Internal modem can be installed in the field on a Niagara G3 ENC
  • Internal modem can be installed in the field on a Niagara G3 ENC
  • sesa116873_brid
    sesa116873_brid
  • CraigEl
    CraigEl
‎2018-09-06 01:25 PM
Last Updated: Administrator CraigEl Administrator ‎2022-08-10 02:17 AM
Can an internal modem be installed in the field on a Niagara G3 ENC. If so, what is the part number?
TAC IA Series
Niagara G3, ENC-410, ENC-520
Can an internal modem be installed in the field on a Niagara G3 ENC?
An internal modem can be field installed on an ENC after purchase. No license changes are required. Both the ENC-410 and the ENC-520 uses the same part number, UNC-410-MDM.
Reference the Replacing the Modem section of the TAC I/A ENC-xxx Installation Instructions documents for details on installing the internal modem.
  • ENC-410 (document #F-27415)
  • ENC-520 (document #F-27416)
Reference Configure a Niagara G3 ENC serial port for dialup modem on setting up the port for dialup modem.
  • TAC IA Series
  • 6186