Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Building Automation Knowledge Base
  • Label: TAC IA Series
Options
  • My Knowledge Base Contributions
  • Subscribe
  • Bookmark
  • Invite a Friend
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • Andover Continuum 2,197
  • TAC Vista 2,029
  • EcoStruxure Building Operation 1,897
  • TAC IA Series 1,684
  • TAC INET 1,444
  • Field Devices 722
  • Satchwell BAS & Sigma 402
  • EcoStruxure Security Expert 343
  • EcoStruxure Building Expert 222
  • Satchwell MicroNet 212
  • EcoStruxure Access Expert 153
  • CCTV 52
  • Project Configuration Tool 48
  • EcoStruxure Building Activate 19
  • EcoStruxure Building Advisor 13
  • ESMI Fire Detection 13
  • Automated Engineering Tool 5
  • EcoStruxure Building Data Platform 3
  • EcoStruxure Workplace Advisor 1
  • EcoStruxure for Retail - IMP 1
Top Contributors
  • Product_Support
    Product_Support
  • DavidFisher
    DavidFisher
  • CraigEl
    CraigEl
See More Contributors
Related Products
Thumbnail of EcoStruxure™ Building Operation
Schneider Electric
EcoStruxure™ Building Operation
4
Thumbnail of SmartX IP Controllers
Schneider Electric
SmartX IP Controllers
1
Thumbnail of EcoStruxure™ Building Advisor
Schneider Electric
EcoStruxure™ Building Advisor
1

Related Forums

  • Intelligent Devices Forum

Previous Next

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite

Label: "tac ia series"

View in: "Building Automation Knowledge Base" | Community

1684 Posts | First Used: 2018-09-06

Building Automation Knowledge Base

Sort by:
Date
  • Date
  • Views
  • Likes
  • Helpfulness
Options
  • Subscribe
  • Bookmark
  • Invite a Friend
  • « Previous
    • 1
    • …
    • 30
    • 31
    • 32
    • …
    • 85
  • Next »
Label: "TAC IA Series" Show all articles

Downgrading an UNC to an earlier Niagara build

Issue Downgrading an UNC to an earlier Niagara build Product Line TAC IA Series Environment I/A Series R2 Universal Network Controller (UNC) Cause Station is unable to run in an UNC with newer version of Niagara R2 because a 3rd party module does not have an updated JAR file Resolution The procedure to downgrade an UNC would be to use the version of WorkPlace Pro that you want the UNC to be and commission the UNC as per what you would do for a new UNC or to upgrade an UNC. The modules installed in the station should also match the Niagara version of the UNC. Refer to Can jar files from Niagara R2 version 532 be used with a UNC running version 330?. Refer to Procedure 4 on pages 9 and 10 of the UNC-520 Installation Instructions for details on installing the software to an UNC-520. It is important to note that newer UNCs with the newer boot flash chip requires I/A Series R2 version r2.301.527 or newer. Installing the UNC with newer boot flash chip with an I/A Series R2 version lower than r2.301.527 will make the UNC inoperable. Refer to Cannot get my I/A Series (Niagara) R2 UNC to boot after downgrading the system software to a version earlier than release 529 for details.
View full article
Picard Product_Support
‎2018-09-10 11:25 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 08:41 PM

Labels:
  • TAC IA Series
3747 Views

MNL-800 both the top green and amber LEDs are on continuously

Issue What does it mean on an MNL-800 if both the top green LED (Transmit) and the Amber LED (Receive) are on continuously? Product Line TAC IA Series Environment MNL-50 MNL-100 MNL-200 MNL-800 MNL-V1R MNL-V2R MNL-V3R Cause LEDs indicate LON traffic on the trunk Resolution For an explanation of the Transmit (Green LED) and Receive (Red LED) see F-26724, MNL-800 Installation Instructions, Table 1 LED Indications: LED Operation Status Green ON Normally ON indicating controller is powered and not actively transmitting data on the LON. Flashes OFF Flashes OFF while actively transmitting data on the LON. Amber OFF Normally OFF unless actively receiving data from the LON. Flashes ON Flashes ON while actively receiving data from the LON. Red OFF  (Neuron - normal communications) indicates the Neuron is operating properly allowing normal communications to and from the HVAC application. OFF  (Neuron - Offline) Neuron responds to network management messages only. In this state, communication to and from the HVAC application is not possible. To correct, place the Neuron online by downloading an application using WP Tech or configure using a third party management tool. Blinking The service LED blinks at 0.5 Hz rate (1 second ON, 1 second OFF) to indicate that the Neuron is unconfigured (i.e. communications parameters not loaded). Corrective action: Configure the Neuron by downloading an application using the Work Place Technician's Tool or configure the neuron using a third party management tool. ON Indicates Neuron is not operating properly. Replace controller.  Heartbeat (Green LED) Blinking (Normal Operation) The heartbeat LED blinks at 0.5 second ON, 0.5 second OFF to indicate controller is operating properly. Wink Mode Wink mode provides a visual means for identifying the controller using WP Tech or third party management tool. During wink, the heartbeat LED blinks as follows: With revision 1.x firmware: 2 seconds ON, 0.5 seconds OFF; cycles five times for a total of 12.5 seconds of wink time. With revision 2.x (or later) firmware: 3 seconds ON, 1 second OFF; cycles three times for a total of 12 seconds wink time. Diagnostic Blink (RAM/ROM Failure) The heartbeat LED repeats a pattern of 2 quick flashes followed by pause. To correct, turn power OFF then ON. Replace controller if necessary. Diagnostic Blink (ROM Failure) The heartbeat LED repeats a pattern of three quick flashes followed by a pause. To correct, turn power OFF then ON. Replace controller if necessary. Diagnostic Blink  (RAM Failure) The heartbeat LED repeats a pattern of four quick flashes followed by a pause. To correct, turn power OFF then ON. Replace controller if necessary. OFF Indicates controller is not operating properly. Check power. Replace controller if necessary.      If the amber LED is blinking fast enough, it appears to be ON continuously, so it is receiving data at a high frequency. The other MNL devices on the same LON should all be behaving the same way, indicating a lot of LON traffic. Confirm with a LON protocol analyzer. If excessive LON communications traffic is suspected, see How can LON communications be throttled in MNL-800 controllers? for a method of throttling LON traffic.
View full article
Picard Product_Support
‎2018-09-10 12:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 07:03 PM

Labels:
  • TAC IA Series
2135 Views

ENC-520 with 512MB of RAM

Issue Can an ENC-520 be ordered with 512MB of RAM? Product Line TAC IA Series Environment I/A Series G3 ENC-520 / ENC-520-2-N Cause Need for 512MB RAM in an ENC-520 instead of the standard 256MB RAM Resolution There is no option to order an ENC-520 with 512MB or any other RAM size other than 256MB. New ENC-520s ordered will be of the extended memory version and shipped with 256MB of RAM. Also refer to related Can I upgrade the ENC-410 or ENC-520 memory in the field or return to the factory to have the memory increased?.   
View full article
Picard Product_Support
‎2018-09-10 08:16 PM

Last Updated: Admiral David_Kendrick Admiral ‎2022-08-09 03:15 AM

Labels:
  • TAC IA Series
1277 Views

I/A Series R2 (Niagara) station opened in the Admin Tool displays "Disabled"

Issue An I/A Series R2 (Niagara) station opened in the Admin Tool displays "Disabled." What does this error message mean? Product Line TAC IA Series Environment An I/A Series R2 (Niagara) UNC. Cause When a station is in the disabled mode, it indicates that the station has rebooted multiple times in a five minute period. Possible causes are rapid fluctuations in the AC power supplying the UNC, a bad battery, or a station with less than 20% idle time. Resolution Disconnect the battery, then cycle power to the UNC and see if it boots up normally. Run the system spy: in a browser, enter  http:// (ipaddress of UNC):3011/system/spy. Login with the hardware user name and password. At the bottom of the page, click on "Reset Counter", then check to see if the idle time exceeds 20%. If not, the station will need to be tuned to increase the idle time. Check battery per Niagara R2/G3 UNC/JACE reboots every 15 minutes with "Battery test failed" logged. See Batteries for the UNC-410 and UNC-520 are interchangeable for battery part numbers.
View full article
Picard Product_Support
‎2018-09-10 05:33 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:20 AM

Labels:
  • TAC IA Series
1797 Views

Integrating Xenta programmable controllers into a Niagara R2 UNC-520 Controller

Issue Since both products -- Xenta programmables and the UNC 520 -- speak LON protocol, there is some assumption that integration should be seamless.  In the case of ASCs, this is true, but Xenta programmable controllers use some forms of proprietary communication that can complicate the integration. Product Line TAC IA Series, TAC Vista Environment Xenta programmables Xenta 280, 281, 282, 283, 300, 301, 302, 401, 401:B UNC-520 Niagara Tridium Cause Xenta programmables use proprietary communications for three main purposes: To communicate their online status between group members and group masters To communicate between a base unit and associated I/O modules To pass proprietary TAC Network Variables between two programmable controllers In a UNC-520, the first function would be taken over by the new network manager (Local Lon Device).  However, the second two must use Group Bindings set through a Vista compatible network management tool like LonMaker or NL220.  If the controllers are commissioned into the UNC-520, that communication will be broken and I/O modules will go offline and no network variables will pass. Resolution  It is possible to engineer a TAC Vista network as usual, using an LNS management tool to create group bindings to facilitate proprietary communications.  A UNC-520, set to non-network management mode could then be implemented on top. However, any attempt to commission the devices into the UNC-520 network will break that proprietary communication.  To prevent this scenario from occurring, the simplest method is: Do not use proprietary TAC Network Variables to pass data between controllers. Use only SNVTs which will be available to a third party LON network manager like the UNC-520 Make no SNVT bindings in a temporary LonMaker or NL220 database.  Let the UNC-520 handle all network management duties. Do not define Xenta I/O modules in the Menta Device Specification. Use only Xenta 421A, 422A, 451A and 452A I/O modules.  These have the capability to act as stand-alone LON nodes. Define the modules as LON nodes, configure them using Configuring inputs on Xenta 421A or 451A when using the controller as a stand alone Lonworks node. Bind to the inputs and outputs of the I/O modules in the UNC-520.
View full article
Picard Product_Support
‎2018-09-07 05:41 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 05:06 AM

Labels:
  • TAC IA Series
  • TAC Vista
2285 Views

Time Zone Database shows +0 for all time zones when the platform date is in 2016

Issue Time Zone Database shows +0 for all time zones when the platform date is in 2016. IA Series G3 version 3.6.407 IA Series G3 version 3.7.108 IA Series G3 version 3.8.41 Product Line TAC IA Series Environment IA Series G3 versions 3.6.407, 3.7.108, and 3.8.41 Cause This error appears when listing the contents of the Niagara Time Zone database where the Time Zone Database shows +0 for all time zones when the platform date is in 2016.  The issue is related to an error within the 3.8.41 baja and hx modules and only affects the display within the Platform view only.  The actual behavior and operation of the Time Zone remains accurate.  Prior IA Series G3 versions (e.g. 3.8.38, 3.7.106, and 3.6.406) or earlier will not exhibit this issue. Resolution Download and upgrade the baja and hx modules available in the latest consolidated patch files. baja 3.6.407.3 (or higher) and hx 3.6.407.1 (or higher) baja 3.7.108.3 (or higher) and hx 3.7.108.1 (or higher) baja 3.8.41.2 (or higher) and hx 3.8.41.1 (or higher) The consolidated patch files are available for download on the Buildings Download Center.  Login to the Schneider Electric Buildings Download Center and enter Consolidated_Patches in the search area (reference Latest consolidated patch files for I/A Series G3 maintenance builds with details).  Download and install the appropriate patch for the version.
View full article
Picard Product_Support
‎2018-09-10 01:51 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:56 AM

Labels:
  • TAC IA Series
2310 Views

I/A Series G3 software documentation

Issue Where to obtain the documentation for I/A Series G3 software. Product Line TAC IA Series Environment I/A Series G3 software and hardware Cause Documentation is provided as a part of the software package.  Resolution The current documentation for any release of the I/A Series G3 software (except for proprietary drivers) is installed with the full software installation.  The documentation can be found in the docs folder under the \Niagara\niagara-x.x.x\ installation folder. Refer to Documentation for the I/A Series G3 Schneider Electric proprietary drivers for information on the availability of the I/A Series G3 Schneider Electric (TAC) proprietary driver documentation.
View full article
Picard Product_Support
‎2018-09-10 05:35 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:45 AM

Labels:
  • TAC IA Series
1766 Views

I/A Series G3 weather service will not connect - error indicates java.net.SocketTimeoutException: connect timed out

Issue I/A Series G3 weather service will not connect - error indicates java.net.SocketTimeoutException: connect timed out.  A browser on the same computer is able to access www.weather.gov without issue.  The application director output window displays the following ... WARNING [12:56:28 05-Dec-13 EST][weather] Updating forecast failed for Battle$20Creek java.net.SocketTimeoutException: connect timed out at java.net.PlainSocketImpl.socketConnect(Native Method) at java.net.PlainSocketImpl.doConnect(Unknown Source) at java.net.PlainSocketImpl.connectToAddress(Unknown Source) at java.net.PlainSocketImpl.connect(Unknown Source) at java.net.SocksSocketImpl.connect(Unknown Source) at java.net.Socket.connect(Unknown Source) at javax.baja.naming.BIpHost$SocketFactory.open(BIpHost.java:271) at javax.baja.naming.BIpHost$SocketFactory.open(BIpHost.java:264) at javax.baja.naming.BIpHost.openSocket(BIpHost.java:129) at javax.baja.net.HttpConnection.connect(HttpConnection.java:263) at javax.baja.net.HttpConnection.connect(HttpConnection.java:238) at com.tridium.weather.nws.NwsForecastReader.getFeed(NwsForecastReader.java:76) at com.tridium.weather.nws.NwsForecastReader.getFeed(NwsForecastReader.java:55) at com.tridium.weather.nws.NwsForecastReader.getForecast(NwsForecastReader.java:135) at com.tridium.weather.nws.BNwsWeatherProvider.updateReport(BNwsWeatherProvider.java:450) at javax.baja.weather.BWeatherReport.doUpdateWeatherReport(BWeatherReport.java:269) at auto.javax_baja_weather_BWeatherReport.invoke(AutoGenerated) at com.tridium.sys.schema.ComponentSlotMap.invoke(ComponentSlotMap.java:1357) at com.tridium.sys.engine.EngineUtil.doInvoke(EngineUtil.java:49) Product Line TAC IA Series Environment I/A Series G3 Enterprise Network Server ENC JACE Cause The connection timeout may be related to the proxy server.  By default, the weather service driver contacts the various weather.gov sites (alerts.weather.gov, graphical.weather.gov, etc.) directly as opposed to routing through the proxy server.  The connection times out as the proxy server is unable to route the request. I/A Series G3 (3.4 and higher) provides a service that can be added to the station.  The HttpProxyServer service is used to configure the station so that outbound web services know how to get through an outbound non-transparent proxy server.  The HttpProxyServer service located in the net module. Configure this service to the proxy server that will be routing. The user guide states the following. All services that make use of the bajax.baja.net.HttpConnection class will automatically roll over to using the proxy server once the HttpProxyService has been configured and enabled. The Weather Service is one of the services that is affected by this feature. Resolution Verify the updated weather modules are installed, see Weather information provided through the weather module in I/A Series G3 is no longer updating. weather-3.4.67.3 or higher weather-3.5.39.5 or higher weather-3.6.37.4 or higher To use this component: Open the net (Network API) module in the Workbench palette. Add the HttpProxyServer to the Services of the station. Configure the following properties in the Property Sheet view as required.     Status - This display only property displays the status of the Http Proxy Service. Fault Cause - This display only property provides an error message that indicates the reason for a fault. Enabled - This property has a true (enabled) and false (disabled) option. Server - This property provides a text field for entering the address of the proxy server you are connecting to. Port - This property is for specifying the port number for communicating with the proxy server. Exclusions - This text field allows you to designate addresses that are allowed to be contacted directly, therefore “excluding” them from having to be contacted through the proxy server. The default addresses in the field are typical addresses followed by a slash (/) and the subnet mask designation. Authentication Scheme - This property provides the following two options:      None - no authentication is required at the proxy server when this option is set.      Basic - basic authentication is required at the proxy server when this option is set. User - This is the login name to be used when authentication is set to Basic. Password - This is the password text that is to be used when authentication is set to Basic.
View full article
Picard Product_Support
‎2018-09-11 06:26 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:19 AM

Labels:
  • TAC IA Series
1910 Views

Ordering more LNS credits

Issue How to place an order for more LNS credits to allow LNS plug-ins to work and to be able to commission more devices. Product Line TAC IA Series, TAC Vista Environment LonMaker NL220 LNS Cause There are two types of credits: Product specific credits like LonMaker and NL credits LNS credits   LNS LNS credits are assigned to the PC and when they reach zero, the LNS Server license goes into deficit mode. After 14 days the deficit mode will expire, at which time no LNS tools will be able to be used on that PC. To reverse the lockout, enough LNS credits must be ordered to cover the deficit and any additional nodes that need to be commissioned. Backing up, sharing, and restoring LNS databases can sometimes corrupt these LNS credits, which then prohibits you from launching any LNS plug-ins. For more help with corrupt LNS credits see Corrupted LNS Credits. LonMaker LonMaker credits are assigned to the PC. Both LNS and LonMaker credits are required, however when commissioning devices in LonMaker, LonMaker credits are consumed but LNS credits are not. Even though LNS credits are not consumed in LonMaker they are still necessary because certain LNS applications (i.e. TAC Vista System Plug-in) require them to operate. NL220 Each time a node is commissioned in NL220 it requires a NL credit and a LNS credit. NL credits are assigned to the NL220 dongle and can be used on other PCs in "MOVED" mode. LNS credits are also necessary in NL220 to operate certain LNS applications such as the TAC Vista System Plug-in.   To order more Echelon LonMaker credits see Ordering more Echelon LonMaker credits. To order more Newron NL220 credits see Ordering more Newron NL220 credits. Resolution To check the amount of LNS credits remaining on a PC go to Start > All Programs > Echelon LNS Utilities > LNS Server License Wizard and look for Credits Available.   To order more LNS credits: Go to Start > All Programs > Echelon LNS Utilities > LNS Server License Wizard In the box named Credit Order, type in how many credits to order, then click Next. Following the instructions at the top of the window, Click the Copy to Clipboard button to copy the PC key generated by LNS Server License Wizard. Click Cancel. Compose a new email and paste the PC key into the body of the email. Address the email to credits@echelon.com or your local Schneider Electric Buildings Business order department so they can place the order. Follow the instructions at the top of the email making sure to fill out all required fields. Once Echelon or the local Schneider Electric Buildings Business order department sends back an Application Key, go to Start > All Programs > Echelon LNS Utilities > LNS Server License Wizard. Click next and paste the application key into the field titled "Application Key". Click Finish.
View full article
Picard Product_Support
‎2018-09-10 05:16 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 01:16 AM

Labels:
  • TAC IA Series
  • TAC Vista
2304 Views

Ensure proper network biasing on a BACnet MS/TP network

Issue All MNB devices under the UNC-520 are offline and not communicating. Product Line TAC IA Series Environment MNB controllers connected to UNC-520 RS-485 port Cause The MNB-300 and MNB-1000 bias resistors (jumpers label 'MS BIAS') should be disabled by default as indicated in their respective documentation. However, it appears that the MNB-1000 bias resistors are coming enabled. As a requirement of EIA-485 network topology, an MS/TP network must have at least one set, and no more than two sets, of network bias resistors on each MS/TP network segment, preferably (but not required to be) in the middle of the segment. In MS/TP networks, this requires an MNB-300, MNB-1000, or UNC-520 with the appropriate jumper settings. UNC-520 bias resistors on its RS-485 ports are enabled by default. Resolution Ensure that no more than 2 sets of bias are enabled on the MS/TP segment. The bias on the UNC-520 is enabled by default and as such, there should not be more than 1 MNB controller with its bias resistors set enabled on the BACnet MS/TP segment. Refer to page 71 of the document ‘F-27360 IA Series Micronet BACnet Wiring, Networking and Best Practices Guide’ for further information. Also refer to Enabling MSTP bias resistors on a MNB-1000.
View full article
Picard Product_Support
‎2018-09-07 04:14 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:27 AM

Labels:
  • TAC IA Series
2967 Views

Can a Niagara G3 ENC license be branded as "open" so that any Tridium integrator can access it?

Issue A job site has several ENCs installed each doing a LON integration and a Schneider-Electric legacy integration (like ASD, GCM, DMS, or MS). Any ENC is currently licensed with the following filter: accept.wb.in="TAC". This only allows copies of Workbench branded as "TAC" to connect with it and perform tasks like data extraction and logic programming. Can an ENC's brand filter of "TAC" be changed to "*" to allow any company's copy of Workbench to access it? Product Line TAC IA Series Environment Niagara G3 ENC-410, ENC-520 Cause Sites may contain equipment from two Tridium integrators and the end customer wants one copy of Workbench to work with all equipment. A performance contracting company may also be Tridium integrators and want access to the ENCs with their own copy of Workbench. Resolution Typically, if the ENC does not have a Schneider-Electric legacy integration, an open branding of the license is allowable. However, for all requests to open brand a Niagara G3 license, contact Schneider-Electric's Regional Sales Manager (customer care can provide the contact name for your office) If this is a new order, an open branding of the license can be requested directly on the license order form. See Niagara G3 (NiagaraAx) Open NiCS (Niagara Compatibility Statement) for details.
View full article
Picard Product_Support
‎2018-09-10 03:05 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:26 AM

Labels:
  • TAC IA Series
1985 Views

Cannot get the AX Tunnel client to establish an ASD connection through the UNC to ASD devices, reporting "GCM Not responding"

Issue Gets error message "GCM Not responding" when he attempts to make a connection to a device on the ASD bus under the UNC. Product Line TAC IA Series Environment I/A Series R2 UNC I/A Series R2 TunnelAX jar file, version 2.301.534a or later I/A Series ibsASD jar file, version 2.301.534a or later I/A Series G3 Serial Tunnel 2.0 Client Cause Misconfiguration of tunnel name Resolution Before attempting to configure the AX Tunneling, verify that the correct versions of the R2tunnelAX and ibsAsd jar files have been installed as documented in How to install an I/A Series R2 JAR File. Tunnel Name in AX Tunnel Client must match the Tunnel Instance name in the ASD Service. When you add the AxSerialTunnel to the ibsAsdService, the identifier is automatically assigned based on the port defined in the communications configuration of the IbsAsdService itself.  This name is displayed under the Status tab of the AxSerialTunnel: Figure-1 When configuring the "Niagara AX Serial Tunnel 2.0", the following window is displayed. Figure-2 The tunnel name (See Figure 2) entered in this window must match the port identifier shown in the AxSerial Tunnel definition (See Figure 1).  If these identifiers do not match, the Ax Serial Tunnel Client will not be able to connect to the tunnel in the I/A Series R2 station. NOTE: When installing the I/A Series G3 Serial Tunnel 2.0 Client, no control panel applet is created as with the earlier version of the I/A Series R2 Serial Tunnel Client.   To configure the I/A Series G3 Serial Tunnel 2.0 Client,  run the program C:\niagara\VserAx\vseraxConfig.exe.  If you need to frequently reconfigure this client, you can create a Window Start Menu shortcut or Desktop shortcut pointing to this file.
View full article
Picard Product_Support
‎2018-09-10 10:14 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:17 AM

Labels:
  • TAC IA Series
2022 Views

Managing the address table in a Lonworks device

Issue Managing the address table in a Lonworks device Product Line EcoStruxure Building Operation, TAC IA Series, TAC Vista Environment I/A Series MNL TAC Xenta Third-party LON devices Building Operation Automation Server Cause A LonWorks device contains an Address Table which will hold a maximum of 15 addresses. Once this table is full, all bindings will only be able to use the broadcast setting which is not desirable. A Xenta 200,300 or 400 controller will have its first 2 address tables used with TAG 0 and TAG 1 binding. This leaves only 13 addresses for user bindings not the 15 addresses like other LonWorks devices. Resolution ​When you create a binding in LonWorks, you decide its behavior by selecting a binding profile. You either select a binding profile, or you use the default profile. There are basically three types of binding profiles: Acknowledged profiles Unacknowledged profiles Broadcast profiles Using an Acknowledged profile will consume one of the 15 available address table addresses on both the sending and the receiving device. The Unacknowledged profiles will only use one Address on the sending device's address table. Broadcast binds do not use an address but are not recommended. Use an acknowledged binding profile when the sending device should receive an acknowledgment from the receiving device indicating that the value of the bound variable was successfully sent. Binding profile Transmit timer Retry count Acknowledged Profile 96 ms 3 Acknowledged, Tx tmr 256, 3 retries 256 ms 3 Acknowledged, Tx tmr 256, 5 retries 256 ms 5 Acknowledged, Tx tmr 1024, 5 retries 1024 ms 5 Be careful of creating large, acknowledged fan-out bindings because they generate a lot of traffic, especially if the device of one of the recipients is offline.  Use an unacknowledged binding profile when the sending device should not receive an acknowledgment from the receiving device. Use this type when the value being sent is not critical and is of low importance to the control logic. Binding profile Repeat timer Repeat count Unacknowledged Profile   0 Unacknowledged Repeated Profile 48 ms 3 Unacknowledged Repeated, 5 repeats 48 ms 5 Use a broadcast profile when you do not want to use up an entry in the address table. The device address table has 15 available entries for bindings but the first entry is a reserved broadcast entry that all broadcast bindings can share. Binding profile Repeat timer Repeat count Broadcast Profile   0 Broadcast Profile, 5 repeats 48 ms 5 If no binding profile is selected, a default profile is used: Point-to-point bindings use the Acknowledged profile as default. Fan-out bindings use the Unacknowledged Repeated profile as default. Building Operation uses the broadcast profile as default when the device address table has run out of entries. If a point-to-point binding is changed to a fan-out binding, the binding profile is automatically updated to an Unacknowledged Repeated profile. If a fan-out binding is changed to a point-to-point binding, the binding profile is automatically updated to an Acknowledged profile.  This and other information about lon bindings is available on the online help guide Using a Lon Binding in StruxureWare Building Operation More information on the different tables used by each LON device
View full article
Picard Product_Support
‎2018-09-06 08:51 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:16 AM

Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC Vista
2603 Views

G3 Enterprise Server "ERROR [web.server] HTTP Server failed to bind to port. Address already in use: JVM_Bind"

Issue MESSAGE [08:29:10 31-May-13 CDT][sys] *** Station Started (203ms) [1919ms total] *** niagara>MESSAGE [08:29:12 31-May-13 CDT][history.db] Starting async warmup of history config index... MESSAGE [08:29:12 31-May-13 CDT][history.db] Async history config index warmup completed in 15 ms. ERROR [08:29:16 31-May-13 CDT][web.server] HTTP Server failed to bind to port. Address already in use: JVM_Bind ERROR [08:29:21 31-May-13 CDT][web.server] HTTP Server failed to bind to port. Address already in use: JVM_Bind Product Line TAC IA Series Environment I/A Series G3 Enterprise Server, all versions Cause Another service on the pc is using port 80, conflicting with the Enterprise Server. For example, Skype will use port 80 as an alternative unless you uncheck the box in Skype options. As a second example, another Niagara station may be running on the same computer. See Changing the HTTP, HTTPS, or TCP ports of the Enterprise Server for a similar port conflict issue with SmartStruxure. Resolution In the Skype menu > Tools > Options > Advanced > Connection, uncheck the box for "Use port 80 and 443 as alternatives for incoming connections"
View full article
Picard Product_Support
‎2018-09-11 04:46 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:11 AM

Labels:
  • TAC IA Series
2161 Views

WorkPlace Commissioning Tool UDP Port: "A critical error occurred in the communication server rtmonitor.exe"

Issue In WorkPlace Commissioning Tool, the following error message appears when browsing a BACnet/IP network: "A critical error occurred in the communication server rtmonitor.exe. Please shutdown this application and the communication server then try again." Product Line TAC IA Series Environment WorkPlace Commissioning Tool Cause There could be a Niagara R2 station running on the computer configured for BACnet/IP. Since the Niagara station also uses UDP port 47808 by default, the Niagara service prevented WorkPlace Commissioning Tool from "binding" to the UDP port. Resolution There are two ways to resolve this issue: Disable the Niagara service when using the WorkPlace Commissioning Tool In Workplace Pro, stop the station that has the BACnet/IP service enabled, and configure it so that it does not auto-start. NOTE: If this procedure does not correct the issue and the WorkPlace Tech Tool software is being run on the Windows 7 operating system, refer to WorkPlace Commissioning Tool Windows 7: "A critical error occurred in the communication server rtmonitor.exe" for information on how to correct what may be a program security settings issue.
View full article
Picard Product_Support
‎2018-09-07 01:27 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:58 PM

Labels:
  • TAC IA Series
2580 Views

Ordering more Newron NL220 credits

Issue How to order more NL credits in order to commission more devices. If the following message displays when opening a NL220 database, then more credits will need to be purchased soon. " BEWARE: less than 20 credits are available on this machine. If you need to install more than 20 device please order the amount of needed credits as soon as possible. Do you want to ask for new credits?" Product Line TAC IA Series, TAC Vista Environment NL220 LNS Cause There are two types of credits: Product specific credits like LonMaker and NL credits LNS credits   Echelon LNS LNS credits are assigned to the PC and when they reach zero, the LNS Server license goes into deficit mode. After 14 days the deficit mode will expire, at which time no LNS tools will be able to be used on that PC. To reverse the lockout, enough LNS credits must be ordered to cover the deficit and any additional nodes that need to be commissioned. Backing up, sharing, and restoring LNS databases can sometimes corrupt these LNS credits, which then prohibits you from launching any LNS plug-ins. For more help with corrupt LNS credits see Corrupted LNS Credits. Echelon LonMaker LonMaker credits are assigned to the PC. Both LNS and LonMaker credits are required, however when commissioning devices in LonMaker, LonMaker credits are consumed but LNS credits are not. Even though LNS credits are not consumed in LonMaker they are still necessary because certain LNS applications (i.e. TAC Vista System Plug-in) require them to operate. Newron NL220 Each time a node is commissioned in NL220 it requires a NL credit and a LNS credit. NL credits are assigned to the NL220 dongle and can be used on other PCs in "MOVED" mode. LNS credits are also necessary in NL220 to operate certain LNS applications such as the TAC Vista System Plug-in.   To order more Echelon LNS credits see Ordering more LNS credits. To order more Echelon LonMaker credits see Ordering more Echelon LonMaker credits. Resolution When working in NL220, it is wise to maintain a higher level of LNS credits than NL credits to help avoid locking out the LNS server license. To check the amount of NL credits remaining go to Start > All Programs > NL Suite > NLCreditsGenerator and look for Remaining NLCredits. The number of NL credits remaining can also be found at the bottom of the NL220 LonWorks Manager window with a project open. To check the amount of LNS credits remaining on a PC go to Start > All Programs > Echelon LNS Utilities > LNS Server License Wizard and look for Credits Available. The number of LNS credits remaining can also be found at the bottom of the NL220 LonWorks Manager window with a project open.   To order more NL220 credits: Open the NLCreditsGenerator Utility that is installed with NL220. Go to Start > All Programs > NL Suite > NLCreditsGenerator > NLCreditsGenerator Utility. Enter the number of NL220 credits to be added  in the request area. Click Next. Click "Yes, this PC will be used for commissioning" Enter your name and contact details. Select "Copy to clipboard". Then either paste the information into notepad or in an email. Send the NL credit request to your local Schneider Electric Buildings Business order department  (NLCredits@buildings.schneider-electric.com). When you order has been processed by the local Schneider Electric Buildings Business order department you will receive an upgrade key. Open the NLCreditsGenerator Utility again. Go to Start > All Programs > NL Suite > NLCreditsGenerator > NLCreditsGenerator Utility. Click the Next button. Enter the key into the "Upgrade key" field of the credits generator. A message indicating you credits were added is then displayed.   Note: Once the request key has been generated, DO NOT commission or decommission any devices with the dongle until the upgrade key has been applied to the dongle. If devices are commissioned before then, the upgrade key will no longer be valid.
View full article
Picard Product_Support
‎2018-09-07 06:11 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:39 PM

Labels:
  • TAC IA Series
  • TAC Vista
2931 Views

Verifying Serial Port Communications with loopback test.

Issue Verifying the Com Port on a PC is working properly by using "Loopback" test in Terminal Emulator. Product Line Andover Continuum, Field Devices, Other, Satchwell MicroNet, Satchwell Sigma, TAC IA Series, TAC INET, TAC Vista Environment Hyperterminal RS-232 serial port Cause The following test writes to the serial port and reads from the same port. This will verify the Full duplex operation of the RS-232 communication. Resolution Short the TX and RX pins of the cable (pins 2 and 3) following the pinouts below. Gender is determined by pin type.                Male DB9 (Left) and Female DB9 (right)   Launch Hyperterminal by selecting Start>>Programs>>Accessories>>Hyperterminal. If you do not have Hyperterminal, please read Hyperterminal on Microsoft Windows Operating Systems. If you are asked if you would like to install a modem, select No. Choose any icon and name the session, select "OK". In the next Pop-Up menu, choose direct to COMx (where x is the number of the COM Port you are testing.) Set the flow control setting to None. Leave the other settings to default settings, select "OK" Select File » Properties from the menu bar, select the Settings tab, and then push the ASCII Setup button. Check the option for Echo typed characters locally. Type something. If you see double characters the serial port is setup correctly and is functional. The display is showing characters that are sent out and what is read in. The Emulator will send and display the TX and immediately read and display  RX. If you see exactly what you are typing, you have a communication issue. which could be: Bad Com Port Bad cables Pins not shorted correctly If you are out of physical ports to try, use a USB Serial Port converter. If you are using a USB, use Reassigning a USB Serial Adaptor to a desired COM port for instructions of assigning Com to another port.
View full article
Picard Product_Support
‎2018-09-10 05:10 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 11:15 PM

Labels:
  • Andover Continuum
  • Field Devices
  • Satchwell BAS & Sigma
  • Satchwell MicroNet
  • TAC IA Series
  • TAC INET
  • TAC Vista
3277 Views

Ordering more Echelon LonMaker credits

Issue How to order more LonMaker credits in order to commission more devices. Product Line TAC IA Series, TAC Vista Environment LonMaker LNS Cause There are two types of credits: Product specific credits like LonMaker and NL credits LNS credits   LNS LNS credits are assigned to the PC and when they reach zero, the LNS Server license goes into deficit mode. After 14 days the deficit mode will expire, at which time no LNS tools will be able to be used on that PC. To reverse the lockout, enough LNS credits must be ordered to cover the deficit and any additional nodes that need to be commissioned. Backing up, sharing, and restoring LNS databases can sometimes corrupt these LNS credits, which then prohibits you from launching any LNS plug-ins. For more help with corrupt LNS credits see Corrupted LNS Credits. LonMaker LonMaker credits are assigned to the PC. Both LNS and LonMaker credits are required, however when commissioning devices in LonMaker, LonMaker credits are consumed but LNS credits are not. Even though LNS credits are not consumed in LonMaker they are still necessary because certain LNS applications (i.e. TAC Vista System Plug-in) require them to operate. NL220 Each time a node is commissioned in NL220 it requires a NL credit and a LNS credit. NL credits are assigned to the NL220 dongle and can be used on other PCs in "MOVED" mode. LNS credits are also necessary in NL220 to operate certain LNS applications such as the TAC Vista System Plug-in.   To order more Echelon LNS credits see Ordering more LNS credits. To order more Newron NL220 credits see Ordering more Newron NL220 credits. Resolution To order more LonMaker credits: Echelon LonMaker v3.1 Open up a LonMaker database and go to LonMaker menu > LonMaker Credits Info... Here you can view how many LonMaker available credits that you have. Click on Add Credits... In the box named Credit Order, type in how many credits to order, then click Next. Following the instructions at the top of the window, click the Copy to Clipboard button to copy the PC key generated by LonMaker License Wizard. Click Cancel. Compose a new email and paste the PC key into the body of the email. Address the email to credits@echelon.com or your local Schneider Electric Buildings Business order department so they can place the order. Follow the instructions at the top of the email making sure to fill out all required fields. Once Echelon or the local Schneider Electric Buildings Business order department sends back an Application Key, open up the LonMaker License Wizard again. Click Next and paste the application key into the field titled "Application Key". Click Finish. Echelon LonMaker v3.2 Turbo Open up the LonMaker License Wizard by going to Start > All Programs > Echelon LonMaker > LonMaker License Wizard. Here you can view how many LonMaker credits that you have available. In the box named Credit Order, type in how many credits to order, then click Next. Following the instructions at the top of the window, click the Copy to Clipboard button to copy the PC key generated by LonMaker License Wizard. Click Cancel. Compose a new email and paste the PC key into the body of the email. Address the email to credits@echelon.com or your Schneider Electric Buildings Business Order Entry Department (888-444-1311) so they can place the order. Follow the instructions at the top of the email making sure to fill out all required fields. Once Echelon or the local Schneider Electric Buildings Business order department sends back an Application Key, open up the LonMaker License Wizard again. Click Next and paste the application key into the field titled "Application Key". Click Finish.
View full article
Picard Product_Support
‎2018-09-10 11:08 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 10:02 PM

Labels:
  • TAC IA Series
  • TAC Vista
3238 Views

Serial connection to I/A Series R2 UNC VxWorks Target Shell using Windows HyperTerminal

Issue Serial connection to I/A Series R2 UNC VxWorks Target Shell using Windows HyperTerminal Product Line TAC IA Series Environment I/A Series R2 Universal Network Controllers: UNC-410-1 UNC-410-1-N UNC-520-2 UNC-520-2-N Cause There maybe a need to access the UNC via its serial port if the IP address of the UNC is unknown or for troubleshooting purposes when the UNC's Ethernet port is not functioning. Resolution Hardware required for connection to UNC's RS-232 port: 8-conductor flat silver satin stranded cable with standard male (plug) RJ-45 connectors RJ-45 to DB-9 adapter (part number: UNCC-405) or a socket-to-plug type RJ-45 to DB-25 adapter (part number: UNCC-430) A functioning COM port on a computer A 2-pin jumper for connection to the UNC's "Mode" connector Refer to the Installations Instructions for UNC-520 (page 15) for details on the cable and adapter (applies for both UNC-410 and UNC-520). Pinout configuration for a RJ-45 to DB-9 Null Modem Adapter (part number UNCC-405) also refers to these pin outs. Connection to UNC's VxWorks Target Shell using Windows HyperTerminal (for operating systems without HyperTerminal, please refer to Hyperterminal on Microsoft Windows Operating Systems😞 Connect the cable and adapter between the UNC's RS-232 port and the RS-232 COM port used on the computer. Start HyperTerminal (Programs > Accessories > Communications > HyperTerminal). In the 'Connection Description' dialog, type a name for this session. For example, 'Connection to UNC'. Click OK. In the 'Connect to' dialog, use the 'Connect using' drop-down list to select the COM port used on the computer. Click OK. In the Com(n) Properties dialog, choose the following settings: Bits per second: 9600 Data bits: 8 Parity: None Stop bits: 1 Flow control: Hardware Click OK. On the UNC circuit board, locate the 4-pin Mode connector and put a 2-pin jumper on the 2 outer pins. Refer to page 17 UNC-520 Installation Instructions for position of the Mode connector (top right corner). With the HyperTerminal session active, remove power from the UNC, let it cycle down, then reapply power. After some number of seconds, text should appear in the HyperTerminal window similar to: Press any key to stop auto-boot... To enter commands to the UNC, press any key to break out of the boot sequence. A prompt similar to the following is shown: [VxWorks Boot]: To determine the IP address / subnet mask of the UNC, do not break the auto-boot sequence as described in step 7. Allow the UNC to finish booting. When the controller stops displaying new messages, press ENTER to reach the command prompt. The prompt is similar to the following: -> Using the scroll bars on the HyperTerminal window, scroll up until the section that begins with the line 'Press any key to stop auto-boot...'. The IP address of the UNC is listed on the line that begins 'inet on ethernet (e)' The IP address is listed (in dotted decimal), followed by a colon, and then the subnet mask (in hexadecimal). Disconnect from the UNC when complete. Press the 'Disconnect' button on the HyperTerminal toolbar. Exit from the HyperTerminal application, selecting to Save if planning to reuse this HyperTerminal setup for future connection to an UNC. Remove the 2-pin jumper from the Mode connector of the UNC. Reboot the UNC by removing the power connector, waiting for all lights to extinguish, and plugging the power connector back in. * If troubleshooting the UNC, send the HyperTerminal start up messages to Product Support for analysis.
View full article
Picard Product_Support
‎2018-09-10 09:11 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:59 PM

Labels:
  • TAC IA Series
7481 Views

Error "The Bcpv3 service is not installed under Config/Services" adding a discovered BACnet device to station database

Issue Encountered the error 'The Bcpv3 service is not installed under Config/Services' while trying to add a discovered BACnet device to the station database Product Line TAC IA Series Environment I/A Series G3 Enterprise Network Server / Workbench Cause The default view of the BacnetNetwork is now the 'Bcp Bacnet Device Manager' instead of the standard I/A Series G3 'Bacnet Device Manager'. This happens when the Distech Controls EC-NET-AX Support Package  v3.0.2.8 (I/A Series G3 support files for Proview) is installed on the computer running the station. Refer to BCP Device Manager showing up with the BACnet Device Manager. The Bcp Bacnet Device Manager is used to discover and add Distech devices. Using it to discover and add I/A Series BACnet controllers will result in the 'The Bcpv3 service is not installed under Config/Services' error. Third party non Distech devices may also exhibit the same symptoms. Resolution Discover and add BACnet devices using the 'Bacnet Device Manager' instead of the 'Bcp Bacnet Device Manager'. The 'Bacnet Device Manager' is now the 2nd view of the BacnetNetwork (right-click on the BacnetNetwork and go to 'Views' > ' Bacnet Device Manager').
View full article
Picard Product_Support
‎2018-09-10 05:12 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-08 09:51 PM

Labels:
  • TAC IA Series
3760 Views
  • « Previous
    • 1
    • …
    • 30
    • 31
    • 32
    • …
    • 85
  • Next »
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.