A network of GCM-86000s with EtherNet NIMs does not have bi-directional communications between all GCM/ NIMs

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • A network of GCM-86000s with EtherNet NIMs does not have bi-directional communications between all GCM/ NIMs
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support
  • SESA113595
    SESA113595

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1660 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

A network of GCM-86000s with EtherNet NIMs does not have bi-directional communications between all GCM/ NIMs

Picard Product_Support
‎2018-09-10 05:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-10 05:38 PM

Issue

A network of GCM-86000s with EtherNet NIMs does not have bi-directional communications between all GCM/ NIMs. It is a shared network with routers. Some symptoms reported include:

  1. A GCM/ NIM may be able to send to some GCM/ NIMs, but not to others.
  2. A GCM/ NIM may be able to receive data from some GCM/NIMs, but not from others.
  3. A GCM/ NIM may be able to send to a GCM/NIM, but not receive data from that GCM/NIM.
  4. You might be able to "ping" all GCM/NIMs on the network, and ACCESS all of them from the GCM menu, but still have issues as in 1-3 above.

Product Line

TAC IA Series

Environment

  • GCM-86000 series (including LNC-100, SIM-CCN, SIM-MTECH, SIM-TRANE, and SIM-YORK)
  • EtherNet NIM (GCM-ETH-001)
  • Shared (customer's) EtherNet LAN with routers

Cause

In the NIM block of one or more of the affected GCM/ NIMs, the IP Multicast address (IPMLT) is set incorrectly. In the following example, the NIM block parameters were taken from a network of four GCM/NIMs, experiencing all four of the issues noted above.

 

 

GCM#1 GCM#2 GCM#3 GCM#4

 

5.4A 5.3A 5.4A 5.4A

 

11.2T 11.2T 11.2T 11.2T
PNLIP 010.020.000.028 010.020.000.019 010.020.004.008 010.020.004.009
RTRIP 010.020.000.001 010.020.000.001 010.020.000.001 010.020.000.001
DIRSV 010.020.000.028 010.020.000.028 010.020.000.028 010.020.000.028
ETHML 01.20.96.01.00.00 01.20.96.01.00.00 01.20.96.01.00.00 01.20.96.01.00.00
IPMLT 010.020.000.019 010.020.000.019 010.020.000.019 010.120.000.019
IPSUB 255.255.000.000 255.255.000.000 255.255.000.000 255.255.000.000
UDPPT 1235 1235 1235 1235

Resolution

On a shared network with routers, the IP Multicast address (IPMLT) should be the same as the Panel IP address (PNLIP);
IPMLT = PNLIP.

  1. Using the appropriate FLASH clear procedure, and set the NIM block parameters so that IPMLT = PNLIP. In the example below, make the changes to the IPMLT as high-lighted in yellow.

 

GCM#1 GCM#2 GCM#3 GCM#4
GCM Rev. 5.4A 5.3A 5.4A 5.4A
NIM Rev. 11.2T 11.2T 11.2T 11.2T
PNLIP 010.020.000.028 010.020.000.019 010.020.004.008 010.020.004.009
RTRIP 010.020.000.001 010.020.000.001 010.020.000.001 010.020.000.001
DIRSV 010.020.000.028 010.020.000.028 010.020.000.028 010.020.000.028
ETHML 01.20.96.01.00.00 01.20.96.01.00.00 01.20.96.01.00.00 01.20.96.01.00.00
IPMLT 010.020.000.028 010.020.000.019 010.020.004.008 010.020.004.009
IPSUB 255.255.000.000 255.255.000.000 255.255.000.000 255.255.000.000
UDPPT 1235 1235 1235 1235

See the Nim Networking and Configuration Guide, F-25955-4, Chapter 2, "GCM Shared Network Address Guidelines (Routed Network)" for details.

  1. For EtherNet NIMs with firmware revisions 11.2P or 11.2T, see "Special NIM Address Switch Functions" for the REVISED FLASH clear procedure.
  2. For EtherNet NIMs with firmware revisions 11.1F or earlier, see "Flash clear" procedure for GCM Ethernet NIMs (GCM-ETH-001) with firmware prior to revision 11.2P.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 6718
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore