • 4985
  • b3867
  • continuum
  • ebo
100% helpful (1/1)