Door show Deny Entry Schedule after deleting a special day schedule on the special day
  • Door show Deny Entry Schedule after deleting a special day schedule on the special day
‎2018-09-06 03:25 PM
I/NET Access Control
The process to execute the Special Day begins at midnight on the first day of the duration, and ends at the end of the last day of duration. If you delete the Special day while it is running you will get denied entry.
  1. Do not Delete special Day schedules on special days
  2. Modify the special day schedule to match the desired access control results.
  3. On the next non-special day, Delete the schedule
If you have already deleted the special Day or special Schedule
Option A -
  1. Delete the special day from the Host and the Controller
  2. Perform a station restore to force the controller to use the current programming
Option B -
  1. Determine which special day schedule type the controller is operating on
  2. Modify or create a schedule for that special day with the desired access privileges
  3. On the next non-special business day, enter the desired programming for special days.
  • TAC INET
  • 1120