Issue
Conversion coefficients values for the Setpoint Adjustment Dial on a 7200 UC
Environment
I/NET site
Cause
Need for conversion coefficients values for the Setpoint Adjustment Dial on a 7200 UC
Resolution
M = 0.01666; B = -2.1333. The resolution counts range is 68 to 188.