Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Cannot get the AX Tunnel client to establish an ASD connection through the UNC to ASD devices, reporting "GCM Not responding"

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • Cannot get the AX Tunnel client to establish an ASD connection through the UNC to ASD devices, reporting "GCM Not responding"
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • CraigEl
    CraigEl
  • DavidFisher
    DavidFisher
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
1930 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

Cannot get the AX Tunnel client to establish an ASD connection through the UNC to ASD devices, reporting "GCM Not responding"

Picard Product_Support
‎2018-09-10 10:14 PM

Last Updated: Administrator CraigEl Administrator ‎2022-08-09 12:17 AM

Issue

Gets error message "GCM Not responding" when he attempts to make a connection to a device on the ASD bus under the UNC.

Product Line

TAC IA Series

Environment

  • I/A Series R2 UNC
  • I/A Series R2 TunnelAX jar file, version 2.301.534a or later
  • I/A Series ibsASD jar file, version 2.301.534a or later
  • I/A Series G3 Serial Tunnel 2.0 Client

Cause

Misconfiguration of tunnel name

Resolution

Before attempting to configure the AX Tunneling, verify that the correct versions of the R2tunnelAX and ibsAsd jar files have been installed as documented in How to install an I/A Series R2 JAR File.

Tunnel Name in AX Tunnel Client must match the Tunnel Instance name in the ASD Service.

When you add the AxSerialTunnel to the ibsAsdService, the identifier is automatically assigned based on the port defined in the communications configuration of the IbsAsdService itself.  This name is displayed under the Status tab of the AxSerialTunnel:


Figure-1

When configuring the "Niagara AX Serial Tunnel 2.0", the following window is displayed.


Figure-2

The tunnel name (See Figure 2) entered in this window must match the port identifier shown in the AxSerial Tunnel definition (See Figure 1).  If these identifiers do not match, the Ax Serial Tunnel Client will not be able to connect to the tunnel in the I/A Series R2 station.

NOTE: When installing the I/A Series G3 Serial Tunnel 2.0 Client, no control panel applet is created as with the earlier version of the I/A Series R2 Serial Tunnel Client.   To configure the I/A Series G3 Serial Tunnel 2.0 Client,  run the program C:\niagara\VserAx\vseraxConfig.exe.  If you need to frequently reconfigure this client, you can create a Window Start Menu shortcut or Desktop shortcut pointing to this file.

Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 8244
Was this article helpful? Yes No
No ratings

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore