Issue
When trying to reload a B3867 controller or add log arrays to existing points, a memory error is encountered.
Product Line
Andover Continuum
Environment
- Continuum 1.xxx
- B3867
Cause
A memory allocation defect that was found in the -V versions of the controller was fixed in drop 51 of the -V firmware. The same issue was resolved in drop 64, but was not listed in the release notes.
Resolution
Update the B3867 version to the drop 64 rev.