Signing a Niagara N4 Program Object

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Signing a Niagara N4 Program Object
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
2 Likes
3068 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Signing a Niagara N4 Program Object

Guinan RandyDavis Guinan
‎2022-08-10 04:01 PM

on ‎2022-08-10 04:01 PM

Issue

Every time you compile a program object you get a message saying the "Program is not signed"

ProgamObject_1.gif

 

Product Line

TAC IA Series

Environment

  • I/A Series N4 Jace 8000
  • I/A Series N4 Enterprise Server

Cause

Tridium's Niagara N4 product will at some point in the future require code signing

Resolution

Create the main certificate in our Workbench to be used for signing our Program Objects.

  1. Go to the top drop-down menu on the Workbench and select "Tools - Certificate Management". Note: do not open the Certificate Management of your Platform. That is different and will be used for our running stations, not for this purpose.
  2. On the "User Key Store" tab, press "New" to create a new certificate.
  3. Fill in all the required fields.
  4. Make sure you change the "Not After" date so the certificate does not expire in just 1 year.
  5. Select the specific "Certificate Usage" as "Code Signing"
    ProgamObject_2.gif

     

  6. Press "OK" and set a password for your certificate. Remember: this password will be asked by the workbench at the point of compiling your code.ProgamObject_3.gif
  7. Now select the new certificate, then press the "Export" button below
    ProgamObject_4.gif

     

  8. Export the certificate without the private key. You will be prompted then to give your certificate file a name and store it in your computer.
    ProgamObject_5.gif

    We would also recommend exporting the certificate again, this time with the private key included, and storing it with an indicative name, in case you want to transfer it to a different machine.

  9. Change tab and move to the "User Trust Store".
  10. From there, press the button "Import" at the bottom and select the certificate without the private key. It should appear in green as accepted in the windows above.ProgamObject_6.gif
  11. Go to the top drop-down menu, and select "Tools - Options"
  12. Find the "Code Signing Options" on the left-hand side, and on the "Signing Cert" section select the certificate we have just created and accepted on our Workbench. Then press OK to confirm.

    ProgamObject_7.gif
  13. Open the local host Platform, and double-click the platform Certificate Management.
  14. Select the tab "User Trust Store", then press the button "Import" and select again the certificate without the private key.

On the station running locally, you can now compile your code.

Note that the first time the Workbench will ask for your password (the one you assigned when creating the certificate). Add the password and see that the code now compiles with no certificate error
ProgamObject_8.gif

If you try compiling code on a Jace, it will return the "Certificate not trusted" until you add the certificate to the Jace Certificate Management too.
ProgamObject_9.gif

On the Jace Platform, double click the "Certificate Management", then select the tab "User Trust Store".

In there, press "Import" and select your certificate without the private key. Your program objects will now compile correctly.

 

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • RandyDavis22
Was this article helpful? Yes No
100% helpful (4/4)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore