Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

I/A series R2 Niagara Master/Slave schedules not working

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • I/A series R2 Niagara Master/Slave schedules not working
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • Kim_Baze
    Kim_Baze
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1286 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

I/A series R2 Niagara Master/Slave schedules not working

Picard Product_Support
‎2018-09-10 06:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 11:35 PM

Issue

Master / Slave schedules not working

Product Line

TAC IA Series

Environment

I/A series R2 Niagara

Cause

When Master / Slave schedules not functioning properly the most common cause is an issue with the Address books.

Another issue that can cause this is the firewall application on the Enterprise Server computer.

Resolution

To confirm it is an Address book issue conduct the following test:

  1. Create an AO object in the Master device (typically the Enterprise Server) and the Slave device (typically the UNC). 
  2. Link the output of the AO in the Master device to the input of the AO in the Slave device. 
  3. Link the output of the AO in the Slave device to the input of the AO in the Master device. 

When viewing the AO's at each station in the WorkspaceEditor there should be little boxes on both sides of each AO indicating both devices can send and receive data. 

If an Address book issue exists there will be a box missing at one device or the other.  To correct this issue:

  1. Reboot which ever station only shows one box by its AO.  If the issue persists go to step 2.
  2. Clear the address book entries in the device that has the AO with both boxes (this is usually the UNC) and reboot the device. 
  3. When the station comes back up carefully re-enter the Address book data and then check each AO to make sure both have two boxes.  Typically this will resolve the issue, but until both AO's have boxes on both sides the issue is not resolved. 

It may be necessary to clear and redefine the address book a second time or clear and redefine the address books in both devices to pass this test.  Once the AO test is successful the Master / Slave scheduling will link and function as expected.


Ensure that ports 80 and 3011 are added as exceptions in the firewall application. Refer to Which antivirus software is compatible with Niagara R2 and G3? for details.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 7132
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of