Share the value of a DM point with several controllers using indirect points
  • Share the value of a DM point with several controllers using indirect points
‎2018-09-06 03:25 PM
I/NET Resident I/O
Sharing global points designated as DMs.
  1. Use an internal DI point with a "P0" calculation tied to the DM point.
  2. Set this DI as Global.
  3. The indirect points (which exist in the other controllers) should be built as DIs with the same Station Parameters used for the DM point.
  • TAC INET