Migrating Users from SP-C-WEB to Security Expert

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Migrating Users from SP-C-WEB to Security Expert
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2761 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Migrating Users from SP-C-WEB to Security Expert

Guinan AdamSteele Guinan
‎2019-02-24 09:57 PM

Last Updated: Crewman ContentModerator ‎2025-09-01 03:35 AM

Issue

Require details on how to migrate Users from an SP-C-WEB to Security Expert.

Product Line

Security Expert

Environment

  • SP-C-WEB
  • Security Expert

Warning

Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance.

Cause

Have a site that has outgrown it's SP-C-WEB installation and is upgrading to Security Expert to expand.

Resolution

Door configuration and programming cannot be migrated from an SP-C-WEB installation to Security Expert, but the User database can be exported to a CSV file and then imported into Security Expert to help with the migration.

Exporting User database from SP-C-WEB to CSV file

  1. From the SP-C-WEB user interface navigate to Users | User Search.
  2. In the User Search page on the top right (under date) is the Export button. Clicking the Export button will generate a .csv file of all User details. (See attached example Exported Users.zip)

Editing User CSV file for importing into Security Expert

  1. The Security Expert User import requires the CSV file to be in a specific format:
    • FirstName,LastName,FullName,Facility,Card,PIN,AccessLevel
  2. The rules for this format are that:
    • Each field must have a value however the firstname/lastname can be omitted if the fullname is used and vice versa.
    • The facility can be omitted if it is prepended to the card number and separated with a colon (eg 123:4567).
    • If a matching Access Level is not found, a new access level is created.
    • The PIN and Card must be unique for each user.
    • The file cannot contain a header row.
  3. Some examples of correctly formatted data are:
    • Joe, Stanley,Joe Stanley,123,4587,1418,Warehouse Staff
    • Georgia, Smith,,123,4654,6884,Warehouse Staff
    • ,,Billy Randall,123,4727,3492,Warehouse Staff
    • Frank,Powell,,,123:4639,3160,Warehouse Staff

Importing Users from a CSV File into Security Expert

  1. In the Security Expert Client navigate to Sites | Import Users to launch the Import Users Wizard.
  2. Browse to and select the CSV File you wish to import the users from, then click OK.Figure 1 - User Import DialogFigure 1 - User Import DialogFigure 1 - User Import Dialog
  3. The Users records are created and a message is displayed to indicate the action was successful.
Labels (1)
Labels:
  • EcoStruxure Security Expert
Attachments
Exported Users.zip
Tags (3)
  • Find more articles tagged with:
  • AdamSteele19
  • HernanUruena23
  • HernanUruena24
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore