Issue
Sequence zero does not run when power is restored to the Micro Regulators (MR).
The MRI is on a UPS in another part of the building and never loses power.
Product Line
TAC INET
Environment
- MicroRegulator (MR) SubLAN devices
- MicroRegulator Interface (MRI) Controller LAN Interface
Cause
By design, sequences are stored in the MRI. Sub-LAN controllers do not store sequences.
Resolution
Sequence zero is designed to trigger the power restore event (Sequence 0) in the event of the Interface (MRI) power failure being restored, hence the MR will not trigger this sequence 0 in the MRI. The action is correct.