Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,208
  • TAC Vista 2,045
  • EcoStruxure Building Operation 1,838
  • TAC IA Series 1,821
  • TAC INET 1,458
  • Field Devices 721
  • Satchwell BAS & Sigma 474
  • EcoStruxure Security Expert 325
  • Satchwell MicroNet 252
  • EcoStruxure Building Expert 228
  • EcoStruxure Access Expert 147
  • CCTV 53
  • Project Configuration Tool 46
  • EcoStruxure Building Advisor 12
  • EcoStruxure Building Activate 11
  • ESMI Fire Detection 6
  • Automated Engineering Tool 4
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
  • Previous
  • 1 of 2
  • Next
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • Cody_Failinger
    Cody_Failinger
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1821 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 29
    • 30
    • 31
    • …
    • 92
  • Next »
Label: "TAC IA Series" Show all articles

How to connect 2-10 Vdc position output signal of an actuator to an analog input of LON or BACnet controllers.

Issue How to connect 2-10 Vdc position output signal of an actuator to an analog input of LON or BACnet controllers. Controller’s Analog Inputs are limited to 0-5 Vdc input. Environment WorkPlace Tech I/A Series Lon (MNL) controllers I/A Series BACnet (MNB) controllers Cause Controller’s Analog Inputs are limited to 0-5 Vdc input. Resolution See the WorkPlace Tech Tool Engineering Guide (F-27254-3) Analog Input object discussion (page 129) for reference. Setting up a 2 to 10 VDC feedback voltage divider, use a 120 K (120,000) Ohm in series with a 100 K (100,000) Ohm resistor; connect the UI across the 100K Ohm resistor. As long as the signal never exceed 10 VDC, the voltage across the 100 K Ohm will never exceed 5.0 VDC. Based on the above test results, 10Vdc [actuator output] = 4.545 Vdc [after voltage divider] 2 Vdc [actuator output] = .909 Vdc [after voltage divider] Set-up the Analog Input Object Linput= 0.909 Vdc LScale= 0 Hinput= 4.545 Vdc HScale= 100 Your values maybe different based on the resistor accuracy.
View full article
Picard Product_Support
‎2018-09-06 01:59 PM

Labels:
  • TAC IA Series
2405 Views

How to use the Send Group object in a G3 (Niagara) station containing the ASD driver.

Issue The TAC I/A Series G3 ASD Driver Installation and Configuration Guide, F-27522, does not describe the Send Group object. Environment I/A Series G3 (Niagara) station containing the ASD driver I/A Series Network 8000 ASD controllers ; MicroZone II, MicroFlo II, LIM, or PEM1 PSI / XPSI to edit database in the ASD controller. Cause Setup not documented. Resolution Basic setup procedure: Verify the configuration of the ASD controller, using PSI: ASD device, Edit, device, Setup, Group # RGRP:n block, where n matches the Group Number in step 1 Edit the G3 station using the Workbench, as follows: In the ENC station, AsdNetwork, Groups (AsdGroup Device); verify Enabled = True verify status = OK  SendGroup object under the Groups. Verify Device Type matches the controller type ( Mz2, Mf2, Lim, or Pem) Verify Group Number is the same as in Steps #1 & #2 above. Set Mbx Input = true;  by either setting Mbx Input Default = true, or by connecting a Boolean Writeable to the Mbx Input
View full article
Picard Product_Support
‎2018-09-07 02:29 PM

Labels:
  • TAC IA Series
1124 Views

Pinout configuration for a RJ-45 to DB-9 Null Modem Adapter (part number UNCC-405)

Issue Pinout configuration for a RJ-45 to DB-9 Null Modem Adapter (part number UNCC-405) used for serial integrations to a Niagara R2 UNC or Niagara G3 ENC. Product Line TAC IA Series Environment Niagara R2 UNC-520 Niagara G3 ENC-520 Cause Pinout diagram for wiring Resolution This image details two pinout configurations:  Null Modem and Straight-through.  The Null Modem version is available for purchase using part number UNCC-405.  The Straight-through version is not available for purchase. This image is also part of the UNC-520 Installation Instructions (F-27391)
View full article
Picard Product_Support
‎2018-09-07 02:03 PM

Labels:
  • TAC IA Series
1872 Views

New installation of the I/A Series (Niagara) R2 WorkPlace Pro software cannot connect to existing UNC

Issue Installed the I/A Series(Niagara) R2 software on a new Windows computer but cannot get it to connect to an existing UNC that has the same release of the I/A Series R2 software.  One possible error, "Java.io.EOF Exception", that might be displayed is shown below: Another possible error message is an HTTP 401 error. This issue may also prevent the I/A Series R2 tunnel client from connecting to UNC. Environment Computer with any supported version of Windows software including the usual assortment of utility and security / anti-virus software. I/A Series (Niagara) R2 software (any version) installed on the computer. Cause The Windows Firewall and/or Anti-Virus/Internet Security software has been installed and configured such that it is blocking Ethernet communications into or out of the computer on certain Ethernet ports. According to the I/A Series Networking & Connectivity Guide, provided with the I/A Series (Niagara) R2 software, specific user definable Ethernet ports, must be open for two-way communications between the WorkPlace Pro software and a UNC.  If communications is blocked on these ports, the WorkPlace Pro software will not be able to communicate across the Ethernet network. Similar issues are caused by the firewall built into many of the Internet Security software packages.  The following programs have been known to cause port blocking issues: Trend Micro Internet Security - Workstation Edition Trend Micro Office Scan - Workstation Edition Symantec Internet Security Suite version 9 Avast 7 (Free) Antivirus with 30 day demo of Avast Internet Security Bitdefender Antivirus Software Kaspersky PURE 3.0Total Security Kaspersky Endpoint for Business Resolution Verify that the Windows Firewall has been configured to pass bidirectional Ethernet communications over the two required Ethernet ports (default ports are 80 and 3011 - for both the TCP and UDP protocols).  Refer to the online Windows Help for configuration information.  Note that  computers that are members of a Windows Domain may have firewall configuration restrictions enforced by domain policies.  In these situations, it will be necessary to contact the Domain Administrator or facility PC-Help Desk for assistance. Verify that any installed Internet Security software does not block the required Ethernet communications ports.  Some specific Internet Security software packages are known to permanently block the use of some Ethernet ports, for specific uses.  Any Internet Security software of this type must be totally removed from the computer before the required communications can be established.  Three known software packages of this type are the "Symantec Internet Security Suite, version 9", "Bitdefender Antivirus Software" and "Trend Micro Internet Security software".
View full article
Picard Product_Support
‎2018-09-07 06:46 AM

Labels:
  • TAC IA Series
2013 Views

In I/A Series G3, history extensions cannot be enabled to begin collection.

Issue History Extensions in History Service show a “Fault” Status.  The Fault cause displays: "Duplicate history id:" followed by the name of the object. Environment I/A Series G3, version 3.3.22 and later Cause  By default, history extensions inherit the name of the objects they’re attached to (e.g. CFM).  If CFM is to be trended on multiple VAV units (VAV1, VAV2, etc.), this can cause issues when enabling history collection in the History Service; one or more histories will be in a “Fault” state, with the error message: “Duplicate history id:” for the Fault Cause. Resolution To resolve the issue, the history names can be configured to include the parent folder names:     1.  Open the Program Service in the station’s Services container, and click on the “Find Objects” button at the bottom of the Batch Editor view 2.  In the Bql Query Builder window, select (Custom Type) in the “Of type:” drop-down menu.  Two more drop-down menus will appear.  In the middle drop-down, select “history”.  In the last drop-down, select the appropriate history extension (e.g. NumericIntervalHistoryExt).  Then, click OK.  The Batch Editor view will populate with all of the history extensions in the station for the extension type selected     3.  In the Batch Editor view, highlight all of the history objects, then click the “Edit Slot” button at the bottom of the view 4.  In the Edit Slot window, select “historyName” in the Property drop-down menu.  In the New Value field, type the following:      %parent.parent.name%_%parent.name%     NOTE:  Depending on the tree structure, the filter may need to be modified in order to create a unique history name.  For example, if the network is structured in the following format:   In this example, the object nviSatSwitch1_value is a child of the Points container, which is a child of the device MnlRs3_10. In order to create a unique name for the history extension, the correct filter would need to be:         %parent.parent.parent.name%_%parent.name%.   5.  Click OK.  After a few seconds, the BatchEditor Results window will appear, displaying the objects that were changed.  The history extensions now have unique names, and can be enabled in the History Service
View full article
Picard Product_Support
‎2018-09-07 05:24 AM

Labels:
  • TAC IA Series
1288 Views

Register for The Exchange

Issue The Exchange Download Center contains all of the assets you once accessed through the Buildings Extranet are now available on a brand new platform. It's easy to search and fast to download. Stay tuned for more great features as we roll this into the all-new extranet solution for Buildings. We ask that you register for a new account on The Exchange.   Product Line Andover Continuum, EcoStruxure Building Expert, EcoStruxure Building Operation, Field Devices, Other, Pelco, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Exchange Download Center Cause You can utilize the new Buildings web experience from The Exchange. Resolution Navigate to https://ecoxpert.se.com/ * Use a modern browser for the best experience: Google Chrome, Mozilla Firefox, Microsoft Edge, and Microsoft Internet Explorer version 8 or later. If you receive the following error in Internet Explorer despite using version 8 or later, the browser displays the page in Compatibility View. Click here for more information on Compatibility View and how to disable it. The Download Center will not function properly in Compatibility View.   On the header bar, you will see the option in the top right corner for “Login / Register.” Click it.   If you are already registered, enter your email address and password. If this is your first time registering, click the link for “New to the Download Center? Register here!”   Answer whether or not you are a Schneider Electric employee using the radio buttons. If you are a Schneider Electric employee, enter your SESA ID and your desired password for The Exchange. Click to accept Schneider Electric’s Terms and Conditions and hit “Create Account.” * The first time you register, you must be connected to the Schneider Electric network or connected via VPN. This is only required at registration. All future logins can be done externally. If you are not a Schneider Electric employee, enter your first name, last name, company name, location, business email address, and desired password for The Exchange. * It is important to use your business email address if you are a licensed partner. Your email address is used to automatically validate your Partner status and assign the correct permissions to your user profile.   An email is sent to your designated inbox with a link to click through and validate your email address. Once this is done, your login is created, and you are ready to start using the Download Center. * If an error is displayed when trying to validate your authentication code, please try to log in. This happens when an email address has already been verified and oftentimes does not indicate an error with the registration.   Once logged in, you can search and download assets available to your user profile. If you attempt to download a file that you do not have access to, you will be given a chance to report if this is in error. Your username, email, and the asset you are trying to access are recorded. Please enter a message if any further description is required and hit “Submit.” A member of our team will get back to you promptly with a resolution. Web Site Support For any issue regarding The Exchange Download Center, please contact us at exchangesupport@schneider-electric.com.
View full article
Picard Product_Support
‎2018-09-11 07:28 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2021-06-17 03:35 PM

Labels:
  • Andover Continuum
  • CCTV
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
6702 Views

Niagara 4.9+ and IT Network Scanners

Issue Network scanning software causes a loss of Jace network communication. Product Line TAC IA Series Environment I/A Series Jace 8000 N4.9 and later Cause As network security awareness continues to expand, software-based scanners, such as industry-standard Qualys and Nessus, intended to detect and report on vulnerabilities within internal networks will likely continue to gain popularity.  Today, Tridium is seeing these scanners being deployed and run against Niagara-based platforms like the JACE-8000 and Edge 10.  In some cases, these scans are causing Niagara platforms to become unresponsive or reboot via an Engine Watchdog Timeout, all of which are not acceptable for the critical applications that Niagara facilitates. Resolution While Tridium has no control over how these scanners behave, or how and when they are executed within an organization, Niagara 4.9 introduces a number of changes intended to allow a Niagara-based hardware platform to appropriately respond to the scanning utilities, and also maintain operation.  Below is a brief explanation of how Niagara will function under the different known circumstances currently employed by these scanners, and how to interpret the results.   Recognition of non-Niagara Traffic on the platform In the event a scanner is interrogating a Niagara 4.9+ platform connection, the Niagara Daemon has been modified to recognize non-Niagara traffic over a period of time, shut down the connection if necessary, and wait for a pre-determined amount of time before re-enabling connectivity.  Under these conditions, a scanning utility may report that the Niagara instance has encountered denial of service, when in fact, Niagara has simply disabled the communication mechanism by which the scanner was attempting its interrogation. During this time, normal platform communication will also be affected; however, the Niagara platform and station will continue to run.   Prioritization of Internal vs. External Communication on the Niagara station In the event, a scanner is interrogating a Niagara 4.9+ station (external communication) and Niagara detects that this interrogation may cause an Engine Watchdog Timeout, the station’s web server will be stopped and restarted. Under these conditions, a scanning utility may report that the Niagara instance abruptly stopped communicating, and may have encountered denial of service.  During this time period, normal/expected client web connections to the station will also be affected; however, the Niagara platform and station will continue to run. As mentioned, these scanners are outside the control of Tridium, and likely always evolving to meet the needs of the various threats they are intended to protect against. As a best practice, Tridium recommends not scanning in production if possible, as any findings would be just as legitimate during scheduled downtime. Additionally, it may be prudent to work with the scanning tools to configure the appropriate priority of a scan, as the intensity of which you scan a production multicore, failover redundant web server host, is likely not the best choice for scanning a single-core JACE. Should you encounter an issue with a network scanning utility and Niagara 4.9 and above, please contact your support organization.
View full article
Guinan RandyDavis Guinan
‎2021-04-30 10:45 AM

Last Updated: Guinan RobertAndriolo Guinan ‎2021-05-02 05:38 PM

Labels:
  • TAC IA Series
1386 Views

System DB Must Be Re-indexed for Upgrades to Niagara 4.10+ from Earlier Niagara

Issue There is a problem after upgrading the SystemDB to N4.10. Product Line TAC IA Series Environment I/A Jace 8000 N4.10 I/A Enterprise Server N4.10 Cause In Niagara 4.10, we upgraded SystemDB from Orient v2 to v3, and as a result of that change, any customers that are utilizing SystemDB on their Supervisor stations will need to re-index accordingly upon upgrading to 4.10. Resolution In Niagara 4.10, the SystemDB has been upgraded from Orient v2 to v3.  Because of this change, customers that are utilizing SystemDB on their Supervisor stations will need to re-index upon upgrade to 4.10.  Please note, re-indexing can take a considerable time upon upgrade, and the DB will not have accurate information when queried until the index upgrade is complete. After upgrading to 4.10, invoke the actions that force system indexing.  Be aware that re-indexing can take some time, and that the DB won’t have accurate information when queried until the index is complete. The following image shows how to invoke execute on the Local System Indexer: If the Station has a DB configured to contain information about points on other stations, the Niagara Network System Indexer should be used, rather than the Local System Indexer.  Additional details regarding indexer actions can be found in the Niagara System Database and System Indexing Guide.
View full article
Guinan RandyDavis Guinan
‎2021-04-20 10:21 AM

Labels:
  • TAC IA Series
950 Views

Workplace Tech 5.10.1 Rtmonitor.exe Error

Issue When attempting a device browse in Workplace Tech 5.10.1, an error pop up, "CoCreateInstance(CLISD_RTApplication) failed" is invoked A critical error with Rtmonitor.exe when running Workplace Commissioning Tool Product Line TAC IA Series Environment Workplace Tech => 5.10.1  Workplace Commissioning Tool => 5.10.1 Windows OS 32 bit Cause Environment Variables /variable/path includes the incorrect path to the LonWorks\bin.  This doesn't allow the rtmonitor.exe to be executed. Resolution When the Workplace Tech 5.10.1 bundle of applications are installed, the Environment Variables is modified to include,  %ProgramFiles(x86)%\LonWorks\bin In a 32 bit OS, this ProgramFiles(x86) folder does not exist.  This path has to be modified so the assets can be found. Remove the "(x86)" so the path appears as below. Note: This is only applicable for 32 bit operating systems.
View full article
Guinan RandyDavis Guinan
‎2021-04-21 12:32 PM

Labels:
  • TAC IA Series
2570 Views

Tridium N4.10 Upgrade Considerations

Issue What should be considered when prepairing for upgrading to Niagara 4.10? What known issues should I be aware of when upgrading to Niagara 4.10 and how can I prepair for them? Product Line TAC IA Series Environment I/A Series N4 Enterprise Server I/A Series N4 Jace 8000 Cause Define potential issues with an N4.10 upgrade Resolution The following details a set of upgrade considerations and known issues and their workarounds regarding Niagara 4.10. Please review prior to upgrading to Niagara 4.10. Niagara 4.10 and Default NRE Memory Changes: The increased size of some core libraries in Niagara 4.10 required changes to the default NRE Memory Pool settings for use on a JACE-8000. MetaSpace memory needed to be increased to allow applications to run without issue.   Note: any previous custom memory configuration applied to the JACE-8000 will be reset upon upgrade to 4.10. Prior to upgrading your JACE-8000, please review Default NRE Memory Pool Configuration Changes In 4.10.     Niagara 4.10 System DB Upgrade: In Niagara 4.10, we upgraded SystemDB from Orient v2 to v3, and as a result of that change, any customers that are utilizing SystemDB on their Supervisor stations will need to re-index accordingly upon upgrading to 4.10.   Please note, re-indexing can take a considerable time upon upgrade, and the DB will not have accurate information when queried until the index is complete accordingly. Prior to upgrading your Supervisor, please review System DB Must Be Re-indexed for Upgrades to Niagara 4.10+ from Earlier Niagara.     Niagara 4.10 and Third-Party Modules Keeping your Niagara installations safe and secure is our highest priority. In Niagara 4.10, ALL third-party modules must be signed with either a trusted valid certificate or a self-signed certificate to successfully run on a station. This new policy greatly increases the security posture of Niagara installations by making administrators aware of any modules that may have been tampered with, compromised or derived from untrustworthy sources.   Niagara's new signature enforcement feature is being rolled out over multiple Niagara releases. The first iteration was built into release 4.8 to give developers adequate time to make the transition to always signing any third-party modules.   Niagara 4.8 produced console and Security Dashboard warnings about unsigned modules but allowed them to run on a station. As of Niagara 4.10, unsigned modules will not execute.   For more information, please review the Niagara documentation on Third Party Module Signing   Niagara 4.10 Updated Operating Systems, Browsers, and Databases For the latest information on supported operating systems, please refer to Supported OS and other software in the Niagara 4 Framework Installation Guide.   Tridium remains focused on keeping pace with advancing IT infrastructure to enable more efficient, long-term support of each release version. This policy enhances the security posture of a Niagara installation by ensuring that only the most robust, secure operating systems and enterprise applications are compatible with the framework. The list below provides information on what we will be supporting with Niagara 4.10.   OS, Browser, Database Version Red Hat Enterprise Linux 8.1 (64 bit), 7.7 Windows Server 2019 (64 bit), Server 2016 (64 bit), Windows 10 (64 bit) VMWare ESXi 6.7 Oracle Database 19.3, 18.3, ... 12.2/12.1 MySQL Database 8 MS SQL Database 2019, 2017, 2016 Browsers Chrome, FireFox, Microsoft Edge Mobile Browsers Safari (iOS 12, 13), Chrome (Android 8, 9, 10)   As with all software products, we must also deprecate support for some operating systems and enterprise applications.  Nevertheless, you can be confident that the above list will handle your needs moving forward.   Using Web Launcher with Niagara 4.10 Web Launcher 20.4.2 was recently revamped for Niagara 4.10 to include essential software dependencies updates along with critical defect fixes. This version of Web Launcher has Java version 8 update 275 and certificate management has been updated to work with Niagara 4.10 along with any legacy or prospective release.   Prior to using Web Launcher with Niagara 4.10, the customer should update Web Launcher accordingly (see steps below). Updating WebLauncher Web Launcher has a feature to check for updates over the internet and prompts the user when a new version is available in the cloud. However, the existing version of Web Launcher has a bug that prevents a smooth update. Users will be required to perform a fresh install by downloading the latest version from the cloud via the station web Login page.   Click on the Niagara Web Launcher Installer link on the station's Web Launcher Web Page, which can be reached via the link on the Login page itself. Once the download is successful, click on the msi file and follow the installation wizard. You do not have to uninstall the older version. The new installation will automatically update to the latest version.
View full article
Guinan RandyDavis Guinan
‎2021-04-20 11:08 AM

on ‎2021-04-20 11:08 AM

Labels:
  • TAC IA Series
2432 Views

Default NRE Memory Pool Configuration Changes In N4.10

Issue The following error occurs on startup following upgrading of Niagara Station to  4.10.   SEVERE [20:42:01 23-Oct-20 UTC][nreconfig] invalid nre memory configuration values, 832 > 816   Product Line TAC IA Series Environment I/A Jace 8000 N4.10 Cause The default NRE memory pool settings are incorrect after an N4.10 upgrade and need configuration to function correctly. Resolution Niagara 4.10 and Default NRE Memory Pool Changes The increased size of some core libraries in Niagara 4.10 required changes to the default NRE Memory Pool settings for use on a JACE-8000. MetaSpace memory needed to be increased to allow applications to run without issue.   Note: Any previous custom memory configuration applied to the JACE-8000 will be reset upon upgrade to 4.10. The overall size of the pool of memory available to the NRE installation has decreased.  T As the overall size of the pool has decreased, customizations based on the old total pool size are invalid and cannot be maintained.   If a custom memory configuration is required, the user will need to manually adjust the platform administration menu after a device is upgraded. A longer-term approach to address this issue is in development and should be available with the Niagara 4.11 release.   NRE Memory pool default settings for Niagara 4.9: Changes to the default configuration: Heap Space size 4.9 value: 384 MB 4.10 value: 360 MB Meta Space size 4.9 value: 48 MB 4.10 value: 56 MB System reserve 4.10: allocated additional 16MB NRE Memory pool default settings for Niagara 4.10:
View full article
Guinan RandyDavis Guinan
‎2021-04-20 10:36 AM

on ‎2021-04-20 10:36 AM

Labels:
  • TAC IA Series
1278 Views

JACE 8000 LED status and accessibility in absence of MicroSD card

Warning Potential for Data Loss: The steps detailed in the resolution of this article may result in a loss of critical data if not performed properly. Before beginning these steps, make sure all important data is backed up in the event of data loss. If you are unsure or unfamiliar with any complex steps detailed in this article, please contact Product Support for assistance. Issue Both the STAT LED and the BEAT LED is off on the Jace controller and cannot successfully ping the JACE 8000 IP address Product Line TAC IA Series Environment I/A Series JACE 8000 Cause The STAT and BEAT LED remaining in an off state is an indication that no SD card is installed in the JACE card carrier.  When the Micro SD card is installed the STAT LED is solid Green, and BEAT LED is blinking Amber. Resolution Make sure to insert the SD card prior to startup commissioning of the JACE 8000. See JACE-8000 Install and Startup Guide
View full article
Lt. Commander Reza Lt. Commander
‎2021-03-30 08:40 AM

Last Updated: Guinan RandyDavis Guinan ‎2021-04-15 06:54 AM

Labels:
  • TAC IA Series
6399 Views

DUI Expander Objects for BACnet Devices in WorkPlace Tech

Issue Where are the DUI expander objects for the MNB-300 and MNB-1000 controllers in Workplace Tech? Product Line TAC IA Series Environment I/A Series WorkPlace Tech version 5.1 through 5.9.4 I/A Series WorkPlace Tech version 5.10.0 till current Cause The standard stencils do not include an object for Momentary SS or a DUI multiplexer.  Resolution The I/A Series BACnet controllers do not currently support the DUI object directly within the MNB-300 or MNB-1000. An application performing the same basic function was created and factory tested. This application was created as a custom object named "DUI_App". For support of these objects in Workplace Tech 5.1 until 5.9.4, log into The Exchange Download Center and download the file Application Objects_rev1.zip. There is also a detailed DUI_Application_Documentation_rev1.pdf that describes the operation of the "DUI_App". For support of these objects in Workplace Tech 5.10.0 until further notice, log into The Exchange Download Center and download the file Application Objects_rev2.zip. There is also a detailed DUI_Application_Documentation_rev2.pdf that describes the operation of the "DUI_App". Note: VAV box controllers do not have DUI expander objects available. See TB06-02 for additional details.
View full article
Picard Product_Support
‎2018-09-07 06:41 AM

Last Updated: Guinan RandyDavis Guinan ‎2021-04-02 06:02 AM

Labels:
  • TAC IA Series
2614 Views

Installation Guidelines for Electromagnetic Compatibility (EMC)

Issue Faulty operation of BMS equipment due to electrical interference from other equipment can be difficult and costly to identify and fix.  Guidance is required for the best installation practices to minimize the source of the interference and to protect against it when it occurs. Product Line Andover Continuum, EcoStruxure Building Operation, Field Devices, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC Vista Environment All electrical equipment Cause Poor installation can cause equipment to generate high and low-frequency electromagnetic interference that can disrupt the operation of other systems. Resolution Schneider Electric has produced a document Practical Installation Guidelines which discusses the theory and offers practical guidelines to protect against and minimize the generation of, electromagnetic interference.
View full article
Picard Product_Support
‎2018-09-06 12:00 PM

Last Updated: Administrator CraigEl Administrator ‎2021-02-01 04:32 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Operation
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC Vista
11622 Views

Disable items in Startup in Windows XP

Issue What utility in Windows XP can disable items in Startup? Environment Windows XP Cause Items that run on startup can sometimes make the boot up process for a PC very slow. Depending on which applications have been added to start automatically on startup, it can also cause problems if things load in the incorrect order. Resolution Click the Start button in Windows XP Select Run Type msconfig and click OK.
View full article
Picard Product_Support
‎2018-09-06 03:20 PM

Last Updated: Administrator CraigEl Administrator ‎2021-02-01 02:26 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1062 Views

How to find the IP address information on a PC?

Issue How to find the IP address information on a PC? Environment Windows Operating Systems Cause Need to identify the IP address of the workstation (PC). Resolution For a Windows 95/98 PC, go to a DOS screen and run WINIPCFG. For a Windows NT / XP / Windows7 / Server 2008 PC, run a CMD window and run IPCONFIG.
View full article
Picard Product_Support
‎2018-09-06 03:27 PM

Last Updated: Administrator CraigEl Administrator ‎2021-02-01 02:25 PM

Labels:
  • Andover Continuum
  • EcoStruxure Access Expert
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1317 Views

Controlling LonWorks sunblind actuator results in incorrect end position

Issue When opening (pull up) sunblind, it stops at the end of runtime and then rolls back down. When closing (pull down) sunblind, it stops at the end of runtime and then rolls back up. Environment Lonworks devices including REG-N MSE4 (SVEA 32237-346) Sunblind actuators Cause The sunblinds only have UP/DOWN functions, and there is no panel angle setting. The sunblinds are not venetian, just simple sunblinds. The sunblind actuator is preconfigured for use with venetian blinds. For example when driving down completely first the motor is energised for the time configured in UCPTdownDriveTime, then stops a short moment and then turns the angle of the lamella by energising the motor for the time configured in UCPTpanelTurnTime (dependent on the value of parameter UCPTdownPanelAngle). Resolution When not  using venetian blinds the parameters UCPTdownPanelAngle, UCPTupPanelAngle, UCPTpanelTurnTime and UCPTpanelTurnTimeBottom should be set to zero. Commands to the sunblind actuator then should as well have the value of zero in the rotation part of the SNVTsetting command.
View full article
Picard Product_Support
‎2018-09-06 08:41 AM

Last Updated: Administrator CraigEl Administrator ‎2021-02-01 02:19 PM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC Vista
1092 Views

Assign a static IP address on Windows 8

Issue Change an IP address on Windows 8 to a static address. Product Line Other Environment Windows 8 Cause Changing the IP address of a PC is often done to ensure it resides on the same subnet and network as the system or devices it is trying to communicate with. Resolution From the Start Menu (Tiles), open the Charms bar by moving the mouse to the right bottom corner of the screen or press the Windows Key + C and click on Search. Highlight Settings. In the Search box type Network to search for any network related options From the list options choose Network and Sharing Center. From the View Your Active Networks section, select Local Area Connection. Go to Properties. Result: The Local Area Connection Properties screen appears. Highlight Internet Protocol Version 4 (TCP/IPv4) and click on Properties. Result: The Internet Protocol Version 4 (TCP/IPv4) Properties screen appears. Click Use the following IP address. Complete the configuration fields as shown below. This part of the configuration requires attention to detail, because one error will prevent you from getting on the network. Be sure you have this information at hand when you start to configure the TCP/IP protocol: IP Address: x.x.x.x Subnet mask: 255.255.255.0 Default gateway: x.x.x.x  Enter these numbers in the appropriate fields and click OK. Continue to click OK or Close as appropriate until you return to the Network Connections screen. The Local Area Connection icon text should now say "Enabled". To test the new IP address: Open a command prompt in Windows 8 Swipe to show apps screen Scroll down and locate Windows system section heading Under Windows system, press or click on Command Prompt (a new Command Prompt window will open up on the Desktop.) You then can type in IPCONFIG then hit Enter and look for the new IPV4 address. You can also try to type in PING (IP ADDRESS) that should reply with the new IPV4 address if set correctly.
View full article
Picard Product_Support
‎2018-09-06 09:07 AM

Last Updated: Administrator CraigEl Administrator ‎2021-02-01 02:17 PM

Labels:
  • Andover Continuum
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1344 Views

Some helpful basic IP commands.

Issue Some helpful basic IP commands. Product Line Other Environment Computer with IP NIC or Network Cause Need for basic IP configuration or IP address Resolution Go to start, click run and type in "cmd". This takes you to the command prompt. Type in: "ping xxx.xxx.xxx.xxx" to see if your device is online and its response time. Make sure you put the space between "ping" and "xxx". "ipconfig" and hit enter to get the info of the computer you are currently using. You'll get the IP address, subnet mask and the gateway. "ipconfig/all" and hit enter to get more info on the machine your using. It will give you all the above and then some including the DNS server addresses. "tracert xxx.xxx.xxx.xxx" and hit enter and you can see the servers that you are going through to get to your destination. This can be used when connecting to a Loytec or a iLon and the IP address is being presented to the L-IP or iLon is unknown. Connecting through a firewall/gateway/NAT server, you are not presenting the PC's address - when you do the tracert you will go through your gateway and the next address will be the IP you are presenting- Use this in the iLon as the LNS server address.
View full article
Picard Product_Support
‎2018-09-06 03:05 PM

Last Updated: Administrator CraigEl Administrator ‎2021-02-01 02:16 PM

Labels:
  • Andover Continuum
  • EcoStruxure Access Expert
  • EcoStruxure Building Expert
  • EcoStruxure Building Operation
  • EcoStruxure Security Expert
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
1834 Views

Contact Barber Colman

Issue What is the contact information for Barber Colman Dyna group? What is the contact information for Barber Colman Aerospace division? What is the contact information for Barber Colman Industrial Instruments division? Environment Barber Colman Cause The old Barber Colman Dyna group is now a part of Woodward Governor. The old Barber Colman Aerospace division is now a part of the GE Aerospace. The old Barber Colman Industrial Instruments is now part of Eurotherm, an Invensys company. Resolution Barber Colman Dyna group is now Woodward Governor. They can be reached at 800-543-5811 Barber Colman Aerospace division is now GE Aerospace. They can be reached at 815-637-3500 Barber Colman Industrial Instruments is Eurotherm, an Invensys company. They can be reached at 815-637-3222 or 815-637-3404 for tech support.
View full article
Picard Product_Support
‎2018-09-07 02:24 AM

Last Updated: Administrator CraigEl Administrator ‎2021-02-01 02:10 PM

Labels:
  • Field Devices
  • TAC IA Series
3562 Views
  • « Previous
    • 1
    • …
    • 29
    • 30
    • 31
    • …
    • 92
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of