Managing the address table in a Lonworks device

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Managing the address table in a Lonworks device
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • RandyDavis
    RandyDavis
  • DavidFisher
    DavidFisher
  • PeterLarsen
    PeterLarsen
  • Derrick_Ratliff
    Derrick_Ratliff
  • CraigEl
    CraigEl
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2517 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Managing the address table in a Lonworks device

Picard Product_Support
‎2018-09-06 08:51 AM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:16 AM

Issue

Managing the address table in a Lonworks device

Product Line

EcoStruxure Building Operation, TAC IA Series, TAC Vista

Environment

  • I/A Series MNL
  • TAC Xenta
  • Third-party LON devices
  • Building Operation Automation Server

Cause

A LonWorks device contains an Address Table which will hold a maximum of 15 addresses. Once this table is full, all bindings will only be able to use the broadcast setting which is not desirable.

A Xenta 200,300 or 400 controller will have its first 2 address tables used with TAG 0 and TAG 1 binding. This leaves only 13 addresses for user bindings not the 15 addresses like other LonWorks devices.

Resolution

​When you create a binding in LonWorks, you decide its behavior by selecting a binding profile. You either select a binding profile, or you use the default profile.

There are basically three types of binding profiles:

  • Acknowledged profiles
  • Unacknowledged profiles
  • Broadcast profiles

Using an Acknowledged profile will consume one of the 15 available address table addresses on both the sending and the receiving device. The Unacknowledged profiles will only use one Address on the sending device's address table. Broadcast binds do not use an address but are not recommended.

Use an acknowledged binding profile when the sending device should receive an acknowledgment from the receiving device indicating that the value of the bound variable was successfully sent.

Binding profile Transmit timer Retry count
Acknowledged Profile 96 ms 3
Acknowledged, Tx tmr 256, 3 retries 256 ms 3
Acknowledged, Tx tmr 256, 5 retries 256 ms 5
Acknowledged, Tx tmr 1024, 5 retries 1024 ms 5

Be careful of creating large, acknowledged fan-out bindings because they generate a lot of traffic, especially if the device of one of the recipients is offline. 

Use an unacknowledged binding profile when the sending device should not receive an acknowledgment from the receiving device. Use this type when the value being sent is not critical and is of low importance to the control logic.

Binding profile Repeat timer Repeat count
Unacknowledged Profile   0
Unacknowledged Repeated Profile 48 ms 3
Unacknowledged Repeated, 5 repeats 48 ms 5

Use a broadcast profile when you do not want to use up an entry in the address table. The device address table has 15 available entries for bindings but the first entry is a reserved broadcast entry that all broadcast bindings can share.

Binding profile Repeat timer Repeat count
Broadcast Profile   0
Broadcast Profile, 5 repeats 48 ms 5

If no binding profile is selected, a default profile is used:

  • Point-to-point bindings use the Acknowledged profile as default.
  • Fan-out bindings use the Unacknowledged Repeated profile as default.
  • Building Operation uses the broadcast profile as default when the device address table has run out of entries.

If a point-to-point binding is changed to a fan-out binding, the binding profile is automatically updated to an Unacknowledged Repeated profile.

If a fan-out binding is changed to a point-to-point binding, the binding profile is automatically updated to an Acknowledged profile. 

  • This and other information about lon bindings is available on the online help guide
  • Using a Lon Binding in StruxureWare Building Operation
  • More information on the different tables used by each LON device
Labels (3)
Labels:
  • EcoStruxure Building Operation
  • TAC IA Series
  • TAC Vista
Tags (3)
  • Find more articles tagged with:
  • 18218
  • PeterLarsen19
  • PeterLarsen21
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore