How to install an I/A Series R2 JAR File

Building Automation Knowledge Base

Schneider Electric Building Automation Knowledge Base is a self-service resource to answer all your questions about EcoStruxure Building suite, Andover Continuum, Satchwell, TAC…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Building Automation Knowledge Base
  • How to install an I/A Series R2 JAR File
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close

Related Forums

  • Intelligent Devices Forum

Previous Next
Contributors
  • Cody_Failinger
    Cody_Failinger
  • DavidFisher
    DavidFisher
  • sesa116868
    sesa116868
  • Product_Support
    Product_Support

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Building Automation Knowledge Base
Start a Topic
Options
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
0 Likes
2314 Views

Link copied. Please paste this link to share this article on your social media post.

Trying to translate this page to your language?
Select your language from the translate dropdown in the upper right. arrow
Translate to: English
  • (Français) French
  • (Deutsche) German
  • (Italiano) Italian
  • (Português) Portuguese
  • (Русский) Russian
  • (Español) Spanish

How to install an I/A Series R2 JAR File

Picard Product_Support
‎2018-09-06 02:16 PM

Issue

I cannot find any published instructions giving the procedure to install an updated version of one of the JAR files on my I/A Series (Niagara) system.

Product Line

TAC IA Series

Environment

I/A Series (Niagara) R2 software (any version) installed on a Windows computer

Cause

An updated version of one of the JAR files installed in an I/A Series (Niagara) R2 system has been published.  The updated file has been downloaded to my computer but there are no instructions on how to install it.

Resolution

For the purpose of this explanation of the procedure, the following steps reference an update to the "programlib" jar file for release 2.301.522.   Substitute the name of the jar file being updated and release number in the following steps.

* NOTE: Before attempting to update a jar file, verify that Windows Explorer is configured to display file type extensions. (See * below for more information).

The JAR file update is published, currently on the  as a .zip file containing two files. 

  1. Copy the file programLib-2.301.522c.v1.jar.emb to the \niagara\r2.301.522\emb folder.
  2. Rename the existing file  from programLib-2.301.522.v1.jar to programLib-2.301.522.v1.jar.old.
  3. Rename new file from programLib-2.301.522c.v1.jar.emb to programLib-2.301.522c.v1.jar (removing the .emb extension).
  4. Copy the file programLib-2.301.522.v1.jar.nt to the \niagara\r2.301.522\nt folder.
  5. Rename the existing file  from programLib-2.301.522.v1.jar to programLib-2.301.522.v1.jar.old.
  6. Rename new file from programLib-2.301.522c.v1.jar.nt to programLib-2.301.522c.v1.jar (removing the .nt extension).
  7. Copy the file programLib-2.301.522.v1.jar.nt  to the \niagara\r2.301.522\nre\modules folder
  8. Rename the existing file  from programLib-2.301.522.v1.jar to programLib-2.301.522.v1.jar.old.
  9. Rename new file from programLib-2.301.522c.v1.jar.emb to programLib-2.301.522c.v1.jar (removing the .nt extension).

To install the new jar file into a UNC, perform the following procedure after completing steps 1 through 9, above.

  1. Start the Niagara 522 version of the Admin Tool.
  2. Open a connection to the UNC
  3. Select the "Installation" tab then click the [Installation Wizard] button.
  4. Select the "emb" folder in the "Select Distribution Directory" window then click [Install]
  5. In the "Niagara Remote Installation" window, select the "Configure Modules Only" radio button then click the [Next >] button.
  6. Verify that there is a checkmark in the "Upgrade/Add" column for the updated jar file.
  7. Click the [Next >] button to continue. Make sure that on the "Database Backup" screen that you do backup the existing database.
  8. Continue through the remaining steps and allow the upgrade to install and the station to restart.

 


* To properly rename the files as described in this procedure, Windows Explorer must be configured to show file type extensions.  To configure this setting or verify it, proceed as follows:

  1. Open Windows Explorer by clicking on the My Computer (or Computer) icon on the computer's desktop or by making the selection from the Windows start menu.
  2. From the Windows Explorer "Tools" menu, select "Folder Options"
  3. Select the "View" tab.
  4. Scroll down through the "Advanced Settings" list to locate the entry "Hide extensions for know file types".  Verify that this entry is unchecked.
  5. Click the [OK] button to save the change, if any, and exit the Folder Options screen.
Labels (1)
Labels:
  • TAC IA Series
Tags (1)
  • Find more articles tagged with:
  • 4361
Was this article helpful? Yes No
100% helpful (1/1)

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.