Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,854
  • TAC IA Series 1,826
  • TAC INET 1,459
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 334
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 150
  • CCTV 53
  • Project Configuration Tool 47
  • EcoStruxure Building Activate 17
  • EcoStruxure Building Advisor 12
  • ESMI Fire Detection 12
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Building Automation Knowledge Base

Sort by:
Helpfulness
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 492
    • 493
    • 494
    • …
    • 509
  • Next »

Sequence zero does not run when power is restored to a Micro Regulator (MR)

Issue Sequence zero does not run when power is restored to the Micro Regulators (MR). The MRI is on a UPS in another part of the building and never loses power. Product Line TAC INET Environment MicroRegulator (MR) SubLAN devices MicroRegulator Interface (MRI) Controller LAN Interface Cause By design, sequences are stored in the MRI. Sub-LAN controllers do not store sequences. Resolution Sequence zero is designed to trigger the power restore event (Sequence 0) in the event of the Interface (MRI) power failure being restored, hence the MR will not trigger this sequence 0 in the MRI.  The action is correct.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Last Updated: Guinan RobertAndriolo Guinan ‎2023-12-21 10:10 PM

Labels:
  • TAC INET
1138 Views

Sync LED on FOI still on after correcting the line fault on the output of the CRR.

Issue I never reset the "Sync" LED on the FOI after I corrected the line fault on the output of the CRR. Will this cause any communication problems? Environment I/NET CRR Cause Line Fault Resolution Reset the sync LED If you can NOT extinguish the Sync LED you should find the fault. Leaving this light “on” does not cause communication problems.
View full article
Picard Product_Support
‎2018-09-06 03:26 PM

Labels:
  • TAC INET
1007 Views

ADAA problems: can not dial in or out of the site

Issue ADAA problems: can not dial in or out of the site A PCU is set up as a 06 TAP. The RX and TX LEDs are flashing on the RS-232 card. A CBL048 cable is connected from the RS-232 card to the modem. The RD and SD lights are flashing. Environment ADAA Cause The wrong BIN file is in the PCU. Resolution You have the wrong BIN file in the PCU. If the PCU is at the “Boot State”, you may have the wrong EPROM too. Install the correct BIN file; and it is strongly recommend to put in a compatible Asynchronous EPROM.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
944 Views

Controlling AC relays from analog outputs on the motherboard or expansion board of the 7718 PCU

Issue Controlling AC relays from analog outputs on the motherboard or expansion board of the 7718 PCU Environment I/NET Site Cause Controlling AC relays from analog outputs on the motherboard or expansion board of the 7718 PCU Resolution The outputs from these locations are DC. This may cause the AC relays to “chatter” or not work at all. It is recommended to use a P8UI8DO at the expansion board or place DC powered, form “C” contacts, pilot relays on the outputs of the PCU. Refer to TCON106 for more details.
View full article
Picard Product_Support
‎2018-09-06 11:12 PM

Labels:
  • TAC INET
1280 Views

Door show Deny Entry Schedule after deleting a special day schedule on the special day

Issue Door show Deny Entry Schedule after deleting a special day schedule on the special day Environment I/NET Access Control Cause The process to execute the Special Day begins at midnight on the first day of the duration, and ends at the end of the last day of duration. If you delete the Special day while it is running you will get denied entry. Resolution Do not Delete special Day schedules on special days Modify the special day schedule to match the desired access control results. On the next non-special day, Delete the schedule If you have already deleted the special Day or special Schedule Option A - Delete the special day from the Host and the Controller     Perform a station restore to force the controller to use the current programming Option B - Determine which special day schedule type the controller is operating on Modify or create a schedule for that special day with the desired access privileges On the next non-special business day, enter the desired programming for special days.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1096 Views

Docutrend data import fails while connected to a physical 78010 tap.

Issue Docutrend data import fails while connected to a physical 78010 tap. Environment I/NET site Cause Docutrend data import fails while connected to physical 78010 tap. Resolution The system or hardware number in your active profile is different compared to the 78010 tap. Change the profile to match the site 78010 tap.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1109 Views

DPU required signal to add fingerprint verification to a card read before access is granted

Issue In addition to a card read, add fingerprint verification before access is given. What kind signal is required from this third party device to the DPU? Environment I/NET Access Control Site Cause In addition to a card read, add fingerprint verification before access is given. What kind signal is required from this third party device to the DPU? Resolution DPUs require a 26-bit Wiegand format.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1139 Views

Does Configuration Server for an i.Lon 1000 have to be running all of the time?

Issue Does Configuration Server for an i.Lon 1000 have to be running all of the time? Environment i.LON 1000 Cause The Config Server provides the path for communication to the iLon when used as an RNI. Resolution If using the i.Lon 1000 as an RNI to communicate with the LonWorks network, then the Config Server must be open.   If the i.Lon 1000 is being used as a router (not RNI), it is not necessary to have Config Server running unless you are in the configuration process for the router.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
1173 Views

Dial Network and LNS Network in the same Vista Network

Issue Is it possible to have a Dial Network and LNS Network in the same Vista Network? Environment Vista Network Dial Network LNS Network Cause  A dial up network communicates via the PC comport directly (no LTA driver), therefore there is no conflict with LTA card drivers (like the conflict that occurs between Classic and LNS networks). Resolution There is no problem having both types of communication in a single Vista network.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
1307 Views

How to connect the RoamIO service tool directly to a standalone BACnet b3 controller.

Issue When connecting the RoamIO-2 service tool directly to a standalone BACnet b3 controller which is not connected to the MSTP network yet, the RoamIO-2 does not show the b3 controller on the screen. Environment RoamIO-2 Continuum SmartStruxure BACnet b3 controller Cause By default, the View option of the ROAMIO2 Bacnet Service Tool is set to view "By Network".  Resolution Connect the RoamIO2 service tool directly to the b3's service port. Launch the BACnet Service Tool and in the 'View' menu de-select 'By Networks' and 'BACnet Only' menu entries. Click the green icon to connect. Now, it will show the b3 controller in the service tool.
View full article
Picard Product_Support
‎2018-09-10 02:20 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
2028 Views

When will the connection in a Dial network disconnect?

Issue When will the connection in a Dial network disconnect? Environment Xenta 901 Cause The 901 connection will continue as long as live values are being viewed. Resolution If the Status window is open (for example), the connection will continue until that window (and any other window viewing live data) is closed.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
866 Views

Using the Xenta 511, will value pages only show temperatures in Celsius? How do you get them to display in Fahrenheit?

Issue Using the Xenta 511, will value pages only show temperatures in Celsius? How do you get them to display in Fahrenheit? Environment XBuilder Cause Regional settings can be project wide or per point. Resolution When creating a new TAC Xenta 511 project, select to use US values. You can also select conversions to occur per object.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
925 Views

Is it not possible to have multiple Xenta 901s from multiple sites in a single LNS network

Issue Is it possible to have multiple Xenta 901 controllers from multiple sites in a single LNS network and access the remote sites as needed? This would leave any controllers not connected offline. Environment TAC Xenta 901 LNS Network Cause TAC Xenta 901 is an "LTA" and in TAC Vista there can only be one per LonWorks network. Resolution Create one LNS database per TAC Xenta 901. You can have up to 240 TAC Xenta 901 networks per TAC Vista Server (all can dial up the same TAC Vista Modem(s)). Add another TAC Vista Server if you need more dial up connections.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC Vista
972 Views

Wiring diagram of the breakout box connections between the Reader and the 7910 or 7920 DPU

Issue Need a wiring diagram of the breakout box connections between the Reader and the 7910 or 7920 DPU. Product Line TAC INET Environment I/NET site Cause Need a wiring diagram of the breakout box connections between the Reader and the 7910 or 7920 DPU. Resolution Recommend you look in TCON 112 (Readers) for illustrations the match your requirements. Check for TCON Number and Title Cross Reference (with links).
View full article
Picard Product_Support
‎2018-09-06 11:15 PM

Last Updated: Admiral David_Kendrick Admiral ‎2022-08-09 08:11 AM

Labels:
  • TAC INET
1374 Views

How to adjust the illumination level on the 7798 (B)

Issue How to adjust the illumination level on the 7798 (B) Environment I/NET site Cause How do you adjust the illumination level on the 7798 (B) Resolution Function Keys F7 increases the level; F8 lowers the level. Older 7798s do not have this feature.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1123 Views

Conversion coefficients values for the Setpoint Adjustment Dial on a 7200 UC

Issue Conversion coefficients values for the Setpoint Adjustment Dial on a 7200 UC Environment I/NET site Cause Need for conversion coefficients values for the Setpoint Adjustment Dial on a 7200 UC Resolution M = 0.01666; B = -2.1333. The resolution counts range is 68 to 188.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
1047 Views

How to remove the "Y" selected in the Alarm Inhibit Editor

Issue How to remove the "Y" selected in the Alarm Inhibit Editor Environment I/NET site Cause How to remove the "Y" selected in the Alarm Inhibit Editor Resolution This node may not be saved in the workstation’s Network Configuration Editor. First save this device in network configuration, then attempt to modify the settings in the Alarm Inhibit Editor. Refer to TCON 237 Alarm Inhibit (AI)
View full article
Picard Product_Support
‎2018-09-06 11:17 PM

Labels:
  • TAC INET
1196 Views

PCU Analog Outputs to transducers do not have consistent performance

Issue PCU Analog Outputs to transducers do not have consistent performance. The first voltage-to-pneumatic transducers installed worked fine. Additional transducers have been added; and now, none of the transducers operate properly. Environment PCU Voltage-to-Pneumatic transducers Cause The amperage or power draw limitations of the PCU have most likely been exceeded. Resolution Sum up the total current and / or power draw of all the transducers and compare this to the maximum current or power output of the PCU. Reduce the number of transducers to stay within the limitations.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
946 Views

MR 160 resets every minute

Issue MR 160 resets every minute. It is the only sub-LAN controller resetting. Replacing the hardware has no effect on the resetting issue. Environment MR160 Cause Station conflicts can cause this behavior. The MR 160 is unique in that it uses two consecutive addresses on the subLAN and is designed for inputs only. The MR 160 provides no output points or MR-resident DDC modules. Resolution Make sure there are no station address conflicts. Make sure the database has not violated the specifications for inputs only. Refer to TCON 126 for more information.
View full article
Picard Product_Support
‎2018-09-06 11:19 PM

Labels:
  • TAC INET
909 Views

Share the value of a DM point with several controllers using indirect points

Issue Share the value of a DM point with several controllers using indirect points Environment I/NET Resident I/O Cause Sharing global points designated as DMs. Resolution Use an internal DI point with a "P0" calculation tied to the DM point. Set this DI as Global. The indirect points (which exist in the other controllers) should be built as DIs with the same Station Parameters used for the DM point.
View full article
Picard Product_Support
‎2018-09-06 03:25 PM

Labels:
  • TAC INET
932 Views
  • « Previous
    • 1
    • …
    • 492
    • 493
    • 494
    • …
    • 509
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of