Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

Niagara R2 to G3 (AX) Data Exchange - oBIX vs. BACnet IP

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Niagara R2 to G3 (AX) Data Exchange - oBIX vs. BACnet IP
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • Chris_Asbury
    Chris_Asbury
  • DavidFisher
    DavidFisher
  • sesa116871
    sesa116871
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
6721 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Niagara R2 to G3 (AX) Data Exchange - oBIX vs. BACnet IP

Picard Product_Support
‎2018-09-11 02:05 PM

Last Updated: Guinan RandyDavis Guinan ‎2022-08-10 06:54 AM

Issue

Factors to consider using oBIX vs. BACnet IP to exchange data between Niagara R2 and G3 systems

Product Line

TAC IA Series

Environment

  • Niagara R2 version 522 and later
  • Niagara G3 version 3.4 and later

Cause

Planning factors to consider as to which method is better suited for the customer

Resolution

Either solution has pros and cons regarding implementation. One needs to think about what fits and how much engineering is required.

 If the R2 UNCs (Jaces) are nearly full (CPU and/or memory or less than 40% idle time), then oBIX probably can't be used. It requires some resources to drop in the oBIX service. But if their CPU usage is good (> 40% idle time) and the resource count isn't near the limit, the oBIX service should fit into the UNC.

With oBIX, one has access to much more information in the R2 station than with BACnet. BACnet just gives access to its standard objects (BV, BO, AV, AO, etc). oBIX would provide access to just about anything in the station, though some things might be in a string format. One could get trend logs and such using oBIX.  Please also note that R2 oBIX is server only - no R2 "shadow objects" exist to obtain remote oBIX data (e.g. from a G3 station).

For additional details, refer to the following documents:

Niagara AX-3.x oBIX Guide

Niagara R2 to Niagara AX via oBIX Engineering Notes

 

With BACnet IP, one would need to set all the R2 points 'Foreign Address' field for any point to be available to the G3 station.  Then, configure the G3 BACnet network, and discover the R2 devices and points (Note that if the G3 station is a supervisor, or Enterprise Server, a BACnet license feature with the appropriate number of BACnet points must be purchased).  

A G3 supervisor PC should handle 5000 oBIX or BACnet points, provided the station is properly licensed.  

Labels (1)
Labels:
  • TAC IA Series
Attachments
Tags (2)
  • Find more articles tagged with:
  • 13352
  • ChrisAsbury22
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore