"Flash clear" procedure for GCM Ethernet NIMs (GCM-ETH-001) with firmware prior to revision 11.2P.
  • "Flash clear" procedure for GCM Ethernet NIMs (GCM-ETH-001) with firmware prior to revision 11.2P.
‎2018-09-10 12:55 AM
Last Updated: Crewman ContentModerator ‎2025-10-10 02:54 AM
Significant changes and improvements were introduced with firmware revision 11.2P, including a streamlined "Flash clear" procedure.
For Ethernet NIMs with firmware revisions prior to 11.2P, the procedure was documented in Technical Bulletin 99-56 (see below).
The procedure in bulletin 99-56 was a revision of the procedure in the original NIM Networking and Configuration Practices manual, F-25955, which is no longer available. The current version of the manual, F-25955-4, applies only to NIMs with firmware  revisions 11.2P and 11.2T.
Ethernet NIM for network 8000; GCM-ETH-001 with firmware revision prior to 11.2P.
"Flash clear" procedure was changed in firmware revision 11.2P
Follow the "Flash clear" procedure per Technical Bulletin 99-56.